I installed a service where the poco wanted a disconnect at the pole about 130 ft from the house. I installed a triplex for direct burial. I learned that since 2008 the code dont allow to use a 3 wire feeder so I dropped a #4 THHN copper in the trench with the other conductors. Now the inspector tells me that it should be with insulation suitable for direct burial.
How"s such when nobody asks that we use anything else but a regular THHN for grounding rods?.
Peter Goldwing is offline   Reply With Quote
Old 11-05-2016, 07:16 AM   #2
Barjack's Avatar
Rewards Points: 280
300.6 Protection Against Corrosion and Deterioration.
Raceways, cable trays, cablebus, auxiliary gutters, cable
armor, boxes, cable sheathing, cabinets, elbows, couplings,
fittings, supports, and support hardware shall be of materials
suitable for the environment in which they are to be
installed.
and...
(A)(3) In Concrete or in Direct Contact with the Earth.
Ferrous metal raceways, cable armor, boxes, cable sheathing,
cabinets, elbows, couplings, nipples, fittings, supports,
and support hardware shall be permitted to be installed in
concrete or in direct contact with the earth, or in areas
subject to severe corrosive influences where made of material
approved for the condition, or where provided with
corrosion protection approved for the condition.
I know it doesn't say "conductor insulation", but I think this is what the inspector is getting at.
Barjack is offline   Reply With Quote
The Following User Says Thank You to Barjack For This Useful Post:
Flyingsod (11-05-2016)
Old 11-05-2016, 07:28 AM   #3
backstay's Avatar
Rewards Points: 296
A disco doesn't mean it has to be 4 wire. If it's an overcurrent device, then it becomes a feeder in need of a separate ground and neutral. I have never seen thhn run to a rod on a house. I use bare copper.
Old 11-05-2016, 07:38 AM   #4
Barjack's Avatar
Rewards Points: 280
I was thinking bare copper would have been fine, but I wonder if the inspector thinks the soil is corrosive.
Old 11-05-2016, 08:04 AM   #5
Rewards Points: 975
Using bare copper is like putting up a sign saying "Please steal this!".
We always use THHN.
Old 11-05-2016, 08:12 AM   #6
Rewards Points: 276
The POCO asked for a disconnect after the meter at the pole location. I put a meter socket and a feed thru panel (one unit)The panel has a 200A main breaker.Is this my overcorrect protection or the one in the panel in the basement.? I normally dont do this kind of arrangement as i run 3 conductors from meter to basement
Old 11-05-2016, 08:31 AM   #7
Rewards Points: 276
So if its ok to use it to the grounding rod why wouldnt be ok as equipment grounding conductor? The inspector cannot make a decision and asked me to show him where it says I can use thhn. I offered to remove insulation but :
There is no article that says the bare copper COULD be used, Article250.120 (B) only says that bare aluminum or copper clad aluminum cannot be used within contact with the earth.
Old 11-05-2016, 08:32 AM   #8
Rewards Points: 2,462
They both are over-current protection, one will protect the feeder and the house the other the house and if you have a fault that trips the house OCP both will most likely trip
Old 11-05-2016, 08:41 AM   #9
Barjack's Avatar
Rewards Points: 280
Your inspector needs to understand that the NEC is a permissive code.
The burden of proof is on him to tell YOU where it says YOU CAN'T use bare copper. I can tell you that it doesn't, unless there is a corrosive influence, and I wouldn't let him in on that if I were you.
Old 11-05-2016, 08:49 AM   #10
Yeah Toast!!
Roger123's Avatar
Rewards Points: 1,370
the inspector cannot make a decision and asked me to show him where it says i can use thhn.
250.62 nec 2011
Old 11-05-2016, 12:21 PM   #11
Rewards Points: 19,051
I have been thru this with an idiotic inspector before when I ran Thhn/thwn . He was insisting that the insulation on the wire wasn't listed for direct burial and the wire should be bare. I told him that since the wire wasn't listed it must mean that it will degrade the insulation away promptly and so therefore we should review the matter again in fifty years, and he left and that was that.........
If you start feeling the effects of a possible Corona infection, do not take Ibuprofen (ADVIL) to relieve pain, it increases the ability of the virus to replicate itself.
Old 11-05-2016, 04:23 PM   #12
backstay's Avatar
Rewards Points: 296
We always use THHN.
Attachment 94522
I pound my rods a little deeper than that.
mbednarik likes this.
Old 11-05-2016, 04:29 PM   #13
Rewards Points: 975
I got those in by hand using brute strength and sex appeal. I had to get the Hilti to finish them off.
Old 11-05-2016, 07:08 PM   #14
cabletie's Avatar
Rewards Points: 1,274
Which one is considered the service disconnect?
Is there a main bonding jumper in the meter main? Is the neutral bonded to the can in the meter?
Is the #4 really an equipment ground or is it the grounding electrode conductor?
This is a unique install. The only time I have had to fuse the conductors away from the building like this, it was considered the service disconnect. And all the grounding electrodes had to be brought outside.
Inside was not the service, and the neutral was not bonded again inside.
It would be different if the utility only wanted a disconnect by the meter, not a fused disconnect. I am guessing they are considering the pole as the service.
I wunder what the guys do for farms with a central pole as a service. Bring all the grounding electrodes to the pole? Is the pole considered a structure with no grounding electrodes present. So you just drive two ground rods?
Old 11-05-2016, 08:26 PM   #15
backstay's Avatar
Rewards Points: 296
You still run ground rods at each building. No bond at the other panels, only the pole. The ground wire from the house to the pole is sized off the OCP device at the pole, just like any other feeder.
Old 11-05-2016, 09:38 PM   #16
cabletie's Avatar
Thanks,
So no need to bring the UFER ground or any others out to the pole?
The only time I had anything like this it was a service rated transfer switch with generator 300' from the building. All grounding electrodes went out to the transfer switch and generator.
Old 11-08-2016, 02:39 AM   #17
Rewards Points: 54
You should contact to relevant contractor who can resolve this.
JoeAPinkley is offline   Reply With Quote
Old 11-08-2016, 10:47 AM   #18
Rewards Points: 276
The question was if I could use THHN as a grounding equipment conductor ( I did use rods on both ends)
Old 11-08-2016, 10:49 AM   #19
Rewards Points: 276
Originally Posted by joeapinkley View Post
you should contact to relevant contractor who can resolve this.
i am an electrical contractor
What does the term "worked on" mean in the NFPA 70E? Colbert Report NEC Code Forum 21 09-26-2016 11:24 AM
When system and equipment grounding first required kg7879 NEC Code Forum 4 05-18-2016 06:05 PM