Heat Pump & Zone System - Page 2 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree10Likes
Old 10-29-2017, 04:08 PM   #21
Rewards Points: 3,006
Originally Posted by A Little Short View Post
First, it is a heat pump only. I think some were getting "furnace" when I mentioned that the HVAC guy said he needed to tell the thermostat that it was controlling a gas furnace, not that I actually have a gas furnace.
The zone system is a Braeburn 3-Zone
The HP is a Goodman.
The way I understand it is the HP defaults to cold and the reversing valve changes it to heat.
What doesn't make sense is the new zone calls for heat and gets heat. But the old zone calls for heat and gets cool.
He said he needed to make the thermostat think it was controlling a gas furnace. Like I said, the two thermostats are identical and wired the same.
He removed the control wire for the cooling as a temp fix. Looks like "W2-O/B.
Someone asked about the ambient temp when it felt cold. Well it started out at 70° and went down to 64°. So it was atually cooling not just feeling cool.
Are you using all 3 zones?
Which zone is the master zone (the one that determines heat or cool)?
If the default (no power to reversing valve) is cooling then disconnecting the control wire for cool makes absolutely no sense.
There is more to the issue than it seems the tech has found.
hardworkingstiff likes this.
Old 10-29-2017, 06:08 PM   #22
Rewards Points: 21,896
Is that a two stage thermosat ?? because I did see someone mention W2 that kinda give me a clue.,,
Is that is the only thermosat on that floor or there is other one on that floor ?
Old 10-29-2017, 07:51 PM   #23
MTW
Rewards Points: 10,214
This can't be diagnosed over the internet. Too many variables. You need a good hvac tech there in person, not some pot smoking kid who just finished hvac school last month.
Old 10-29-2017, 08:05 PM   #24
Rewards Points: 804
Do you partake in the whacky tobacco?
Old 10-29-2017, 08:06 PM   #25
MTW
No, I'm not a millenial like Hackwork is.
Old 10-29-2017, 09:07 PM   #26
A Little Short's Avatar
Rewards Points: 1,014
There is no master zone with this per se. You can make one "priority" or "priority all", which allows either one to call and you set a delay for the other should it call for the opposite.
It's a single stage stat and there is another on the same floor.
The HVAC guy isn't a young kid, he's a seasoned tech. I'm just not sure he's all that experienced with this zone system.
I did look at the back of the thermostat that he replaced and I see a slide switch to set "heat gas (HG) or heat electric (HE)
I believe that's what he's saying he needs to change. If that's the case I can save him a trip and change that myself.
But again, what doesn't make sense is the other stat is the same (setting & wiring) and works correctly.
Old 10-29-2017, 10:03 PM   #27
I've done mostly EWC, Honeywell, and Trane zone dampers.
All those have a master zone to control heat or cool.
That system sounds like if 2 T-stats were too close together the system could switch back and forth constantly.
Old 10-29-2017, 10:32 PM   #28
Rewards Points: 44
The t-stats are communicating with a controller not the HP, they need to be set for gas furnace.
FF301 is offline   Reply With Quote
Old 10-29-2017, 11:16 PM   #29
The thing is the OP do have heat pump but no gas furnace at all.
Old 10-29-2017, 11:49 PM   #30
That is correct but the 'furnace' setting in the panel means the T-stat calls for a/c, fan, and heat.
It doesn't call for reversing valve, stages of heat, emergency heat, or stages of cooling.
Old 10-30-2017, 12:12 AM   #31
The zone control panel will remain set to HP, only the thermostat will be changed to "gas furnace or gas heat".
Old 10-30-2017, 12:13 AM   #32
Correct it was a mistake for me to say panel.
Wish I could blame auto correct but it was having 2 conversations at once over here.
Old 10-30-2017, 11:08 PM   #33
Default Update
So I found out what needed to be changed on the thermostats. I called the HVAC tech and told him I could save him a trip and change them myself. He agreed so I made the changes.
On the thermostats there are two slide switches that need to be changed. One is Heat Gas (HG)/ Heat Electric (HE) and the other is Heat Pump (HP)/Conventional (C)
I changed the heat to gas and heat pump to conventional
Dip switch on the control panel was to be on reversing valve "O" rather than "B". It was already on "O" so I left it.
Also put the cooling control wire back on the terminal.
I tested the system (both zones) on both heat and cool and everything worked as it should (AFAICT)
Side note: I mentioned that the new zone worked correctly (heat on when heat was called for) to start with. I found out why. The slide switch was already set to "Conventional". The other slide was on "Electric Heat" but I did change it to "Gas". Now I'm not sure it/they have to be changed to "Gas" since it worked being on "E". But both are on "Gas" now and working so I will leave it at that.
The Following User Says Thank You to A Little Short For This Useful Post:
hardworkingstiff (10-31-2017)
Old 10-31-2017, 01:59 AM   #34
backstay's Avatar
Rewards Points: 296
Correct me if I'm wrong, but doesn't the fan run at higher speed for electric heat vs gas? That's the difference I think.
Old 10-31-2017, 07:34 AM   #35
mgraw's Avatar
Rewards Points: 16
Yes, if it is a two speed motor. In this case the fan is controlled by the zone controller.
I should add: In gas mode the fan is not controlled by the t-stat when set to heat.
mgraw is offline   Reply With Quote
Old 10-31-2017, 09:22 AM   #36
Fan is normally in highest speed for cooling and low or medium for heat, depending if it is 2 speed or3 speed motor.
Many of the newer air handlers have a variable speed controller and the speed varies by call and plenum temp or other such criteria.
Heat pump for a pool Sca10 Canadian Electrical Forum 10 08-03-2017 08:49 PM
Water line used as system ground. ELECTRICK2 Residential Electrical Forum 92 05-22-2017 07:48 PM
Heat Pump Question power General Electrical Discussion 7 10-05-2016 12:58 PM
Heat pump 40A? The.Juggernaut Canadian Electrical Forum 61 07-15-2016 05:04 PM
Connecting Grid-tied, PV system to the electrical system katwalatapan Alternative Energy Forum 13 06-15-2016 08:57 PM