Generac install - Electrician Talk - Professional Electrical Contractors Forum
Old 10-07-2014, 12:48 PM   #1
Rewards Points: 87
Default Generac install
Installing a 17kw generac guardian series. How many conductors do I need between ats and generator? Does this number change if I want to add a normally closed contact for a hot tub? Which contacts do I need to tap for the coil of said contact? What voltage coil should I get?
Wyremonkey is offline   Reply With Quote
Old 10-07-2014, 12:50 PM   #2
Rewards Points: 87
I know it's a lot of questions. But I also know there are many of you that know this stuff by heart.
Thanks all
Old 10-07-2014, 01:27 PM   #3
Hmacanada's Avatar
Do you have a wiring diag?
You need 4 , 5 if you have the load shedding option.
I've never tried to tap off to to contactor but I would guess you could use the same terminal the solenoid for the gen transfer .
12 dc.
But I'm sure other guys here would know more!
Sent from my iPhone using electriciantalk.com
Hmacanada is offline   Reply With Quote
Old 10-07-2014, 09:40 PM   #4
Rewards Points: 1,062
You need 6. N1, N2, T1, 0, 194, 23. As far as the contactor. They sell an accessory for generac units that is an enclosed contactor for load shedding. There will be terminals on the load shed boArd in the ats for these connections. I believe its a 120v control now
ElectricJoeNJ is offline   Reply With Quote
Old 10-07-2014, 09:55 PM   #5
Rewards Points: 534
Is the transfer switch a 200 amp switch with built in load shedding or are you installing a 16 circuit panel?
ohiosparky99 is offline   Reply With Quote
Old 10-07-2014, 10:10 PM   #6
Rewards Points: 87
Its a 200 amp
Old 10-07-2014, 10:10 PM   #7
Rewards Points: 621
Those are the signal lines. I'm probably stating the obvious, but in addition you will need the 4 wires for the generator power (2 hot legs, a neutral and a ground). Are you running power and signal in separate conduits? If not, watch your voltage rating on the signal lines. You will need wire rated rated at least as high as the power conductors.
You can get away with 18 ga signal wires, but most pull 14 ga.
RFguy is offline   Reply With Quote
Old 10-07-2014, 10:15 PM   #8
Rewards Points: 87
I'm using teck cable. Rated for 600 volt. Trying to find 8 conductor (in case load shedding module's in the genny's enclosure
Old 10-07-2014, 10:20 PM   #9
It shouldn't be, but then I'm not from Canada.
Old 10-07-2014, 10:20 PM   #10
Lep
THE "BIG RED MACHINE"
Lep's Avatar
Rewards Points: 2,927
care to post any pics?
"See the ball; Hit the ball."
Pete Rose:Joe Morgan
Lep is offline   Reply With Quote
Old 10-07-2014, 10:21 PM   #11
[QUOTE="RFguy"] Those are the signal lines. I'm probably stating the obvious, but in addition you will need the 4 wires for the generator power (2 hot legs, a neutral and a ground). Are you running power and signal in separate conduits? If not, watch your voltage rating on the signal lines. You will need wire rated rated at least as high as the power conductors. You can get away with 18 ga signal wires, but most pull 14 ga.[/QUOTE
Yeah I meant to add that to my post, but I forgot.
Old 10-07-2014, 10:39 PM   #12
Rewards Points: 621
It shouldn't be, but then I'm not from Canada eh.
fixed for ya.
Old 10-07-2014, 10:52 PM   #13
Rewards Points: 87
If only this thread were aboot healthy Canadian accents
Old 10-08-2014, 06:33 AM   #14
Can't Remember
Rewards Points: 1,534
They have an all in one power and control cable (tray cable I believe) designed just for this. I'd have to look and see whether its available and whether you can use it in Canada. I usually run two conduits. One for line voltage and one for the 12v. Others have said it correctly, you need the six control wires and the four power conductors. The question is whether you are going to drop out the hot tub or load shed it. Either method is done at the transfer switch. Load shedding requires a PMM kit and maybe additional PMMs if you have additional loads. To drop the load requires an additional contact bolted to the side of the switch that changes state with the movement of the transfer switch. You also need a contactor that can handle the hot tub as well.
Magnettica (10-08-2014)
Old 10-08-2014, 06:45 AM   #15
Hmacanada's Avatar
Hey nrp3, have you installed a eaton gen lately?
They are asking for shielded control wires.
Old 10-08-2014, 07:00 AM   #16
Can't Remember
I know the air cooled are basically Generac with different transfer switches. I am set up to service them, but have only seen them in pictures truthfully. Anytime I see something like that I'd go with seperate conduits. Which model are you working with. I'll have to look it up.
Old 10-08-2014, 07:08 AM   #17
Hmacanada's Avatar
It was in the spring I did a install.
I used a guardian transfer sw up that I had in the shop with the eaton gen.
While I was scanning through the install/Manuel noticed the shielded cable thing.
It was a 16kw if I remember correctly.
Didn't use shielded cable and it worked fine.
Probably just a Canada thing!😄
Old 10-08-2014, 08:34 AM   #18
Can't Remember
Could be. The low voltage wiring is pretty forgiving in that it's not data, etc, just 12v that changes polarity in the case of #23. The other two just carry 12v dc.
Old 10-08-2014, 11:47 AM   #19
Originally Posted by Hmacanada
It was in the spring I did a install. I used a guardian transfer sw up that I had in the shop with the eaton gen. While I was scanning through the install/Manuel noticed the shielded cable thing. It was a 16kw if I remember correctly. Didn't use shielded cable and it worked fine. Probably just a Canada thing!dde04 Sent from my iPhone using electriciantalk.com
I did an eaton last year that has the newer generac controller in it with an eaton transfer switch and it didn't need any control wiring, just the utility sense and battery charger line. it was crazy.
Old 10-08-2014, 01:00 PM   #20
Rewards Points: 21,863
Last generac I hooked up was the same- 4 control wires total.
I stand with Tucker Carlson
Generac ats Mike500s Residential Electrical Forum 53 09-12-2014 03:34 PM
Turnkey Install 14KW Generac tufts46argled Residential Electrical Forum 41 08-17-2014 11:16 AM
generac 20 kw install tomgt63 General Electrical Discussion 5 01-14-2014 08:13 PM
Generac Install ????? herdfan General Electrical Discussion 6 07-07-2012 05:12 PM
generac install Jamie7613 General Electrical Discussion 52 06-06-2012 09:21 AM