Hello fellows. A couple of questions for you guys. Helping my friend out. He got some wiring issues in his kitchen. First, He has a 12-3 wire going from his panel box to a outlet box on his kitchen counter. The black and red wires are going to separate breakers. The red wire in the outlet box is connected to other wire going down to the dishwasher. The black wire from the panel box is feeding a receptacle and some under counter lights. Both circuits are sharing the white neutral from the panel box. This setup has been working for a while. We ran into a problem when trying to hook up a GFCI outlet in place of the regular receptacle. The GFCI did not like it and wouldn't work.
1) first puzzler. A Bosch high end Dishwasher. I turn the breaker on to the red wire which in turn sends power to the black wire for the dishwasher. With the neutral DISCONNECTED, I can read 120 volts to ground from the white neutral from the dishwasher! When I hook the neutral from the dish to the neutral from the panelbox, I DON'T read any voltage to ground on the neutrals. I don't understand this. Whats going on?
2 )Also, is there something you need to know about sharing neutrals when hooking up GFCI OUTLETS?
Any help and guidance would be greatly appreciated!
The day I stop learning is the day I die
bogart219 is offline
Old 03-11-2018, 07:13 AM   #2
Retired Account
Rewards Points: 14,650
1) Reeks of a switch leg
2) gfi's don't share noodles well
chicken steve is offline
Old 03-11-2018, 07:20 AM   #3
German Spy
Helmut's Avatar
Rewards Points: 4,555
Not a puzzler. It's the way things work, because you shut one side of MWBC off, and left the other one turned on, and my guess is you are troubleshooting this with the under cabinets lights on.
You probably hooked it up wrong.
Helmut is online now
Old 03-11-2018, 07:40 AM   #4
Can't sign em..forget em
lighterup's Avatar
Rewards Points: 10,200
I've never had a problem w/ 12-3 MWBC for
kitchen counter top gfci circuits.
I usually do this for the required (2) small
appliance circuits in kitchen. Neutral is shared
on the line side of both gfci circuits.
If you are attempting to share the neutral
on the load side of the gfci , for a different
circuit ,it will trip off every time.
If you are on the load side of the gfci and
attempting to run the dishwasher , maybe
the dishwasher is tripping it off . I never gfci
protect dishwashers.
lighterup is offline
Old 03-11-2018, 08:20 AM   #5
Barjack's Avatar
Rewards Points: 308
I hope that high end Bosch dishwasher survives your troubleshooting methods.
Disconnecting a neutral in a MWBC creates a series circuit at 240V. If you have those counter lights running on the other circuit along with the D/W, there is a potential for very bad things to happen. Those counter lights will basically determine the voltage the D/W sees.
If you share the neutral on the load side of a GFCI with another circuit, it will trip.
zac likes this.
Barjack is offline
Old 03-11-2018, 08:54 AM   #6
Rewards Points: 2,149
And this is the reason why the NEC pushes against MWBC.
To keep it simple for the unskilled.
I say let em fry their GFI's and appliances trying to figure it out.
zac, Barjack and telsa like this.
active1 is offline
Old 03-11-2018, 09:05 AM   #7
Rewards Points: 3,078
Good Answers
Greg
3DDesign is offline
Old 03-11-2018, 09:15 AM   #8
Rewards Points: 41
First what do you guys mean by MWBC?
Old 03-11-2018, 09:16 AM   #9
Rewards Points: 41
No
Yes, that is why on here asking for help!
Old 03-11-2018, 09:17 AM   #10
Barjack's Avatar
Rewards Points: 308
Multi
Wire
Branch
Circuit
That is what is feeding those two circuits.
This is important stuff, and to be honest, you should know this before troubleshooting.
Barjack is offline
Old 03-11-2018, 09:18 AM   #11
Multi-Wire Branch Circuit, two breakers sharing a neutral.
Greg
3DDesign is offline
Old 03-11-2018, 09:57 AM   #12
Rewards Points: 21,898
Multi Wire Branch Circuit.
That is a super common item on both single and three phase system with neutral conductor in the system.
Anytime you see the MWBC .,, you NEVER ever open the neutral conductor on purpose. you can damage anything on the MWBC.
The voltage will go up or down depending on the type of load it is hooked up on MWBC.
frenchelectrican is offline
Old 03-11-2018, 09:59 AM   #13
Yup on single phase system and on three phase system you will find three breaker sharing a neutral.
Old 03-11-2018, 10:24 AM   #14
Rewards Points: 41
I've seen circuits sharing neutrals before but never seen this acronym before.
So to recap. took one hot and the neutral from the panel box to the dishwasher.
Hooked the black and ground wire to the dishwasher. Left the neutral to the dishwasher from the panel box UNHOOKED. Why am I reading 120 volts to ground on the neutral from the dishwasher?
Old 03-11-2018, 10:30 AM   #15
Barjack's Avatar
Rewards Points: 308
Because the neutral is the return path for the current of the dishwasher.
Because the neutral is disconnected, there is now potential (voltage) to complete the circuit.
If you test between the dishwasher neutral and the circuit neutral back to the panel, you should also read 120V.
The ground wire (albeit not correct) and the neutral are potential paths to complete the circuit.
If those counter lights are also on with the other circuit, that is another path. That is where things will start burning up.
Barjack is offline
Old 03-11-2018, 10:30 AM   #16
Light Bender
eddy current's Avatar
Rewards Points: 8,038
That is how electricity works. Your hot is going through something in the dishwasher and coming back on the neutral. You read voltage on the neutral because you disconnected it.
You’ve most likely fried the dishwasher by opening the neutral at the panel. If both circuits were on and if the neutral downstream was still connected to both the under cabinet lights and the dishwasher, opening the neutral at the panel turns your mwbc into a 240volt series circuit.
Bird dog likes this.
eddy current is offline
Old 03-11-2018, 11:20 AM   #17
Rewards Points: 41
The dishwasher works fine. Never "opened" the neutral at the panel. Didn't connect it at the outlet box.
Old 03-11-2018, 11:24 AM   #18
Rewards Points: 41
This right here is what I'm trying to get at. Is this normal? How can this be?
Thanks!
Old 03-11-2018, 11:33 AM   #19
Light Bender
Thanks!
???? Of course it’s normal. Wire a light bulb with a hot and a neutral. Turn it on and then open the neutral. What voltage do you expect to read from the neutral leaving the light back to the source?
Old 03-11-2018, 12:37 PM   #20
German Spy
Helmut's Avatar
STOP
Put everything you took apart, back together again, except for the GFI that was the initial problem.
You had to of hooked the GFI up wrong, or have a bad GFI, and now your chasing a dishwasher circuit????
Had did you disconnect the old recep, and how did you hook up the new GFI?
Closed Thread
Fronius Symo 20.0-3 480 (Delta - Wye Transformer), Neutral Wire jay_the_gemini Commercial Electrical Forum 2 02-13-2018 07:27 AM
200amp underground service in Alberta, reduced neutral jingles4214 Residential Electrical Forum 10 11-05-2016 07:09 AM
Conductor Electek inc General Electrical Discussion 25 05-04-2016 11:02 PM
Neutral required to be ran to generator? lynes.nathan Canadian Electrical Forum 7 03-01-2016 09:10 PM
115 VAC disconnect - should I break both hot & neutral? Paul Kraemer General Electrical Discussion 11 01-22-2016 10:21 PM