Question Electrical Theory question.. phase balancing
3 phase 4 wire 120/208 system. Phase A pulling 50 amps, phase B pulling 50 amps, phase C pulling 0 amps. Is the neutral carrying a load? Or is does the system balance and leave no load on the neutral. OR would phase C need to pull 50 amps as well to fully balance the system.
Possibly the same question but maybe not...
3 phase 4 wire 120/208 system. Circuit 1, 3 and 5 (first three positions on the left side of the panel) have a 3 pole 20 breaker in place and a 3 phase network circuit going out with a shared neutral. Circuit 1 powers a row of lights (5 amps), circuit 3 powers a row of lights (5 amps) and circuit 5 doesn't power anything. Does the branch circuit shared neutral balance and carry 0 or would it need circuit 5 to also carry 5 amps.
I know in a single phase scenario both cases would result in a balanced load because the two phases are perfectly out of phase with each other by 180 degrees, but with three phase they are out of phase with each other by 120 degrees each which is why I could see the above scenarios balancing to some degree but still leaving some unbalanced load on the neutral- unless all 3 were perfectly equal. Thoughts?
Jmp2016 is offline   Reply With Quote
Old 10-10-2017, 10:43 PM   #2
Band Member
emtnut's Avatar
Rewards Points: 2,146
You would have about 43.3 amps on your neutral.
The system is looked at as vectors, all 3 120˚ apart.
since phase C is zero, the neutral current is sin120˚ X 50 A = 43.3
glen1971, lighterup and Max C. like this.
You should 3D print a toe attachment for your shotgun
Old 10-10-2017, 10:51 PM   #3
Rewards Points: 2,462
Simple formula to remember for 3 Phase Neutral Current.
If A, B and C are the three phase currents, the formula to find the neutral current is the square root of the following:
(A*A + B*B+C*C) - (A*B + A*C + B*C).
I have a better looking formula at work but for now.
frenchelectrican and glen1971 like this.
Old 10-10-2017, 11:34 PM   #4
Ok thanks guys so following that formula..
It simplifies to sqrt ((50^2+50^2+0^2)-(50 x 50 + 50 x 0 + 50 x 0))
Sqrt (5000-2500)
Sqrt (2500)
=50. So would the unbalanced load on the neutral be 50 or am I missing something and it's 43?
Thanks,
Joe
Old 10-11-2017, 01:51 AM   #5
Rewards Points: 1,530
Your missing the point that the phases are 120 degee's apart not 180 !
That's why its 43A not 50A.
study how phase angles effect voltages !
Old 10-11-2017, 03:19 AM   #6
Rewards Points: 26,780
As field electricians, such EE calculations are the stuff of apprentices -- and the occasional j-man test.
We build to the worst case -- ie fattest amps.
In a 208Y120 or 480Y277 system -- one just does not down size neutrals.
Whereas it's common for the Poco to reduce its own Service Laterals to such Services.
The Poco is counting on some load balance -- we can't ever.
As for homework// test questions -- they are answered -- virtually without limit -- in the back threads here at ET.
Old 10-11-2017, 07:14 AM   #7
Rewards Points: 1,642
I would have thought 50 just visualizing the triangle. You have two equal sides at an angle of 60* and a third side of zero length. The neutral current is the length of the segment to close off the triangle.
http://www.jirvine.co.uk/Electrical_...es/Phas_02.gif
If the other two phases are 50 each, what would you need to balance this on the third phase? It's 50 right?
The Following 2 Users Say Thank You to splatz For This Useful Post:
emtnut (10-11-2017), hardworkingstiff (10-11-2017)
Old 10-11-2017, 11:17 AM   #8
Band Member
emtnut's Avatar
Yes, you're right
I was thinking (well, I don't know WHAT I was thinking) ... about the x axis magnitude (@ 120˚)
The neutral current would be 50A
Thanks for catching that Splatzy
hardworkingstiff and splatz like this.
splatz (10-11-2017)
Old 10-11-2017, 12:40 PM   #9
Rewards Points: 1,360
You are a bigot.... you didn't even mention. 600Y/347. There's a new Canuckian here every day!
glen1971 likes this.
Tags
3 phase, electrical, electrical theory, neutral load, theory
Single Phase 480V Transformer Grounding Question Badboy_Matt Industrial Electrical Forum 21 02-24-2017 10:38 PM
Mike holt electrical theory ElectricalArtist Electrician Apprentice Forum 12 12-27-2016 06:31 PM
3 Phase / 1 Phase question J91 Commercial Electrical Forum 16 10-23-2016 04:25 AM
3 Phase Question re same phase in conduit...... conclavicus General Electrical Discussion 21 07-31-2016 08:22 AM