interesting question: what if there is no bonding between ground and neutral? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree23Likes
Old 05-28-2016, 01:07 PM   #1
Rewards Points: 540
Default interesting question: what if there is no bonding between ground and neutral?
we all know we need to bonding the ground and the neutral in the system, either inside the transformer or at the first service point, in this way, the ground can use the bonding point then return to the transformer as a loop
an interesting question is what if there is no bonding between ground and neutral, then the ground can return to the transformer, then there is no complete loop
in this situation, if the ground touch the hot, what will happen? ground fault, short circuit?
don't forget there is no complete loop of the ground
mike883 is offline   Reply With Quote
Old 05-28-2016, 01:10 PM   #2
Rewards Points: 1,360
All the toilets in the building begin swirling the other direction.
The Following 2 Users Say Thank You to RePhase277 For This Useful Post:
Bad Electrician (05-28-2016), Jlarson (05-29-2016)
Old 05-28-2016, 02:15 PM   #3
MTW
Rewards Points: 9,936
If the ground is not connected back to the source somehow (via the neutral), then there is no fault path back to the source. In the event of a fault, the ground would then simply float with a lethal voltage on it until someone gets shocked and notices it, or something much worse happens.
backstay, emtnut and Majewski like this.
The Following 2 Users Say Thank You to MTW For This Useful Post:
mike883 (05-28-2016), samgregger (05-28-2016)
Old 05-28-2016, 05:47 PM   #4
Big nosed attic troll
Majewski's Avatar
Rewards Points: 2,774
Muder death kill. Complete anarchy....unless you never ever touch it or metal connected to it.
backstay and emtnut like this.
Old 05-28-2016, 05:48 PM   #5
Majewski's Avatar
Also this, like in the Simpsons.
Old 05-28-2016, 06:10 PM   #6
Rewards Points: 17,699
Whatever the you do, don't push the doorbell button. It is a danger beyond belief, a two wire and no ground hazard. Remember it only takes .006 amps of stray current to fib the heart muscle. All them current and past code panel members should be shot and then tossed into prison for allowing this tragedy to continue.
JOBS GROWTH SOARS
RECORD WORKING
UNEMPLOYMENT 50-YEAR LOW
Drudge Report
Old 05-28-2016, 07:35 PM   #7
MikeFL's Avatar
Rewards Points: 456
That ground rod is to return a lineside transient back to the POCO and keep it out of your house. Open that connection and you your house starts smoking.
Michael Gookin, President
GPS Timers
(833) GPS-TIME
Old 05-28-2016, 07:38 PM   #8
Gee I'm sorry to tell you this but electricity follows all paths back to the source. I don't agree with you're statement.
JOBS GROWTH SOARS
RECORD WORKING
Drudge Report
Old 05-28-2016, 09:06 PM   #9
Band Member
emtnut's Avatar
Rewards Points: 1,840
Do you mean the ground can't return to the Tx ?
Apart from the earth ?
What do you think would happen ?
Would some current make it back to the Tx ?
Is the soil moist/do we know the resistance of the ground ?
Are there ground rods at the service AND the Tx ?
What voltage are we talking about ?
You mentioned ground fault .... Is this an ungrounded system ?
Old 05-28-2016, 09:49 PM   #10
sbrn33's Avatar
Rewards Points: 3,490
Once again, a decent question from the OP and a bunch of asshole responses from the supposedly "smart" guys.
hardworkingstiff likes this.
The Following User Says Thank You to sbrn33 For This Useful Post:
jr360 (05-29-2016)
Old 05-28-2016, 10:00 PM   #11
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
Eh? Utility already grounds their trannys. Opening the customer ground doesn't change how the transformer operates, it just increases the local neutral-earth potential.
Even if it were to completely float an ungrounded system isn't gonna automatically smoke anything.
macmikeman and emtnut like this.
Always wear your gloves.
Old 05-28-2016, 10:19 PM   #12
spinninwheels's Avatar
Rewards Points: 1,167
So I presume this is a grounded system that has had the grounding conductor disconnected from the xo in the xfmr, or disconnected from the grounded conductor in the main panel. Yes?
Is the bonding system still complete to the neutral bus in the main panel, or the xo still connected to the bonding system?
When you say the ground touches the hot, do you mean the bonding conductor, or part of the bonded system; or do you mean the grounding conductor?
I remember when I was in school, and the instructors would always give these scenarios of possibly faults, and shock potential hazards.
life is a wild adventure or nothing - helen keller
spinninwheels is online now   Reply With Quote
Old 05-28-2016, 10:50 PM   #13
MikeFL's Avatar
Rewards Points: 456
I don't see the word transformer in my post.
GPS Timers
(833) GPS-TIME
Old 05-28-2016, 10:57 PM   #14
MikeFL's Avatar
Rewards Points: 456
Pretty bizarre interpretation there Pineapple.
Where in my post did I say it's the only path? The noodle is the primary path. A basic DC circuit shows us electricity takes all paths.
So where's your magic?
GPS Timers
(833) GPS-TIME
Old 05-28-2016, 11:06 PM   #15
A neutral conductor is to return a lineside transient back to the POCO and keep it out of your house. Open that connection and you your house starts smoking.
There will be multiple paths back to the poco and each will carry current according to its impedance, ground being one path provided the voltage is high enough to overcome impedance of earth. . If an ungrounded line conductor is delivering the surge it will follow all connected loads throughout the building and return on the neutral conductor (smoking the house in the process as it were...). If there is a good quality grounding system it will also deliver a portion of the current at elevated voltage thru the earth if the voltage is high enough to overcome the impedance of the earth medium. If there is metal water piping connected to the service neutral , that path also will deliver current back to the poco thru the other connected neutral wires of closeby connected electrical services.
JOBS GROWTH SOARS
RECORD WORKING
Drudge Report
Old 05-28-2016, 11:09 PM   #16
And since you call me pineapple, may I in return call you gladiolus flower?
JOBS GROWTH SOARS
RECORD WORKING
Drudge Report
Old 05-28-2016, 11:17 PM   #17
Bad Electrician's Avatar
Rewards Points: 4,969
If there is no neutral ground bond, assuming there is no utility grounded neutral such as in a SDS
You have an ungrounded system.
So the first fault is free. Fault to ground on A phase and you have a grounded A phase no harm no foul. Seen it done several times by hacks.
A-Gnd 0 VAC
B-Gnd 208
C-Gnd 208
A-N 120
B-N 120
C-N 120
A-B 208
B-C 208
C-A 208
If there is no fault the voltage to ground floats based on the impedance of the loads.
I was born with a plastic spoon in my mouth.
Old 05-28-2016, 11:25 PM   #18
MTW
A-Gnd 0 VAC
B-Gnd 208
C-Gnd 208
A-N 120
B-N 120
C-N 120
A-B 208
B-C 208
C-A 208
I don't think the OP is talking about a genuine ungrounded system, I think he's talking about having a grounded system but not bonding the neutral and ground together.
Old 05-28-2016, 11:51 PM   #19
Assuming no metallic connection between the main service and the utility transformer the same would apply.
Old 05-29-2016, 12:04 AM   #20
MTW
bond the ground conductor with the neutral conductor problem mike883 General Electrical Discussion 14 05-27-2016 01:21 PM
Ground fault, ship dwong General Electrical Discussion 0 05-22-2016 02:44 PM
Phantom Voltage? touchtester Residential Electrical Forum 9 04-25-2016 10:20 PM
not your normal neutral question Elec tricka Services and Service Equipment 15 04-15-2016 03:38 PM