JUST SHUT DOWN A 10 Story Office Building with a 20A Circuit - Electrician Talk - Professional Electrical Contractors Forum
Like Tree69Likes
Old 02-19-2020, 10:49 PM   #1
Default JUST SHUT DOWN A 10 Story Office Building with a 20A Circuit
Short circuit on a 20A lighting circuit and it shut down the whole building!!
What would have caused this to happen? Why did none of the other breakers in the series trip?
Guessing the trip settings on the existing main were dialed down way too low?
Needless to say, my guys had a stressful morning/
Hawaii Electrical is offline   Reply With Quote
Old 02-19-2020, 11:27 PM   #2
Rewards Points: 8,119
Phase to phase, or to ground? Spiked the CT's in the main sw. gear? But at the least I'd get the distribution, and main breaker's tested. What kind of building management system, or energy efficiency (load shed) scheme do they have?
circuitman1 and five.five-six like this.
joebanana is online now   Reply With Quote
Old 02-19-2020, 11:37 PM   #3
Not certain, it’s an older building. I don’t believe they have any type of management system. I am flying over Friday to take a look. The short was to ground...
Old 02-20-2020, 12:09 AM   #4
Rewards Points: 1,560
perhaps under normal circumstances the main breaker is already running close to the edge, and the lighting circuit short was just the straw that broke the camels back or so to speak !
so check current pull on your main.
Old 02-20-2020, 12:24 AM   #5
dronai's Avatar
Rewards Points: 439
Main breaker is a ground fault type that needs calibration ?
Old 02-20-2020, 12:29 AM   #6
Rewards Points: 3,432
If the 20 amp circuit was 277 volts and the service is 1000 amps or more then it's pretty normal to have a simple ground fault trip the main. I've seen it happen more than once.........
Old 02-20-2020, 01:04 AM   #7
Trained Monkey
TheLivingBubba's Avatar
Rewards Points: 1,536
I’ve done it a time or two working with 277.
Didn’t @MDShunk trip the main in a mall once?
Easy likes this.
I love everyone on Electrician talk...except that one guy.
TheLivingBubba is online now   Reply With Quote
Old 02-20-2020, 01:14 AM   #8
But why wouldn’t the branch circuit breaker trip first? Or the breaker feeding the lighting panel?
Old 02-20-2020, 03:03 AM   #9
Rewards Points: 1,546
A friend of mine did that at the County courthouse, took out a number of courtrooms.
Norcal is offline   Reply With Quote
Old 02-20-2020, 05:48 AM   #10
Rewards Points: 58
Well if the system is not coordinated, a fault on a branch circuit will take out an upstream Main...
shortcircuit2 is offline   Reply With Quote
The Following User Says Thank You to shortcircuit2 For This Useful Post:
Dennis Alwon (02-20-2020)
Old 02-20-2020, 06:14 AM   #11
Rewards Points: 2,320
I agree a coordinated study may not have been done and the setting was too low on the main.
I took out a 400 amp breaker and a 7 pole contactor with a short on a 20 amp circuit at an IBM plant in ny
dronai, glen1971, splatz and 2 others like this.
I can't help it if I'm lucky
Old 02-20-2020, 06:17 AM   #12
Rewards Points: 2,888
LOL at an IBM facility!?! That's priceless, they were known for running a ridiculously tight ship and letting you know about it constantly. I wonder how many of their engineers had eyes on this and it still made it past the goalie...
Old 02-20-2020, 06:51 AM   #13
Rewards Points: 1,166
When we do new construction...typically the engineer will specify the settings on the main breaker or on the Protective relays.....this often gets forgotten by the EC.
The instantaneous trip or the GFCI settings are probably at the minimum
telsa, splatz and Kevin_Essiambre like this.
Tonedeaf is online now   Reply With Quote
The Following User Says Thank You to Tonedeaf For This Useful Post:
Southeast Power (02-20-2020)
Old 02-20-2020, 07:33 AM   #14
Southeast Power's Avatar
Rewards Points: 9,262
They certainly have a coordination issue.
My conversations begin with something like:
"I want this event to be my responsibility but, this simple lighting short has exposed a deficiency in your circuit breaker coordination all the way to the main breaker. This will keep happening until it gets resolved"
Would you like us to commission a coordination study and present you with the remediation plan or do you have an engineer that can help you with it?
Old 02-20-2020, 07:43 AM   #15
MikeFL's Avatar
Rewards Points: 920
Fastest trip curve wins.
Michael Gookin, President
GPS Timers
(833) GPS-TIME
Old 02-20-2020, 08:04 AM   #16
Rewards Points: 578
Just like sperm.
readydave8 and MikeFL like this.
Old 02-20-2020, 09:55 AM   #17
Rewards Points: 990
Coordination study....
cdslotz is online now   Reply With Quote
Old 02-20-2020, 10:15 AM   #18
Rewards Points: 3,041
No coordination. Upstream fuses?
Old 02-20-2020, 11:08 AM   #19
Knotted Ropes Skeery
CoolWill's Avatar
Rewards Points: 2,180
The branch breaker and the panel feeder breaker are still thermal/magnetic. The main is GFP and set wrong.
Old 02-20-2020, 11:11 AM   #20
Rewards Points: 10,226
I’m not entirely sure the mechanics of why, I was probably not paying attention at that point of my apprenticeship but I do know that a 20A phase to phase short has the potential to drop an entire building GFI.
Tags
blackout, main breaker, power outage, short-circuit