I was thinking about this yesterday:
In an attic, we had temp feeder from panel OCPD to a sub panel so we could disassemble and reconnect pipe to new panel.
The temp connection was a splice made with split bolts. The two hot feeds were tapes but grounded conductor splice was not. I tested amps and had about 4 A on it.
What would it take for me to get shocked from touching it? I avoided it, but figure there's no potential to ground so no risk of shock?
Sorry if this is an ignorant question but I need it explained
dielectricunion is offline   Reply With Quote
Old 02-13-2015, 01:22 PM   #2
The_kid's Avatar
Rewards Points: 12
Don't open that splice up and put yourself between it.
The_kid is offline   Reply With Quote
The Following 5 Users Say Thank You to The_kid For This Useful Post:
Grounded-B (02-16-2015), JDJ (02-16-2015), mikey383 (02-13-2015), Mountain Electrician (02-13-2015), Shockdoc (02-13-2015)
Old 02-13-2015, 01:26 PM   #3
Rewards Points: 1,464
If it was terminated at the main panel correctly you should have 0 volts to ground on it. It still has current through it. Draw it out.
Old 02-13-2015, 01:27 PM   #4
Rewards Points: 132
Oh okay, that makes sense. I was thinking... I know I've been shocked by neutral before but how does that happen?
Old 02-13-2015, 01:30 PM   #5
Like the kid said,don't get between it.
Old 02-13-2015, 01:33 PM   #6
The_kid's Avatar
Rewards Points: 12
Think about it.
What's the load on that circuit?
Where's the load going?
If you put yourself in series with that neutral...
The Following User Says Thank You to The_kid For This Useful Post:
RIVETER (02-13-2015)
Old 02-13-2015, 04:02 PM   #7
Very Long Vacation
Rewards Points: 5,262
Its not at ground potential. As soon as load is applied to the neutral the voltage to earth goes up. This is due to the voltage drop across the wire back to the source.
The Following 6 Users Say Thank You to meadow For This Useful Post:
chicken steve (02-13-2015), Grounded-B (02-16-2015), hardworkingstiff (02-13-2015), Mountain Electrician (02-13-2015), Semi-Ret Electrician (02-13-2015), The_kid (02-13-2015)
Old 02-13-2015, 04:36 PM   #8
Rewards Points: 430
An easy way to think of it is the neutral (grounded conductor) is completing the circuit.
Now if for some reason the neutral was too short you would take a short section of wire, connect it to the neutral bar and the neutral conductor thus completing the circuit and current would now be flowing on every component of the circuit.
If you were to remove the short section of wire and replace it with your body you would now have current flowing through your body and be receiving a shock during the duration of current flowing in the circuit.
Originally Posted by piperunner I just told you guys why you just cant read try to read better does that happen a lot up north must be the cold .
Fibes is offline   Reply With Quote
Old 02-13-2015, 06:45 PM   #9
Retired Account
Rewards Points: 14,650
So, to expand on this a tad Meadow....
The further we are down the circuit, the more this phenomenon should appear
Old 02-13-2015, 07:29 PM   #10
The_kid's Avatar
Rewards Points: 12
Voltage drop resistance + natural human body resistance =
Old 02-13-2015, 07:29 PM   #11
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
Exactly. 8 volts of voltage drop will have 8 volt difference of potential from grounding conductor to grounded conductor.
meadow (02-13-2015)
Old 02-13-2015, 08:17 PM   #12
Retired Account
I'm wondering if my Ideal VD tester operates on that simplicity McClary
Old 02-13-2015, 08:48 PM   #13
Very Long Vacation
Yup. Load and wire size also play a role. The smaller the wire and/or the more current, the more voltage drop. The more voltage drop the more voltage your neutral will read to earth.
Old 02-13-2015, 08:49 PM   #14
Very Long Vacation
Said better than me.
Old 02-13-2015, 08:53 PM   #15
Retired Account
Thx Meadow
So we can basically reverse engineer the VD formula from the far end of a circuit, which i suspect my fancy dancy VD meter is doing for me.....~CS~
Old 02-13-2015, 08:59 PM   #16
Very Long Vacation
Thx Meadow
A High impedance meter is good at picking such stuff up.
Basically when you have voltage drop current is being restricted, so a rise in voltage takes place. That rise in voltage wants to push current along alternate paths back to the source. So if you touch the neutral while grounded some of that current will go through you.
Also the reason why current should be kept off grounding wires.
chicken steve (02-14-2015)
Old 02-14-2015, 07:17 PM   #17
220/221's Avatar
Rewards Points: 4,124
I bet everyone remembers when they found that out the hard way.
I was only a few weeks in and troubleshooting some 120V landscape lights.
I went from, "WTF" to "Duh" in about 10 seconds.
Old 02-14-2015, 07:31 PM   #18
Retired Account
Lady calls and complains that she gets shocked doing laundry
But only when the dryer is on , and she's touching the washer or sink.......
Old 02-14-2015, 07:33 PM   #19
The_kid's Avatar
Rewards Points: 12
My buddy gets hit in his stove when he touches a metal knife to the pan he's cooking on.
So I told him to wear shoes when he cooks
Old 02-15-2015, 07:02 PM   #20
Cl906um's Avatar
Rewards Points: 1,206
After reading posts I was wondering if you were talking amps, or volts on the equipment ground. You were saying amps, and others talked volts. Or, were you talking on the grounded conductor? Pretty sure you were getting 4 amps on grounded which has same potential as earth, but like the others said, don't open it..
Loose Neutral Shock Hazard GEORGE D General Electrical Discussion 17 06-13-2013 10:56 PM
Grounded Neutral Dube2 Commercial Electrical Forum 15 05-07-2012 01:12 PM
Neutral v.s. Grounded conductor? Cletis General Electrical Discussion 35 04-16-2012 07:55 AM
Help troubleshooting grounded neutral ShannonWilson General Electrical Discussion 7 05-29-2008 11:01 PM