Fuel dispensing questions - Electrician Talk - Professional Electrical Contractors Forum
Old 09-05-2012, 10:11 PM   #1
Default Fuel dispensing questions
If I understand 514.8 exception 2 right, I only need to go underground with rmc or imc for the first 24 inches and then can change to pvc. I've been told by 2 different fuel dispenser installers that it needs to be 10 feet.
Do I need seal offs where I enter the building if its 25 feet from the dispensers? I will have seal offs at the dispensers.
Is there a way to protect the rmc or imc from rusting where it enters the ground, like sleeve it in pvc? Probably a dumb question!
Landmark is offline   Reply With Quote
Old 09-05-2012, 10:20 PM   #2
erics37's Avatar
Rewards Points: 642
You're right. Exception #2 allows that.
514.9 Sealing.
(B) At Boundary. Additional seals shall be provided in
accordance with 501.15. Sections 501.15(A)(4) and (B)(2)
shall apply to horizontal as well as to vertical boundaries of
the defined Class I locations.
501.15 basically says you need a seal-off within 10 of the boundary. Exception #2 says you can put it where it emerges from grade as long as you bury the conduit per 300.5 and don't put any fittings before the seal-off. So yes you need one at the building.
Use Robroy (PVC coated rigid) for your stub-ups and convert to PVC once you're 24" down. I don't believe you need concrete encasement of the PVC but I'm not sure.
Old 09-06-2012, 04:40 AM   #3
greenman's Avatar
Rewards Points: 698
Up here you can use Tec Cable with Explosion proof conector.
“We the willing, led by the unknowing, are doing the impossible for the ungrateful. We have done so much, with so little, for so long, we are now qualified to do anything, with nothing.”THE NUCLEAR ELECTRICIAN
greenman is offline   Reply With Quote
Old 09-06-2012, 09:01 AM   #4
Rewards Points: 14,714
I've had that discussion with many "fuel installers". It is usually more cost effective to install the 10' length rather than take the time to cut and thread a piece of conduit. Since they have always seen it done that way, they think it's required. It's not.
Ask them for a code reference and you get some weird answers.
Old 09-06-2012, 09:25 AM   #5
Amish Electrician's Avatar
RobRoy / Ocal is nice, but I've done just fine with simple pipe-wrap tape. It's amazing how well a simple layer of tape stops corrosion.
I'd chcek local practices, though. Different soils act differently.
Amish Electrician is offline   Reply With Quote
Old 09-06-2012, 10:27 AM   #6
Just to be clear, I believe it says 2' of steel prior to turning up, so you would go down, turn the 90, then 2' before PVC.
Edit: In case you don't read any farther, this is incorrect as pointed out by eric
Old 09-06-2012, 10:34 AM   #7
erics37's Avatar
Rewards Points: 642
It says 24" before emerging from grade.
Old 09-06-2012, 12:34 PM   #8
So it does, I stand corrected. Thank you.
Old 09-06-2012, 06:35 PM   #9
Thanks everyone! I'll probably just start with a 10' stick of rmc from the seal and go underground and then change to pvc. I'll post more questions as I do this job if I have any.
Above ground fuel dispensing 10492 NEC Code Forum 13 08-28-2012 02:49 AM
M12 fuel coon88 Tools, Equipment and New Products 14 08-21-2012 06:11 PM
Flex fuel? kbsparky Business, Marketing, and Sales 7 01-08-2012 10:28 AM
Fuel cell gold Alternative Energy Forum 21 08-28-2011 10:35 AM