fall of potential grounding testing - Electrician Talk - Professional Electrical Contractors Forum
Like Tree1Likes
  • 1 Post By joebanana
Old 05-30-2018, 07:10 PM   #1
Vacated
Wiresmith's Avatar
Rewards Points: 2,848
Default fall of potential grounding testing
is fall of potential testing practical for outside processing plants, i'm guessing larger than 20 acres.
all of the structures have ground rings and they are all connected
by my understanding of fall of potential testing you should be 8 to 10 times the largest diagonal of the ring away from the ring with your injector
so say a new structure is built inside the existing facility and a new ring installed.
1-if you tie the new ring to the existing stuff and do the fall of potential test don't you need to test outside of the facility? 8 to 10 times further away from entire facilities interconnected rings. your green rod at the ring , injector 8 to 10 x away and measurement probe in the 60% area(multiple spots)
2- even if you leave the new ring unhooked from existing do you know anything by testing outside of only the new ring (the existing is going to influence (lower) the readings right?)
3-is there a better option for testing the grounding system in this scenario?
Old 05-30-2018, 08:02 PM   #2
Senior Moment
drsparky's Avatar
Rewards Points: 128
You could do the Intersecting Curves Method.
The Following User Says Thank You to drsparky For This Useful Post:
Wiresmith (05-30-2018)
Old 05-30-2018, 08:18 PM   #3
Rewards Points: 7,569
Why are you testing ground rings? FOP is for rods. If your ground ring is above 25 ohms, a "supplemental" ain't going to help.
http://en-us.fluke.com/products/eart...und-clamp.html
Old 05-30-2018, 08:30 PM   #4
Vacated
Wiresmith's Avatar
you can use fop for rings as well you go out from ring with your injector 8 to 10 times the largest diagonal of the ring
we aren't measuring for 25 more like we have to be below 1 ohm in substations and 5 ohms everywhere else
Old 05-30-2018, 08:34 PM   #5
Vacated
Wiresmith's Avatar
http://accelconf.web.cern.ch/accelco...rs/tups062.pdf
found this article on your method, along with slope and the problems with using FOP in a similar situation to my question
thank you very much, i have never heard of this before. do you know if this is accepted by ieee in any way?
Old 05-30-2018, 08:45 PM   #6
Vacated
Wiresmith's Avatar
looks like star-delta method might be better for testing the smaller systems, anyone know much about this method or used it? or another good one for my scenario?
Old 05-30-2018, 09:04 PM   #7
You can, but why? What are you expecting to find? Ground rings by their nature have about the most soil contact of all the methods, and there isn't much you could do to improve it.
"8 to 10 times the largest diagonal of the ring"? What if it's 500 feet, as in a warehouse? You'd need 4,000 to 5,000 feet of lead wire.
Make your maintenance supervisor spring for the Fluke.
telsa likes this.
Old 05-30-2018, 09:07 PM   #8
Vacated
Wiresmith's Avatar
yep
ieee standards actually require below 1 ohm resistance in substations, so you have to test, and if you test correctly you might actually find more than one ohm believe it or not
we have to below 5 ohms everywhere else
this star delta method reduces the footage you are concerned about(as was i)
Old 05-30-2018, 09:09 PM   #9
Senior Moment
drsparky's Avatar
Rewards Points: 128
I remember reading about this from the Megger manual on testing large ground systems when researching problems in a expansive antenna farm.
see http://www.weschler.com/_upload/site...owntoearth.pdf
Section III and appendix IV
Megger always has neat stuff to learn about.
Old 05-30-2018, 09:11 PM   #10
Vacated
Wiresmith's Avatar
http://www.electricenergyonline.com/...of-Testing.htm
Old 05-30-2018, 10:07 PM   #11
Chief Flunky
Rewards Points: 338
Beyond 8-10 electrodes the resistance decrease is insignificant. In cases where I get high readings it's because the soil conductivity is awful. At that point the choices are to fix the soil or go Ufala. Filling your trench with bags of concrete or a couple yards from a truck is generally the cure. Concrete is hygroscopuc so it sucks up moisture and keeps the ground moist. Only trouble with it is corrosion issues.
Old 05-31-2018, 12:24 AM   #12
Rewards Points: 1,972
Paul then if you take into account the concrete slabs that are most likely either intentionally or by design tied into the grounding electrode system and then any metallic utility piping it is hard to imagine you could get the ground resistance any lower for a facility as described.
Wiresmith (05-31-2018)
Old 05-31-2018, 05:47 PM   #13
Vacated
Wiresmith's Avatar
i agree, but you don't know what your resistance is until you measure it.
Old 05-31-2018, 06:52 PM   #14
Vacated
Wiresmith's Avatar
do you know if limestone (crushed stone used in concrete) back-fill is a desirable back-fill? probably corrosive to copper like concrete to though huh?
do you know of a good back-fill that's not corrosive? even with less conductivity adding properties
Old 05-31-2018, 10:15 PM   #15
Chief Flunky
Rewards Points: 338
Limestone is not inherently corrosive. It's basically inert and neutralizes acids. Concrete often has residual lime which is why the pH is high and both are highly buffered but concrete plus rebar in contact with copper sets up galvanic corrosion. Copper by itself is fine. Limestone is fairly well drained. The ideal backfill has some clays for water retention but still packs well like any good base. The good drainage is an advantage though on the top layer in a substation where they intentionally want a well drained insulator between the linemen and the ground grid although granite is preferred for that.
Wiresmith (06-01-2018)
Old 06-01-2018, 05:55 PM   #16
Vacated
Wiresmith's Avatar
ive asked some others and im going to research 75% limestone washings with 25%bentonite clay for the bottom 8' and crushed stone for the top 2 (all just going to be approximated)
dennis alwon let me know bentonite clay is used for chemical ground rods
ive read you dont want only bentonite though incase it drys up
thanks man
Old 06-01-2018, 06:01 PM   #17
Vacated
Wiresmith's Avatar
anyone hear the term "IONIC ELECTRODE ground rod" before, sounds like standard ground rod, ive never heard that term, not coming up well in google
http://www.ground1.com/ground_rod_installation.htm
looks like its ionic because of high ionic content surrounding it?
Old 06-01-2018, 07:23 PM   #18
Vacated
Wiresmith's Avatar
ground testing in difficult installations
https://www.netaworld.org/sites/defa...ips-Jowett.pdf
Bonding and grounding of Service confusion rbd1313 NEC Code Forum 26 06-12-2018 05:39 PM
Gec entering enclosure ElectricalArtist General Electrical Discussion 1230 02-13-2018 10:35 PM
Two Questions from Apprentice maverick323 General Electrical Discussion 50 06-06-2017 07:26 AM
Fall of Potential Going_Commando PLCs, VFDs, Motors and Controls 21 04-27-2017 08:36 AM
Grounding system testing BT Electric General Electrical Discussion 18 01-19-2016 06:44 PM