I'm trying to find my question in the code but can't seem to have a clear understanding of this. Example if you had two pipes emt pipe in and out one pipe is used for feed in and out with splice, second pipe is using the box just as a pull point for bends. Does the second pipes egc need to be looped and spliced with the first pipe ? I don't see why I would cut the egc and splice it when they all join back at the panel Together. Another example if we had a
Pull box sized correctly with 4" pipes for a sub panel some 3/4" emt branch circuits spliced in the box the 4" is just the pull point im not going to join that egc with the 3/4" egc? Hope this all makes sense on how I'm asking it. Thanks
Matthew90 is offline   Reply With Quote
Old 12-20-2018, 09:37 PM   #2
Bird dog's Avatar
Rewards Points: 1,720
How much electrical work have you done & what was it (residential, commercial or industrial)?
Old 12-20-2018, 09:49 PM   #3
German Spy
Helmut's Avatar
Rewards Points: 3,965
If your using EMT, why do you need an EGC?
Old 12-20-2018, 09:58 PM   #4
Rewards Points: 12
I'm still a 3rd year apprentice resi/light commercial. Emt can be used as egc but id rather not rely on set screw fittings to trip my over current device in a fault.
Old 12-20-2018, 10:06 PM   #5
Small Potatoes
flyboy's Avatar
Rewards Points: 3,636
Because any self respecting electrican knows that relying on EMT fitting set screws for an effective ground path is Hack. I mean hack.
Speedy Petey likes this.
Old 12-20-2018, 10:09 PM   #6
Rewards Points: 4,442
Are these hypothetical questions? Who intermingles a panel feeder in the same box with local branch circuits?
Old 12-20-2018, 10:09 PM   #7
Small Potatoes
flyboy's Avatar
I posted before I saw your post.
Old 12-20-2018, 10:12 PM   #8
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 1,038
if there is no code violation (which there isn't), it's done somewhere.
Speedy Petey and flyboy like this.
Old 12-20-2018, 10:14 PM   #9
Bird dog's Avatar
Some of us aren't self respecting electricians.
flyboy and Switched like this.
Old 12-20-2018, 10:15 PM   #10
Cow
Rewards Points: 4,598
EMT qualifies as an EGC and there our studies out there, I'm told, that have shown it provides even a better path than a wire type EGC in some instances.
That said, in our shop, we always pull a ground wire. Some people think it's wasteful, I think it's good insurance. We also have customers that don't chisel us down to the gnats ass over pricing, so I don't have any reason not to pull one.
Read 250.96(A) and 250.148.
If you still have questions after that, then feel free to ask them.
Old 12-20-2018, 10:16 PM   #11
Small Potatoes
flyboy's Avatar
There isn't. I've seen it many times. What about a trough above a panel where the feeders come in and branch circuits go out in conduits between them?
wildleg likes this.
Old 12-20-2018, 10:17 PM   #12
Switched's Avatar
Rewards Points: 8,942
Old 12-20-2018, 10:19 PM   #13
Bird dog's Avatar
I had an NEC instructor that said good design dictates that you pull a ground.
Old 12-20-2018, 10:20 PM   #14
Rewards Points: 25,894
Many suffer from high self-esteem.
readydave8 likes this.
Old 12-20-2018, 10:28 PM   #15
wildleg's Avatar
to the OP: unless something has changed since 2011 (my last code cycle),
1) metallic boxes need to be grounded in an approved way
2) if (equipment) grounds are spliced they need a jumper to the metallic box
3) there's no rule that says you can't have pulled through unspliced grounds
if someone disagrees, let them list the article and correct me.
frenchelectrican and gpop like this.
Old 12-20-2018, 10:28 PM   #16
Small Potatoes
flyboy's Avatar
Old 12-20-2018, 10:29 PM   #17
Switched's Avatar
I see
Current on ground big time. just the cowboy General Electrical Discussion 27 05-31-2018 02:04 PM
Y Delta woes chicken steve NEC Code Forum 58 04-03-2018 05:52 PM
Dry ground pulls power boxes from homes in Regina, causes six fires RFguy Canadian Electrical Forum 12 08-02-2017 10:36 PM
Water line used as system ground. ELECTRICK2 Residential Electrical Forum 92 05-22-2017 06:48 PM
Ground fault, ship dwong General Electrical Discussion 0 05-22-2016 01:44 PM