Generator Interlock with solar panels - Electrician Talk - Professional Electrical Contractors Forum
Like Tree1Likes
  • 1 Post By dmxtothemax
Old 01-30-2018, 03:44 PM   #1
WronGun's Avatar
Rewards Points: 710
Default Generator Interlock with solar panels
Has Anyone had any installations like this ?
So far what Iíve gathered is the solar controller may be able to determine the difference between utility and gen power if not a contractor may be required
Old 01-30-2018, 04:31 PM   #2
Liberal Lesbian
Rewards Points: 1,038
No go.
This is where you need a transfer panel. Even if you make one yourself by installing a normal subpanel and install an interlock on the main breaker of the subpanel and then move the essential circuits over to it.
The solar needs to be on the PoCo side of the transfer switch (which is the interlock if you instal one).
Old 01-30-2018, 04:32 PM   #3
Liberal Lesbian
My above post is assuming that your solar system is backfeeding a breaker. If the solar is connected to the service entrance conductors via a line side tap, then it is fine to install an interlock the normal way since the main breaker will isolate them.
Old 01-30-2018, 04:40 PM   #4
Rewards Points: 1,554
QUOTE - [ So far what Iíve gathered is the solar controller may be able to determine the difference between utility and gen power ]
YES !
You are correct, the invertors can tell if they are connected to either the grid or to an generator.
Back feeding a generator just doesn't work !
chicken steve likes this.
Old 01-30-2018, 05:30 PM   #5
WronGun's Avatar
Rewards Points: 710
Itís not back feeding the main panel
The meter socket has a Disconnect main breaker and the solar feeds into it
Old 01-30-2018, 06:18 PM   #6
Liberal Lesbian
Where, exactly, does the solar feed the house system?
A back fed breaker after the main?
Somewhere else?
Is there a panel inside that you can install the interlock on, isolating both the utility and the solar from the generator breaker and branch circuits?
Old 01-30-2018, 06:28 PM   #7
WronGun's Avatar
Rewards Points: 710
There is no breaker at the main panel for solar I only have pictures the customer sent me.
Just Trying to get familiar with this before I go look in person.
The panel only has 2 DP breakers 40A oven and 30A AC..
From the picture it goes to the meter socket and how solar exactly ties in I will have this answer when I go look closer
Old 01-30-2018, 06:52 PM   #8
Liberal Lesbian
Basically, you need to keep the solar on the same side of the interlock as the utility power, this way when you switch over the interlock both the utility and solar are isolated from the house electrical system and generator.
WronGun (01-30-2018)
Old 01-30-2018, 07:03 PM   #9
Rewards Points: 416
What Hack said. Xfer switch between your meter box disconnect and the main panel, when utility and solar fail, Xfer isolates them and panel gets power from gen.
mitch65 is offline   Reply With Quote
Old 01-30-2018, 07:12 PM   #10
Liberal Lesbian
What happens around here that I see often is the solar backfeeding the panel via a branch circuit breaker.
In that situation, you can't just install an interlock in the panel because the solar will still be feeding the house and backfeeding the generator, and vice versa.
Old 01-30-2018, 07:34 PM   #11
Can't Remember
Rewards Points: 1,522
Looks like the solar ties into the meter main. If the panel doesnít have a main then youíll likely have to add one or change the panel to one that has one.
Old 01-30-2018, 10:32 PM   #12
WronGun's Avatar
Rewards Points: 710
Ya I will verify this but from the looks of exterior and panel Pictures I have the solar is at the meter main.
I will need to add a main breaker to the panel
Old 02-09-2018, 12:44 PM   #13
WronGun's Avatar
Rewards Points: 710
The panels tap the service conductors and donít go inside to the panel
Old 02-09-2018, 12:48 PM   #14
WronGun's Avatar
Rewards Points: 710
Not familiar with solar setups. This is new to me.
How does this even work? Technically there are 2 power sources feeding the panel on the same lines.
Old 02-09-2018, 12:50 PM   #15
Liberal Lesbian
FWIW, those aren't the service conductors. Those are the load side of the main breaker, which means they are feeders.
If you add a main breaker to the panel inside, you can install an interlock on it and be compliant. The solar will be on the utility side of the interlocked breaker, which is what you want.
Old 02-09-2018, 12:52 PM   #16
Liberal Lesbian
Yes, that's pretty much it. Two power sources meshed together by the inverter. The solar in that house and all the millions of other houses backfeed into the grid and help power it.
Old 05-23-2018, 08:05 PM   #17
JoeSparky's Avatar
Rewards Points: 2,037
Sorry to bump an old thread, but this one fits. Just looked at this situation today on a Siemens panel. Solar feed is a 2 pole breaker. I think this might work with 2 interlocks. Should be able to relocate the solar feed to ckts 2 and 4 and put the generator breaker in ckts 1 and 3. ecsbpk01 on the generator/solar breakers and ecsbpk03 with the normal tin snipping on the right side of it. Should work if the interlocks don't interfere with each other. Anybody tried this yet?
Questions on solar energy bill39 Alternative Energy Forum 8 11-06-2017 09:04 PM
Geographically Distributed Solar Panels? RePhase277 Alternative Energy Forum 17 11-01-2017 02:50 PM
Learning about solar setup and accounting for losses a long the way Wire Tags Alternative Energy Forum 8 08-14-2017 03:35 PM
DC solar system for a single sign light dham206 General Electrical Discussion 35 02-12-2017 06:42 PM
Sizing solar panels and battery bank mpetro Alternative Energy Forum 14 02-15-2016 08:55 PM