Fuse holder in 1/2" KO? - Page 2 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree13Likes
Old 02-14-2018, 06:24 PM   #21
Rewards Points: 14,273
No doubt JRaef will explain it. I sucked at transformer theory .
Old 02-14-2018, 06:53 PM   #22
Rewards Points: 1,360
I've never seen these before, what are they for?
Fuses are a type of overcurrent protection device, generally used to open a circuit during a fault or overload.
99cents likes this.
The Following User Says Thank You to RePhase277 For This Useful Post:
Arrow3030 (02-14-2018)
Old 02-14-2018, 07:01 PM   #23
Can't sign em..forget em
lighterup's Avatar
Rewards Points: 10,198
In honor of MTW ,,,you get a
Old 02-14-2018, 08:17 PM   #24
Rewards Points: 3,130
I did not know that - why not? I never did it, never really thought about it until looking at hax's picture ...
A CT is a current transformer, it is designed to transmit current, the voltage will fall wherever it will based on the impedance of the circuit.
If a CT circuit is opened, the voltage will go extremely high, many thousands of volts. Even if the CT has a built-in arc chamber, it'll be destroyed quickly because the windings will arc across each other.
A CT typically operates at very close to a short-circuit.....very low impedance.
Think,of it asa normal transformer with the wire through the center an a winding with one turn. Now think of the other winding with many turns.
Lets say the secondary winding is 100 turns. The voltage ratio will be 100:1. Even at 120, this will yield 12,000 volts.
The fuses this case are for the voltage part of the circuit, not the current part.
Note: there is a difference between a current transformer and a current transducer. Most transducers can be operated open circuit, no transformer can.
HackWork, 99cents and splatz like this.
splatz (02-14-2018)
Old 02-14-2018, 08:39 PM   #25
Rewards Points: 1,991
They are to power the Emon Dmon. The installer fails though. Neat install, but they should be inside the panel. The whole point of the fuses is to tap the main to power the Emon Dmon.
You bury them inside the panel so the tenant can't shut off the power to their electric meter and stiff the landlord. Might as well feed it from a breaker if you are going to make the fuses accessible.
The Following User Says Thank You to JoeSparky For This Useful Post:
splatz (02-14-2018)
Old 02-14-2018, 09:55 PM   #26
Rewards Points: 1,972
If you blow the fuse the CT would be open and several things can happen, Destroy the accuracy, burn a hole in the CT, CT blow up. I have seen all three. THE CT has to have a burden across it otherwise the voltage can climb until you destroy the CT.
ALWAYS short the secondary, we never install CT's without shorting blocks.
Emon CTs are actually Current Sensors, and are self-protected, though I would never rely on that nugget of information when stalling or removing them.
micromind and splatz like this.
splatz (02-14-2018)
Old 02-14-2018, 09:57 PM   #27
Emon states in their directions the fuse needs to be a 1.5 amp, (or close) not going to get a 1.5 amp CB for a panel. AS for location if a customer wants to mess with the billing open the Emon and short out the CT's
What caused this fuse melt down? Canaduh Residential Electrical Forum 9 01-16-2018 07:56 PM
Mystery Fuse Blow Aegis General Electrical Discussion 16 08-17-2017 06:07 AM
how do we know what kind of class for the transfomer fuse or switch gear DS fuse ? mike883 General Electrical Discussion 1 04-30-2016 04:44 PM
Harmonic Filter Fuse glen1971 PLCs, VFDs, Motors and Controls 2 04-06-2016 08:14 PM
Upgrading and outdoor screw-in fuse box to a circuit breaker type box Jimmi328 Residential Electrical Forum 2 03-26-2016 09:09 PM