Hospital Grade M.C cable - Electrician Talk - Professional Electrical Contractors Forum
Old 12-09-2013, 08:56 PM   #1
Default Hospital Grade M.C cable
Im currently wiring a physician's doctors office. Alot of hospital grade mc cable but with the inspectors blessing got it approved to use all purpose cable on anything above ceiling. Was elated to not have to use the hospital grade mc on all my 24 light fixtures meaning not having to take that ground to the dog houses! What a time saver.
JustinJ is offline   Reply With Quote
Old 12-09-2013, 09:00 PM   #2
Awg-Dawg's Avatar
Rewards Points: 726
What is all purpose cable?
I feel sorry for people who don't drink, when they wake up in the morning, that's the best they will feel all day.
Awg-Dawg is offline   Reply With Quote
Old 12-09-2013, 09:04 PM   #3
BBQ
Salty Member
BBQ's Avatar
The NEC does not require hospital grade MC for the lighting.
Old 12-09-2013, 09:07 PM   #4
Awg-Dawg's Avatar
Rewards Points: 726
I think hes using MCAP.
Old 12-09-2013, 09:16 PM   #5
Talking
Correct, mcap its got the aluminum ground.
Old 12-09-2013, 09:21 PM   #6
Dash Dingo's Avatar
Rewards Points: 318
Mc cable with a bonding strip in it instead of a copper ground. Like ac cable.
Dash Dingo is offline   Reply With Quote
The Following 2 Users Say Thank You to Dash Dingo For This Useful Post:
Awg-Dawg (12-09-2013), JustinJ (12-09-2013)
Old 12-09-2013, 09:39 PM   #7
BBQ you might want to take a look at 517.11 (patient care vicinity) my interpretation when it says and extending vertically not less than 7 1/2 ft above the floor) I think that your hots and legs coming down to your switches must be hospital grade mc. Your whips in between lights dont have to be. Whats your opinion?
Old 12-09-2013, 09:45 PM   #8
That is the way I was taught. If the wire goes below 7.5 feet and the device opens into a patient care area it needs to have a redundant ground.
Slimshaneee is offline   Reply With Quote
The Following User Says Thank You to Slimshaneee For This Useful Post:
Old 12-09-2013, 09:59 PM   #9
Yes It has an aluminum ground in it that you bend back 120 degrees past the sheath and cut off and when you insert the cable into the connector and tighten that gives you your ground. Just make sure that locknut is tight or you could potentially lose it.
Old 12-09-2013, 09:59 PM   #10
Awg-Dawg's Avatar
Rewards Points: 726
I don't think he was disagreeing with you.
The cable you are calling hospital grade mc, Is actually called Health Care Facilities Cable of HCFC for short.
The Following User Says Thank You to Awg-Dawg For This Useful Post:
Old 12-09-2013, 10:01 PM   #11
Rewards Points: 976
Regular MC still can not be used for the lights above 7.5 feet in a patient care area but AC can, see the exceptions to 517.13(B), the insulated conductor is not required but a metallic raceway recognized as an EGC is.
Roger
Roger is offline   Reply With Quote
The Following 3 Users Say Thank You to Roger For This Useful Post:
BBQ (12-10-2013), Bbsound (12-10-2013), JustinJ (12-09-2013)
Old 12-09-2013, 10:04 PM   #12
Rewards Points: 1,122
I didnt think there was approved connectors for AP that had a locknut
I always use the Arlington snap in connectors
'I believe that banking institutions are more dangerous to our liberties than standing armies"
Thomas Jefferson
electricalwiz is offline   Reply With Quote
Old 12-10-2013, 12:46 PM   #13
CES
Rewards Points: 31
Roger
Thanks Roger I have seen some inspectors interpret the 7 1/2ft rule and let regular m/c go.
CES is offline   Reply With Quote
Old 12-10-2013, 01:25 PM   #14
di11igaf's Avatar
Rewards Points: 282
As roger said, the exception that allows the 7-1\2'(517.13 (B)(1)(3) ex. #2) points back to 517.13(A), which says the metallic raceway, armor, or sheath shall itself qualify as an EGC, which regular MC does not.
Like you I have most definitely seen regular old mc used for lighting in areas considered to be patient care.
IBEW
There's no place like ~/
di11igaf is offline   Reply With Quote
Old 12-10-2013, 06:41 PM   #15
Professional Nit Picker
manchestersparky's Avatar
Rewards Points: 2,180
Then those inspectors need to go back to school !
I disapprove about 35% of ceiling inspections in patient care areas as the EC does not use the proper wiring methods. It has become such an issue that I printed out copies of 517.13 to give to the electrician when discussing it with them.
Anything Worth Doing ....
Is Worth Doing Right
Old 12-10-2013, 07:49 PM   #16
BBQ
Salty Member
BBQ's Avatar
I know that is not an inspectors job but I say thanks to you and other inspectors that do that.
manchestersparky (12-10-2013)
Hospital Grade tkb General Electrical Discussion 19 05-11-2013 02:04 PM
Hospital grade MC MHElectric General Electrical Discussion 39 03-31-2013 03:39 PM
Hospital Grade... blinkers General Electrical Discussion 6 01-04-2011 12:19 AM
When to use Hospital grade recepts? Losrod NEC Code Forum 15 05-18-2008 05:29 PM
Hospital Grade gilbequick General Electrical Discussion 14 11-23-2007 08:50 AM