Max breaker size for QO load center - Electrician Talk - Professional Electrical Contractors Forum
Like Tree14Likes
Old 11-07-2019, 05:59 PM   #1
NDC
NDC's Avatar
Rewards Points: 2,516
Default Max breaker size for QO load center
Does anyone know the max breaker size for a 200A QO push on panel?
I came across a 150A breaker that takes up 4 spaces but I've never used one. The panel doesnt list the max breaker size anywhere.
Its a QO-42m series T3B.
NDC is online now   Reply With Quote
Old 11-07-2019, 06:36 PM   #2
Knotted Ropes Skeery
CoolWill's Avatar
Rewards Points: 1,970
I believe 125 is as large as they go before jumping 4 spaces.
Old 11-07-2019, 07:45 PM   #3
Rewards Points: 8,085
Um.......I'll take 200 amps, for 200 Alex? What do I win?
JoeSparky likes this.
Old 11-07-2019, 09:21 PM   #4
NDC
NDC's Avatar
150amp breaker takes 4 slots but I thought some panels had maximums for branch circuit sizes. Is a 150 amp sub panel in a work shop fed from a 200amp main a bad idea? The home is has primarily gas appliances and the 150amp sub is for 2 car chargers at 48 amps each and they want room for expansion.
Old 11-07-2019, 09:26 PM   #5
Rewards Points: 3,414
As far as I know, if it's single phase, 125 is the max for 2 spaces and the adjacent spaces are limited to 40 amps.....I think........
They also make a 150 amp 2 pole that takes 4 spaces.
If it's 3Ø, the max for 3 spaces is 100 but they make a 110, 125 and 150 that takes 6 spaces. Same with the bolt on type.
A word of caution.......do not use a 2 pole 4 space breaker in a 3 Ø panel. If you do, when you turn it on, you'll have a bolted fault between A and C as well as A and B. If you put a 3 pole 6 space one in a single phase panel, it'll blow up too. These bolted faults will be at the line side, not the load side.
MTW likes this.
telsa (02-23-2020)
Old 11-07-2019, 09:27 PM   #6
Nothing wrong with it.
MTW likes this.
Old 11-07-2019, 09:58 PM   #7
Rewards Points: 60
Or just get a lug kit and run a full 200A over to the shop.
Sent from my SM-G970U1 using Tapatalk
samgregger and MTW like this.
Old 11-08-2019, 08:41 AM   #8
Band Member
emtnut's Avatar
Rewards Points: 2,556
Personally I'd do a quick load calc.
Add the 2 chargers and whatever expansion they want, and see what you get.
Bet you a doughnut that the inspector will ask for it anyways.
I'm sure it will be OK, unless the 'expansion' they want is for a big hot tub or another car charger.
NDC likes this.
Old 11-08-2019, 11:23 AM   #9
Rewards Points: 1,481
Could you just double lug the meter and forget the inside panel entirely?
Old 11-08-2019, 01:18 PM   #10
NDC
NDC's Avatar
Load calc comes in extremely low actually, under 68 amps.
Old 11-08-2019, 01:20 PM   #11
NDC
NDC's Avatar
Do these larger breakers normally come with a neutral lug? Or which neutral lug should I buy for this panel for the large size conductor. I'll be installing 1/0 copper teck90 to the shed.
Old 11-08-2019, 03:12 PM   #12
Service Call's Avatar
Rewards Points: 38
The only other worry would be the buss stab rating. It is additive of all breakers on the stab not the load.
Old 11-08-2019, 09:02 PM   #13
This is why they limit the breakers on the opposite side to 40 amps......I think it's 40.......but it is limited.
Old 11-08-2019, 09:03 PM   #14
Work Speaks for Itself
phamousgrey's Avatar
Rewards Points: 258
that is the million dollar question actually. the breaker your putting in umm, doesnt typically have a name, but most ppl would assume thats a subpanel breaker your installing as i dont know of any load from a single phase panel that a residential home owner would need to supply a 150a load for . .lmfao.
but yeah, as far as the neutral is concerned...so long as the subpanel and loads on the subpanel DO NOT require a neutral [theyd have to be 240v loads] then your fine with supplying them with just 2 conductors and a bond wire. But if your subpanel needs 120v for anything regarding those loads, you need a neutral, and originally that subpanel shouldve been a disconnect/feeder feeding those 240v loads anyways without a neutral.
uh, short version;
240v loads - disconnects fed from a feeder aka 2wire w/bond
120/240v loads- distribution panel/subpanel with 3wire w/bond
phamousgrey is offline   Reply With Quote
Old 11-08-2019, 09:11 PM   #15
The ones I've installed didn't come with a neutral lug but I'm pretty sure you can buy a lug that takes up more than one space on the bar and will accomodate a larger wire.
Old 11-08-2019, 09:25 PM   #16
Rewards Points: 38
It’s limited to the max rating of the stub. For instance, ITE buss rating is 110 amps (I believe). Someone puts a 30/50 quad on both sides of the panel. That one stub now has the potential to carry 160 amps. 80 both sides because that one stub is sharing a 30/50 on both sides.
So if a stub is rated for 125 and you put a 125 on it. Technically you really can’t add any more breakers to that stub.
It’s rated on the total of the breakers, not the load.
Old 02-23-2020, 02:39 PM   #17
Rewards Points: 951
Know you probably have this under control but for future reference a LK100AN lug kit allows for a 100A connection to the existing neutral bus. depending on the neutral bar layout it can end up taking up a significant number of spots once you land the wire.
Old 02-23-2020, 03:40 PM   #18
Rewards Points: 2,300
It all has to do with the load on the buss at one spot. I believe with 4 spots that load is distributed thru the stabs so as to avoid overheating. My guess is that it is ok but it must be written on the panel somewhere
I can't help it if I'm lucky
Old 02-23-2020, 04:00 PM   #19
I have 150 in my panel now that feeds a sub. It’s a Siemens breaker and it takes up 6 spots. 4 spots on one side and 2 spots across from it. I’ll be taking it out soon and installing a sub feed kit. That only takes up 4 spaces.
7635tools is offline   Reply With Quote
Old 02-23-2020, 04:38 PM   #20
joe-nwt's Avatar
Rewards Points: 3,546
They make a QO2200 plug on.
https://www.se.com/us/en/product/QO2...ka%2C-plug-in/
Neutral lug:
https://www.se.com/us/en/product/LK2...2-load-centers
Gnome likes this.