Never had much experience dealing with back up emergency power generators, had a question on test asking "correct location to lock out at is? " is it utility supply or transfer switch?
Thanks
Mcarthur00 is offline   Reply With Quote
Old 09-30-2017, 09:02 PM   #2
Rewards Points: 21,898
Thanks
Short and sweet answer useally at transfer switch location if they have lockout provision then it is used for locked out means. if can be locked out in off postion then that is the answer there.
Plus you will have to lock out the starting and run circuits too ( that will varies depending on the generator set up )
Old 09-30-2017, 09:05 PM   #3
Rewards Points: 485
On the unit itself unless the transfer switch has a lock out means. Most generators we install have breakers on them and some now hvae transfer switches with gen breakers in them.
jsmart84 is offline   Reply With Quote
Old 09-30-2017, 09:08 PM   #4
Yuh that true for small to med size generators but for larger one most common to find breaker at the transfer switch escpally with medium voltage units.
Old 09-30-2017, 09:30 PM   #5
Rewards Points: 485
Maybe medium voltage but the one megger i was at last year had 480 volt breakers within the unit.
Old 09-30-2017, 09:39 PM   #6
Rewards Points: 1,558
QUOTE - [ had a question on test asking "correct location to lock out at is? " ? ]
I think the clue is in this word " lock out "
What would you be locking out
If it's a generator can be only one thing
The incoming mains supply !
So it would be locked in the generator position.
If you read all of the question
And consider carefully what they say
There can only be one answer !