Default Main Nuisance Tripping
Just curious, how often do you see tripped main breakers on new installs where the EC forgot to adjust the trip units from factory min settings?
It seems to happen on projects I am involved with (design) all the time, these things aren't new. At a minimum change the Long time setting to what is on the drawings - if you don't know the rest submit an RFI.
Rant over
NJWVUGrad is offline   Reply With Quote
Old 01-25-2018, 05:26 PM   #2
Rewards Points: 7,575
Maybe you should attach a big red note to the drawings.
Old 01-25-2018, 07:18 PM   #3
Rewards Points: 199
This makes me remember a customer at one of my former employers who was a distributor of switchgear.
The customer was a gent from Fiji who was known to us as someone who did not read written instruction, so I spent some time to generate pictorial instructions for the set of air circuit breakers that he was purchasing for use in a sugar mill on one of the outlying islands.
About 3 months after the circuit breakers had been delivered, we got a call from our customer who was quite peeved that the circuit breakers which were now installed in the sugar mill were tripping whenever the mill machinery operated.
The circuit breakers had been supplied with the trip units set to 0.6 x rating. I asked him if they had read the instructions that we provided and got a long silence over the phone and the reluctant admission that they hadn't even made it out of their envelope.
I got to talk the sugar mill electrician through the setup over the phone, he thought it was hilarious.
MikeFL likes this.
Paulusgnome is offline   Reply With Quote
Old 01-25-2018, 08:38 PM   #4
Rewards Points: 338
Lol...I have placed in it notes, brought it up in construction meetings, still happens.
And every time someone throws a sh*tfit trying to figure out who to blame.
IMO it should be the first RFI an EC sends if it is not on the drawings.
The issue is that at the time of design - the engineer does not always know what make/model of MCB will be provided and what settings it will have . Some jobs we donít even see a submittal.
Old 01-26-2018, 01:06 AM   #5
Rewards Points: 1,972
There should be an Arc Flash Study and a Coordination Study.
Minimum setting for MOST GFPE relays (not on CB's) is 100 amps Instantaneous or .1 seconds.
As a general rule of thumb the GFPE should be set at 400 amps this gets you above the trip setting of most 20 and 30 amp CB's.
But we do not adjust unless there is something from an engineer.
On new construction, we suggest leaving set at minimum settings to minimize damage from ground faults
glen1971 likes this.
Old 01-26-2018, 09:53 AM   #6
Rewards Points: 3,986
I was working for an engineering firm and got called to a recently completed job where the main had tripped. I got there and saw that the trip settings were at the minimum. The building owner was there and not happy that his shop was in the dark and no one could work. I told him that the breaker was not properly set and was at the minimum settings. He was an engineer, and doubted what I told him, because he figured the breakers didn't leave the factory set at the minimum settings and I was just an electrician and he was an engineer. He called a testing company that sent a tech to adjust the trip settings. When he asked for the coordination study, they looked at me, and I said, it was never done as it was removed as a cost savings. The owner had forgotten about that one...
Most other jobs I've seen they usually get set during commissioning by either me or a testing company, using the settings on the single line, or by a separate document from the electrical engineer.
Old 01-26-2018, 10:25 AM   #7
Rewards Points: 3,006
Figure an 'engineer' would have realized you can't cut out certain parts of a job like that.
Old 01-26-2018, 01:16 PM   #8
Rewards Points: 416
We got called to a hotel that was having tripping issues for about 5 years. 2000 A Main tripped whenever someone backed over a parking pedestal. Turned out the main had GF protection that had never been set up. We had to get an engineering outfit to do a coordination study and calculate the proper settings. Good for us bad for hotel.
mitch65 is offline   Reply With Quote
The Following User Says Thank You to mitch65 For This Useful Post:
Bird dog (01-26-2018)
Main lug only vs. Main breaker panels mikedl361 General Electrical Discussion 21 11-30-2017 01:14 PM
Question about residential main breakers carryyourbooks General Electrical Discussion 21 10-13-2017 10:11 AM
Adding a main disconnect Chevys10zr2 Services and Service Equipment 15 09-06-2017 10:45 PM
Main breaker trips Glock23gp General Electrical Discussion 18 12-10-2016 09:39 PM
2017 NEC 555, minimizing gfi tripping class c PLCs, VFDs, Motors and Controls 4 08-16-2016 09:48 PM