I've looked at thousands of generators in my day and I don't know of any here in the big City that actually transferred the building load to the genset except under power failure. Most are programmed to exercise the generator weekly, but to actually transfer the load would cause an interruption, which is a no-go for most buildings.
Some of the more critical data centers have load resistor banks installed so they can be tested periodically under load, but this is rare.
The generator commissioning will require a load bank be brought in and the genset operation verified as to load capability, voltage stability, etc. when first installed but after that genset exercises with no load. Nobody tests the transfer switch except under yearly Fire Dept testing.
I was once on a job where a CAT 1.5 MW genset was undergoing validation in a new high rise building. It started up, transfer switch picked up load bank, and then the big diesel threw a connecting rod right out of the block. It was hell because there was no way to get the new genset in and blown one out due to access. They actually had to pull engine, uncouple generator, and dolly old engine out pulled by a pick up.
Old 07-01-2014, 12:44 PM   #62
Bad Electrician's Avatar
Rewards Points: 4,969
Must be a California thing because here a large majority are tested by transferring the ATS
Almost all the data centers we service either have load banks or we supply them for yearly testing.
The first item is only done if specified the second item as noted is pretty standard here
Been there done that and that is PISS POOR ENGINEERING IMO.
Load Bank Generator Testing vs. Using Building Load to test generators. MR MAB Other Codes and Standards 15 03-16-2009 06:37 PM
load calc. rknrll813 General Electrical Discussion 1 08-14-2008 07:27 PM
Most Basic Generator Load Calculation Formula Randy L General Electrical Discussion 2 07-22-2008 01:53 PM
UF-B load calculation crash63 General Electrical Discussion 1 04-23-2008 08:18 PM