For that size wire I use my rabbit cutter pliers to score . And then I merely pull the insulation off after that, no need to cut it loose.
Never heard of a tool called a rabbit cutter? Sounds like everyone else has. Is it just a wire stripper?
conclavicus is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 12-27-2016, 07:24 PM   #22
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

Quote:
Originally Posted by Suncoast Power View Post
I have a pile of those ripelys, they seem to have to be adjusted for each type of jacket. It's a PITA.

I use a small Klien pocket knife.
I make a small horizontal cut about an 1-1/2 or what ever the depth of the lug is and then make a vertical cut towards the end of the cable.
I then drop back down and complete the horizontal score cut around the cable.
This type of cut leaves a vertical tap that can be used to peel the insulation off of the cable.
This cut and peel can be accomplished in 5 seconds or less and leaves only one piece of insulation that gets dropped in a small box by your feet.
I then hit the termination with a battery impact with a long hex key.
We then determine the torque value usually printed on a label inside of the gear.
Our designated "torque boy" will torque each termination and put a sharpie mark across the lug.
We will also typical write the torque value on each type lug. I.e. 42

This method works best for me but, I only do maybe 300 or so terminations in a year. Other guys here sometimes spend months making up switch gear.
How do you know that you haven't over torqued it with the impact before you hit it with the torque wrench?
Cl906um is offline   Reply With Quote
Old 12-27-2016, 07:27 PM   #23
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

Quote:
Originally Posted by conclavicus View Post
Never heard of a tool called a rabbit cutter? Sounds like everyone else has. Is it just a wire stripper?
The cindys ( loppers). Bunny gun? You know.
Cl906um is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 12-27-2016, 07:29 PM   #24
Senior Member
 
sbrn33's Avatar
 
Join Date: Mar 2007
Location: middle america
Posts: 11,438
Rewards Points: 3,276
Default

I don't really torque anything, but I almost always put a sharpie mark across it.
readydave8 likes this.
sbrn33 is offline   Reply With Quote
Old 12-27-2016, 07:54 PM   #25
Senior Member
 
Cl906um's Avatar
 
Join Date: Jul 2012
Location: Upper Michigan
Posts: 1,626
Rewards Points: 1,206
Default

Quote:
Originally Posted by sbrn33 View Post
I don't really torque anything, but I almost always put a sharpie mark across it.
That's funny. What I am really saying is sometimes maybe. Really never. I myself am more worried about over torqued aluminum. Like it or not, it is here to stay. A lot of guys will wiggle large copper conductors, then spot torque again. A habit that should never be done on aluminum. On copper, I like to do it cause it settles the strands in a bit. Probably the wrong thing to do, but it is how I was taught. Insurance that the wire won't just fall out of the lug I guess. Over torqued aluminum on the other hand will just keep squishing out till there's nothing left.
Cl906um is offline   Reply With Quote
The Following User Says Thank You to Cl906um For This Useful Post:
sbrn33 (12-28-2016)
Old 12-27-2016, 09:56 PM   #26
Senior Member
 
Join Date: Jul 2013
Location: Indiana
Posts: 657
Rewards Points: 114
Default

Quote:
Originally Posted by conclavicus View Post
Never heard of a tool called a rabbit cutter? Sounds like everyone else has. Is it just a wire stripper?
The pieces of conductor left after you trim them to fit are referred to as rabbit. Thus the device used to make them is called a rabbit gun. It's a large diameter cable cutter. Like bolt cutters but for conductor. Do you just call em cable cutters?



Sent from my C6725 using Tapatalk
Flyingsod is offline   Reply With Quote
Old 12-27-2016, 11:09 PM   #27
Senior Member
 
five.five-six's Avatar
 
Join Date: Apr 2013
Location: So Cal
Posts: 6,234
Rewards Points: 8,778
Default

Utility knife, ring and slit then peal.
MechanicalDVR, TGGT, telsa and 1 others like this.
__________________
Liberal Paradise would be a place where everybody has guaranteed employment, free comprehensive healthcare, free education, free food, free housing, free clothing, free utilities, and only authorities have guns. We have such a place. It's called prison.
five.five-six is online now   Reply With Quote
Old 12-28-2016, 05:43 AM   #28
Junior Member
 
Join Date: Dec 2016
Location: DFW
Posts: 4
Default

Quote:
Originally Posted by conclavicus View Post
Do you use a special tool or a blade or a pocket knife???? Any special technique to not damage the conductors?????



I use a blade or sharp knife to cut the circle around the wire, then I cut a lengthwise slit, then I peel back and use blade to complete the job. It is slow but no tool cost involved.


It may seem easier to use the method you are referring to as far as slicing the insulation with your cutting instrument (whatever that may be) perpendicular to the conductor then making a semi parallel slice to the end of the conductor, then removing the insulation. However, it is frowned upon by most inspectors and engineers, for the fact that it has been known to create "hot spots"! Believe it or not that sharp blade or razor knife will definitely score the conductor.
The proper way to remove the insulation is to sort of "carve/whittle" the insulation off the complete diameter of the conductor never holding the blade perpendicular to the actual conductor itself. It is much more painstaking and time consuming, but it is the right way and will create a much better installation and avoid any "hotspots" years down the road.


Sent from my iPhone using Tapatalk
glen1971 likes this.
joellyj7 is offline   Reply With Quote
Old 12-28-2016, 05:47 AM   #29
Old Grumpy Bastard
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: "Old Dominion"
Posts: 59,296
Rewards Points: 1,008
Default

Quote:
Originally Posted by papaotis View Post
around here the linesmen use a carpet layers hook knife. just pull it toward them. either they have a specail technique or they dont worry about nicks
It takes practice to lay the blade flat enough not to dig in just as it does to score and grab enough jacket just to tear it loose with linemans.
joellyj7 likes this.
__________________
I'm as Christian as possible in the times we live in.

Always just a stallion in a china shop
MechanicalDVR is offline   Reply With Quote
The Following User Says Thank You to MechanicalDVR For This Useful Post:
Southeast Power (12-28-2016)
Old 12-28-2016, 05:53 AM   #30
Junior Member
 
Join Date: Dec 2016
Location: DFW
Posts: 4
Default

Quote:
Originally Posted by MechanicalDVR View Post
It takes practice to lay the blade flat enough not to dig in just as it does to score and grab enough jacket just to tear it loose with linemans.


To true! It definitely takes experience! We all have learned tricks of the trade. And only experience and training and being trained will teach us that. I just always like to show my green hands the "proper method" then the more productive method in the field. And as time goes on they will find what best suites them.


Sent from my iPhone using Tapatalk
joellyj7 is offline   Reply With Quote
Old 12-28-2016, 05:59 AM   #31
86 45 20
 
Southeast Power's Avatar
 
Join Date: Jan 2009
Location: Florida
Posts: 17,735
Rewards Points: 8,146
Default

Quote:
Originally Posted by Cl906um View Post
How do you know that you haven't over torqued it with the impact before you hit it with the torque wrench?
Two things to mitigate over torque.
Using a long hex key, they flex more than you would expect.
Lower setting on the impact. You don't want to use an 18 volt Milwalkee on a high setting for this part.
I always expect to get a slight turn and then a pop from the torque wrench.
Southeast Power is offline   Reply With Quote
Old 12-28-2016, 06:00 AM   #32
Old Grumpy Bastard
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: "Old Dominion"
Posts: 59,296
Rewards Points: 1,008
Default

Quote:
Originally Posted by joellyj7 View Post
To true! It definitely takes experience! We all have learned tricks of the trade. And only experience and training and being trained will teach us that. I just always like to show my green hands the "proper method" then the more productive method in the field. And as time goes on they will find what best suites them.


Sent from my iPhone using Tapatalk
As long as they don't use a razor knife, seen far too many slips and stitches after.
__________________
I'm as Christian as possible in the times we live in.

Always just a stallion in a china shop
MechanicalDVR is offline   Reply With Quote
The Following 2 Users Say Thank You to MechanicalDVR For This Useful Post:
glen1971 (12-28-2016), Southeast Power (12-28-2016)
Old 12-28-2016, 06:04 AM   #33
86 45 20
 
Southeast Power's Avatar
 
Join Date: Jan 2009
Location: Florida
Posts: 17,735
Rewards Points: 8,146
Default

Quote:
Originally Posted by joellyj7 View Post
It may seem easier to use the method you are referring to as far as slicing the insulation with your cutting instrument (whatever that may be) perpendicular to the conductor then making a semi parallel slice to the end of the conductor, then removing the insulation. However, it is frowned upon by most inspectors and engineers, for the fact that it has been known to create "hot spots"! Believe it or not that sharp blade or razor knife will definitely score the conductor.
The proper way to remove the insulation is to sort of "carve/whittle" the insulation off the complete diameter of the conductor never holding the blade perpendicular to the actual conductor itself. It is much more painstaking and time consuming, but it is the right way and will create a much better installation and avoid any "hotspots" years down the road.


Sent from my iPhone using Tapatalk
I don't let guys pull out a razor knife on a cable termination or have them waste time penciling a low voltage cable.
If they are an experienced cable splicer, work fast and thay are not milking the job, they can have the whole thing and do whatever they want.
I know how cables to expect to be put up in an hour, it's very telling if someone knows what they are doing.
MechanicalDVR and joellyj7 like this.
Southeast Power is offline   Reply With Quote
Old 12-28-2016, 06:14 AM   #34
Junior Member
 
Join Date: Dec 2016
Location: DFW
Posts: 4
Default

Quote:
Originally Posted by Suncoast Power View Post
I don't let guys pull out a razor knife on a cable termination or have them waste time penciling a low voltage cable.

If they are an experienced cable splicer, work fast and thay are not milking the job, they can have the whole thing and do whatever they want.

I know how cables to expect to be put up in an hour, it's very telling if someone knows what they are doing.


I like the word penciling!


Sent from my iPhone using Tapatalk
joellyj7 is offline   Reply With Quote
Old 12-28-2016, 06:22 AM   #35
Hackenschmidt
 
splatz's Avatar
 
Join Date: May 2015
Location: Parts Unknown
Posts: 8,316
Rewards Points: 4,022
Default

Quote:
Originally Posted by LawnGuyLandSparky View Post
A pipecutter.
I have not tried this but I am going to for the ring cut. I have one of these somewhere



that I use once a year for tubing. I imagine once you figure out how far to turn the wheel after it touches the insulation, it would be totally repeatable to ring the wire without ever going to far and nicking the wires.

I have tried the slitters that will make the parallel cut but they haven't worked great, I still wind up using a knife. I think a cured blade is less likely to dive in and nick the wire but I really have to go slow.
__________________
Everything Should Be Made as Simple as Possible, But Not Simpler
splatz is online now   Reply With Quote
Old 12-28-2016, 06:54 AM   #36
Junior Member
 
Join Date: Dec 2016
Location: DFW
Posts: 4
Default

No


Sent from my iPhone using Tapatalk
joellyj7 is offline   Reply With Quote
Old 12-28-2016, 08:30 AM   #37
Senior Member
 
Join Date: Jul 2013
Location: Indiana
Posts: 657
Rewards Points: 114
Default

Quote:
Originally Posted by joellyj7 View Post
It may seem easier to use the method you are referring to as far as slicing the insulation with your cutting instrument (whatever that may be) perpendicular to the conductor then making a semi parallel slice to the end of the conductor, then removing the insulation. However, it is frowned upon by most inspectors and engineers, for the fact that it has been known to create "hot spots"! Believe it or not that sharp blade or razor knife will definitely score the conductor.
The proper way to remove the insulation is to sort of "carve/whittle" the insulation off the complete diameter of the conductor never holding the blade perpendicular to the actual conductor itself. It is much more painstaking and time consuming, but it is the right way and will create a much better installation and avoid any "hotspots" years down the road.


Sent from my iPhone using Tapatalk
I was taught the same thing in school. One in the field however I realized it's just as easy to gouge the conductor while penciling as it is to nick the conductor while ringing.

So I made up this story about how electrons crossing the gap of a nick created resistance and there for heat. While a gouge allowed the electrons to smoothly flow past as normal. I realize now that it was my minds attempt to assuage my cognitive dissonance about what I was taught and what I observed.

I've been threatening to run some experiments in the shop for years now but haven't got around to it. We def have the equipment needed but it seems that when there's down time there is something more pressing that needs to get done.

So I'm just wondering if you have any scientific data about nicks in the conductor that aren't just anecdotes or opinions of past professors. If anyone has concrete data I would love to hear it.

Sent from my C6725 using Tapatalk
Flyingsod is offline   Reply With Quote
Old 12-28-2016, 10:28 AM   #38
Senior Member
 
Join Date: Nov 2007
Posts: 6,232
Rewards Points: 4,398
Default

Quote:
Originally Posted by splatz View Post
I have not tried this but I am going to for the ring cut. I have one of these somewhere



that I use once a year for tubing. I imagine once you figure out how far to turn the wheel after it touches the insulation, it would be totally repeatable to ring the wire without ever going to far and nicking the wires.
(snip)
Yes, there's a slight learning curve but anyone not an idiot will pickup the process easily. When it comes to terminating 500s and other "huge" wire,I'm not in the least bit concerned if I overtighten and "scratch" the conductors a bit. Everything I work on is overengineered 100% or better anyway.
LawnGuyLandSparky is offline   Reply With Quote
Old 12-30-2016, 08:54 PM   #39
Senior Member
 
Join Date: Oct 2015
Location: england, ar
Posts: 176
Rewards Points: 352
Default

I've skinned a ton of big wire with a knife like Glen1971 pictured. My company had a rule about tools having to be approved and they were really strict on knives.
lightman is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
16 AWG wire ampacity at higher temperatures Paul Kraemer General Electrical Discussion 5 10-13-2016 05:41 PM
is it OK to use the wire connector to connect the ground wire inside the drop ceiling mike883 General Electrical Discussion 29 07-20-2016 12:37 PM
Branch circuit wire for a 12v dc off grid solar cabin Off Grid Alternative Energy Forum 14 05-12-2016 08:13 AM
Wire Strippers for #18 stranded 2 conductor !Tom Tools, Equipment and New Products 22 05-04-2016 08:22 PM
8ga Aluminum Oven Wire vs 8ga Copper Wire? savatreatabvr General Electrical Discussion 17 01-13-2016 07:57 AM


All times are GMT -4. The time now is 01:19 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com