Heating Equipment - Electrician Talk - Professional Electrical Contractors Forum
Old 02-22-2015, 07:45 PM   #1
Aegis's Avatar
Rewards Points: 1,726
I was given a drawing for this new job and it shows 9 'heating coils' around the commercial unit. They are all 600v 3 phase and most are 2kw and a few 4kw. The drawing shows the main breaker as a 40A 3P. So I was thinking of running #8s to a centralized location and then tapping this location with #14 or #12 BX to each heating coil. I've never installed heating like this before. What do you guys think?
Aegis is offline   Reply With Quote
Old 02-22-2015, 08:01 PM   #2
Rewards Points: 18,271
Originally Posted by Aegis View Post
I was given a drawing for this new job and it shows 9 'heating could' around the commercial unit. They are all 600v 3 phase and most are 2kw and a few 4kw. The drawing shows the main breaker as a 40A 3P.
What are you going to do for disconnecting means at each unit?, and does the nameplate call for fuse's?
JOBS GROWTH SOARS
RECORD WORKING
UNEMPLOYMENT 50-YEAR LOW
Drudge Report
Old 02-22-2015, 08:23 PM   #3
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
Land your 8's in a small load center and let each set of heat strips have their own breaker.
Old 02-22-2015, 08:28 PM   #4
That is what I was getting too, but first I wanted to see if the op realized he cannot just terminate a tap into an appliance.
JOBS GROWTH SOARS
RECORD WORKING
Drudge Report
Old 02-22-2015, 08:33 PM   #5
Aegis's Avatar
26-806 Heating equipment rated 117 kW and less
(4) The branch circuit shall be permitted to be tapped as necessary to supply the various pieces of associated equipment, but there shall be no overcurrent protection supplied in the tap to any piece of associated equipment the operation of which is essential to the proper operation of the heating unit, unless the control equipment is of such a nature that the heating unit will be shut down if the associated equipment fails to function due to the operation of the overcurrent device.
I was reading this in the code and was thinking this would apply. Each piece of equipment should come with it's own disconnect or install one, but I wasn't thinking of fusing each one after the tap. Unless this code doesn't apply.
Old 02-22-2015, 08:35 PM   #6
Rewards Points: 3,090
What kind of drawing. Obviously no cable schedule or any detail, I will assume. I am not getting what a 'heating could' is, is this a typo?
I can assume you are using the CEC.
Borgi
Old 02-22-2015, 09:06 PM   #7
Aegis's Avatar
'Heating coils' sorry, I'm using the CEC/Ontario code. These drawings are from an Engineer.
The Following User Says Thank You to Aegis For This Useful Post:
51360 (02-22-2015)
Old 02-22-2015, 09:12 PM   #8
'Heating coil' sorry, I'm using the CEC/Ontario code. These drawings are from an Engineer.
Try Section 62. Many options.
If you could tell us the type of heating unit it is, that would be helpful. If you have that info available.
Borgi
The Following User Says Thank You to 51360 For This Useful Post:
Aegis (02-22-2015)
Old 02-22-2015, 10:03 PM   #9
MTW
Rewards Points: 10,268
Pretty sure there's no such thing as a "small load center" for 600 volts.
Old 02-22-2015, 10:45 PM   #10
Aegis's Avatar
Thanks Borgi.
Now I'm looking to see if I need disconnects near by, they'll probably be on these units when they arrive anyway.
62-114 (4) Where two or more fixtures, cable sets, heating panel sets, or parallel heating sets are grouped on a single branch circuit, the non-heating leads of cable sets and taps to cable sets, fixtures, and strip systems shall
(a) have an ampacity not less than one-third the rating of the branch circuit overcurrent device; and
(b) be not more than 7.5 m in length.
51360 (02-22-2015)
Heating and Air RIVETER Off Topic (Non Trade) 16 12-12-2014 09:08 PM
Heating and AC? cc2kj General Electrical Discussion 25 07-29-2014 09:13 AM
Nm covering on fixed electric space-heating equipment 191Wife NEC Code Forum 0 07-16-2014 04:37 PM
Heating methods electro916 Off Topic (Non Trade) 27 11-11-2013 10:36 AM
Making a heating cable thermostat, and heating cable questions redblackviper General Electrical Discussion 12 01-10-2011 08:22 AM