I have been using standard gfci breakers for all the easy heat i installed within the last two months. No issues reported.
Old 03-02-2015, 03:43 PM   #22
warmsmeallup's Avatar
Rewards Points: 12
NEC requires the use of GFEP (30ma) protection. If you use GFCI it can nuisance trip. It may not happen the first year but as they get older, they will trip more often. The in-rush using Self Regulating cables are tremendous so figure that in to your calculation when buying the GFEP breaker.
The "lesser" prices cables usually comes with a "lesser" warranty (1-3 years). The better self regulating cables should come with a 10 year warranty. With pipe freeze, we recommend 5 watt/ft cable. For gutter/leader ice, we recommend 12 watt/ft.
With pipe freeze, if you don't insulate, it will not work as well or at all. You should use a temperature sensor as activation.
warmsmeallup is offline   Reply With Quote
Old 03-02-2015, 04:15 PM   #23
Self regulating heat trace will have inrush current for the first 3.5 seconds. suggest you use a magnetic breaker on the branch circuit. EX: 74 ft of Cromalox 8W/ft. at -26c inrush was 15.9 amps at 120VAC. After 4 seconds the amp draw stabilized to 5.4A at 120VAC.
The inrush is due to the self-regulating dielectric material. the longer the length the more inrush. Nothing to do with inductive reactance or the like.
CAUSA is offline   Reply With Quote
Old 03-02-2015, 04:58 PM   #24
Scott45ee's Avatar
Rewards Points: 12
We typically use Nelson Self Regulating Heat Trace Tape type CLT-5/CLT-25 for Drain Lines in -20 C Freezers.
Most is connected to 208V (CLT-25), some connected to 120V (CLT-5).
All Branch Circuits are Protected via an OCPD with GFPE (30ma trip threshold).
--Scott (EE)
S.E.T.
Scott45ee is offline   Reply With Quote
Heat tape on metal roof just the cowboy General Electrical Discussion 4 11-26-2014 02:43 PM
Heat tape on Gas Meter fungi020 NEC Code Forum 4 01-24-2014 11:13 PM
Any one use Easy Heat SR Trace cables before? cad99 General Electrical Discussion 5 11-28-2013 10:48 AM
Heat tape on fuel line oakleyrdc General Electrical Discussion 10 10-12-2013 09:42 PM
frost protection/heat tape chrisg UK Electrical Forum 18 11-10-2009 11:46 PM