Hi Guys,
We have recently replaced our transfer switch for our emergency generator. The new switch transfers slower than the old style which has created a problem with some of our controls. I would like to put a ups in-line on the circuit that feeds the 120V to the control transformers. I can't seem to find anything that isn't plug in style. Anyone run into this and have any suggestions?
Thanks
BMA Sparky is offline   Reply With Quote
Old 02-09-2015, 12:32 PM   #2
cuba_pete's Avatar
Rewards Points: 2,985
Originally Posted by BMA Sparky View Post
Hi Guys,
Thanks
KVA of the load?
Put in a recp.
Old 02-09-2015, 12:38 PM   #3
Electrical Simpleton
Pete m.'s Avatar
Rewards Points: 172
Just out of curiosity is your generator an actual "emergency generator" or is it an "optional standby"?
Pete
Old 02-09-2015, 12:55 PM   #4
Rewards Points: 2,950
What did you have in place previously to maintain power between utility power failure and generator power energizing? Why does it not work now?
Old 02-09-2015, 01:31 PM   #5
Rewards Points: 42
The KVA of the load is minimal maybe .8. I believe the new generator would be classified as a standby unit. There was nothing in place previously as the old transfer switch transferred so quickly that the equipment didn't pick up the loss of power. I am told that the new unit is set to transfer as fast as it can be set, but it is still slower that the old one.
Old 02-09-2015, 04:31 PM   #6
That's not possible. In the event of a power loss, the ATS senses the loss, signals the generator to start and then transfers the load only after it verifies a proper voltage is available. There is no way your equipment was able to remain energized during this procedure.
Old 02-09-2015, 04:33 PM   #7
Jlarson's Avatar
Rewards Points: 4,074
Look at the Allen Bradley 1609-B series or the Sola SDU series.
Jlarson is online now   Reply With Quote
Old 02-09-2015, 04:50 PM   #8
Rewards Points: 42
I wasn't clear. The problem occurs when we test our generator and switch from utility to generator and back. Not in an actual power outage.
Old 02-09-2015, 06:04 PM   #9
Rewards Points: 3,078
I like APC, you can contact them and ask their advice on custom configurations.
Greg
Old 02-09-2015, 06:58 PM   #10
Cl906um's Avatar
Rewards Points: 1,206
We just put in a couple uf hard wired Siemens ups in data rooms that worked pretty well.
Old 02-09-2015, 06:59 PM   #11
Rewards Points: 1,361
Can you use a plug in style and install an inlet for your load?
Old 02-09-2015, 09:32 PM   #12
Bad Electrician's Avatar
Rewards Points: 4,969
Moral of the story, know what you are buying before you buy.
Lots of options google it, I used a Liebert
Old 02-09-2015, 09:48 PM   #13
Rewards Points: 25
Most of APC's larger (3000 & 5000 series Zander up) can be optioned for hard wiring.
raldous is offline   Reply With Quote
The Following User Says Thank You to raldous For This Useful Post:
Old 02-10-2015, 10:00 AM   #14
Rewards Points: 42
One other thought. I had planned to install the ups near the panel that the circuit originated from. This is because it branches out to two locations to feed two control transformers. I am concerned that I am violating a code or at least creating a safety risk if someone were to turn off the breaker and then attempt to work on the wiring, which would still be fed by the ups. Would it be code compliant with proper labeling to warn of the risk?
Old 02-10-2015, 12:36 PM   #15
Like this maybe?
The Following User Says Thank You to samgregger For This Useful Post:
Bad Electrician (02-10-2015)
Inspector wants hardwired smokes in existing house? aftershockews General Electrical Discussion 28 08-28-2013 09:10 PM
Ups ohmontherange General Electrical Discussion 2 04-13-2013 10:54 PM
Dc ups quanchai General Electrical Discussion 6 11-23-2012 12:25 AM
Recent trouble with Kidde hardwired smoke and co alarms farlsincharge Residential Electrical Forum 6 04-06-2012 08:44 PM
Ups calimurray General Electrical Discussion 3 11-02-2007 11:26 PM