Hi, fairly new to the forums, but I feel like I need another set of eyes. I did a complete rewire with a 200A service about a year ago. Recently the customer has been coming home after work and finding several circuits off throughout the house. They aren't in the tripped position, they're off. It's a Siemens panel with seimens breakers. Both standard single poles, and arc faults. She also complained of certain circuits going out, and then power coming back on by itself. I went to troubleshoot, B phase was dead in the panel. Went to check the meter socket, and found that the meter actually wasn't plugged in all of the way. PECO had recently replaced the meter with a smart meter. Made sense to me. That leg wasn't getting a good connection which would cause arcing and possibly a surge causing breakers to trip into the off position. Problem solved. Customer calls me back a week later. Same problem, and now lights are dimming throughout the house on different circuits. Sounds like a loose neutral. Now I wired the panel myself, but I went back, checked all of the connections, everything is tight. Service is grounded properly. Taps are tight. So now I'm thinking that it's a PECO neutral problem. PECO went there today and tested the load side of the meter. Said everything checked out, but they didn't check the load side of the transformer. I'm going back tomorrow and I'm going to disconnect the service ground and then test for voltage at the meter. If they did lose the PECO neutral, we both could have been getting a false reading through the ground. If that turns out not to be the case, I'm at a loss. I don't know what else it could be. Can a bad arc fault cause other breaks to nuisance trip? I'd appreciate any suggestions. Sometimes a second set of eyes comes in handy.
paulpupo is offline   Reply With Quote
Old 02-15-2015, 08:10 PM   #2
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
Is she on municipal water or well?
chicken steve (02-15-2015)
Old 02-15-2015, 08:15 PM   #3
Rewards Points: 14
Municipal.
Old 02-15-2015, 08:16 PM   #4
Cl906um's Avatar
Rewards Points: 1,206
Does she have a restraining order out on anyone? If they are off and not tripped, that sounds funny. Is she lonely? Maybe she wants your company. We rented Gone Girl the other day. Good movie. Suspenseful. Get some fingerprints off the ones that are pushed off.
The Following 3 Users Say Thank You to Cl906um For This Useful Post:
chicken steve (02-15-2015), jbfan (02-15-2015), pete87 (02-15-2015)
Old 02-15-2015, 08:17 PM   #5
Rewards Points: 14
That thought had crossed my mind. But the lights were dimming when I was there last.
Old 02-15-2015, 08:31 PM   #6
Cl906um's Avatar
So when you say circuits were off, you mean breakers were on, but circuits were not? Or, arc and ground faults were tripped? Maybe she installed some dimmers on her own from a Home Depot handbook for effect. btw, I am a sceptic on weird chit. You didn't explain if the breakers were in off position, or circuit from live breaker was off.
Old 02-15-2015, 08:40 PM   #7
The_kid's Avatar
Rewards Points: 12
Just last night I went to a lady's house who had the same problem. Some circuits off, some circuits dimmed, some circuits completely fine. Very very strange. Everything was tight. I had her call the PoCo. Turns out there was an issue on there end.
I thought the same thing, loose neutral, but if you checked everything on your end, it's gotta be on there end.
Have you check the voltage line to line, line to ground, line to neutral, and neutral to ground on your feeders in your main panel?
The_kid is offline   Reply With Quote
Old 02-15-2015, 08:40 PM   #8
Rewards Points: 14
No dimmers. Breakers are off and circuits are dead.
Old 02-15-2015, 08:44 PM   #9
Rewards Points: 14
Yes. I checked line to line, line to neutral, and neutral to ground. Everything checks out. The only thing I didn't do was disconnect the service ground and then test line to neutral. But I plan on doing that tomorrow. If I do that and then have nothing line to neutral, I know I was reading through the ground before and it has to be on Peco's end. Other then that, I got nothing.
Old 02-15-2015, 08:46 PM   #10
The_kid's Avatar
Rewards Points: 12
Very strange dude. Mine was a 200A Siemens with the same issue.
I'm sure you tested the voltage output of each individual breaker as well?
well anyway, good luck. And let's hope it's PoCo.
Old 02-15-2015, 08:54 PM   #11
Rewards Points: 14
Yep. Tested every breaker. Everything on my end tests out. In almost 20 years, I've never seen a problem like this. I've had open service neutrals before, but not with these symptoms. It's driving me nuts.
Old 02-15-2015, 08:58 PM   #12
Voltron's Avatar
Rewards Points: 480
Voltron is offline   Reply With Quote
Old 02-15-2015, 09:00 PM   #13
Rewards Points: 3,078
Ask the PECO to place a recording meter on the service. It will record voltage, amperage and surges for a week or so. They should do it for free. West Penn Power will do it.
Greg
The Following User Says Thank You to 3DDesign For This Useful Post:
Old 02-15-2015, 09:04 PM   #14
evil bastard
Rewards Points: 746
Municipal.
I would bet there's an open or high resistance neutral at the xfmr. You're probably grounding through the water pipe grounding electrode conductor.
The Following 3 Users Say Thank You to mcclary's electrical For This Useful Post:
360max (02-15-2015), guest (02-16-2015), hardworkingstiff (02-16-2015)
Old 02-15-2015, 09:11 PM   #15
Rewards Points: 14
That's what I think. I'm checking for that tomorrow.
Old 02-15-2015, 09:20 PM   #16
MXer774's Avatar
Rewards Points: 608
How about the meter jaws. Have seen this problem when poco wants to change meter. Maybe the jaws are bent. Other than that I agree about the possible neutral issue.
MXer774 is offline   Reply With Quote
Old 02-15-2015, 09:20 PM   #17
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
Any deaths occurred in the premises. I'd recommend a qualified spiritual advisor.
The Following User Says Thank You to Shockdoc For This Useful Post:
Old 02-15-2015, 09:52 PM   #18
The_kid's Avatar
Rewards Points: 12
Yes I agree with shock...
How are ya? Mike "the kid" ****, electrician and licensed spiritual advisor. Give me all your money $$$$$
Old 02-15-2015, 10:25 PM   #19
jbfan's Avatar
Rewards Points: 174
Very strange woman in that movie!
"The problem isn't that Hillary Clinton lies. We all know she lies. The problem is that her supporters don't seem to care"
jbfan is offline   Reply With Quote
Old 02-15-2015, 10:32 PM   #20
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
http://www.house-crazy.com/wp-conten...rror-house.jpg
Stumped duganwa General Electrical Discussion 8 11-11-2014 10:41 PM
Hello everyone, I'm stumped... SparkedOut76 General Electrical Discussion 17 06-09-2013 02:26 PM
Stumped Dash Dingo General Electrical Discussion 16 02-24-2013 09:08 PM
Need help....Stumped Rhiggins1981 General Electrical Discussion 13 09-03-2012 08:35 PM
Stumped BIGRED General Electrical Discussion 37 03-01-2007 03:29 PM