When can low-voltage input and output cables be run in the same conduit? Is it 24 v thermostat wire or ac current or signal of less than 120 v
JWD111 is offline   Reply With Quote
The Following User Says Thank You to JWD111 For This Useful Post:
chrisjacob (08-06-2013)
Old 08-05-2013, 09:11 PM   #2
Sbargers's Avatar
Rewards Points: 79
I believe it can as long as it is 600 volt rared
Sbargers is offline   Reply With Quote
Old 08-05-2013, 09:14 PM   #3
BBQ
Salty Member
BBQ's Avatar
Need a lot more info than that
If other articles don't prohibit them being together the insulation has to be rated for the highest voltage in the conduit
The Following 2 Users Say Thank You to BBQ For This Useful Post:
8V71 (08-06-2013), micromind (08-05-2013)
Old 08-05-2013, 09:14 PM   #4
Rewards Points: 1,646
Not sure what you are asking? If the cables are for the T-stat then it should not matter. Sounds like all the wiring is t stat
I can't help it if I'm lucky
Old 08-05-2013, 09:17 PM   #5
B4T
Scotchkote Installer
B4T's Avatar
Rewards Points: 15,378
Recently we had a chat about running "bell wire" for control of ATS and it was said only THHN/THWN could be used in same conduit..
Old 08-05-2013, 09:20 PM   #6
ponyboy's Avatar
Rewards Points: 709
depends on circuit class and purpose. but as we know THHN is rated for 600v and I don't believe your run of the mill bell wire is
The Following 2 Users Say Thank You to ponyboy For This Useful Post:
Big John (08-05-2013), chrisjacob (08-06-2013)
Old 08-05-2013, 09:23 PM   #7
B4T
B4T's Avatar
It is rated 300V I think... but the voltage in the conduit is 240V..
Old 08-05-2013, 09:27 PM   #8
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
Which would be okay as long as the bell wire wasn't running a Class 2 or Class 3 circuit, but it probably was. Gotta check the power supply.
Always wear your gloves.
The Following 3 Users Say Thank You to Big John For This Useful Post:
360max (08-06-2013), Pete m. (08-06-2013), ponyboy (08-05-2013)
Old 08-05-2013, 09:39 PM   #9
ponyboy's Avatar
Rewards Points: 709
gotcha I didn't catch that thread and I was assuming 480v. but like john said it all boils down to circuit class
Old 08-06-2013, 02:37 AM   #10
Rewards Points: 25
Performing this process is just an wire insulation. I think there is no problem in running low voltage input cables and output voltage in the same conduit as long as the wires rating of insulation would match the voltage in conduit and all the wires were being rated correctly.
chrisjacob is offline   Reply With Quote
Old 08-06-2013, 06:26 AM   #11
BBQ
Salty Member
BBQ's Avatar
The NEC prohibits it in many cases regardless of insulation.
Old 08-06-2013, 12:25 PM   #12
Rewards Points: 502
Often, remote-control and signaling circuits that do not meet
the requirements of Class 2 or Class 3 circuits are classed as
Class 1 circuits by default. For example, a listed nurse call
system may contain a power supply with an output of 500
watts at 24 volts. Because this power supply exceeds the
maximum permitted output of a Class 2 power supply and
the output terminals are not marked to indicate the equipment
as suitable for a Class 2 power supply, the output circuit
wiring is classified as Class 1 and subject to all the
Class 1 circuit requirements.
Don't let fear be your guide!
Rockyd is offline   Reply With Quote
conduit run Ice5884 NEC Code Forum 48 02-21-2013 11:53 AM
conduit josh rsi NEC Code Forum 8 11-06-2011 01:00 PM
Conduit al13nw4r3LC76 Commercial Electrical Forum 10 07-08-2011 10:02 AM
2.5 v.s. 3 Conduit Cletis General Electrical Discussion 4 05-09-2011 07:37 PM
Conduit kev900 Commercial Electrical Forum 30 02-13-2011 04:37 AM