I am going to put in a 400 amp service for a residence. I will have a 15' conduit for my feeders for the meterbase. May I use 500 MCM XHHW aluminum conductors for the feed to the meterbase, even though they are rated at 350 amps? I thought I read in the NEC (can't find it) that the feeders may be sized to the load, not necessarily to the service ampacity. Am I correct? My inspector told me one time that those ampacity charts are figured on a 100' or longer run; shorter runs cans be smaller wire. help me out here.
John M. is offline   Reply With Quote
Old 07-27-2018, 08:58 PM   #2
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 1,038
315.10 B 7 or thereabouts.
also 230.23
what code cycle are you on.
Old 07-27-2018, 09:33 PM   #3
Chief Flunky
Rewards Points: 338
Ampacity charts are based on amperes. There is no length consideration. Resistance (technically impedance) in a cable is in ohms per foot. Cable heating is proportional to I*I*R per foot. Cooling is also per foot. Of course more cable means more voltage drop so that increases with length but current is current. The inspector is just plain wrong.
Old 07-30-2018, 07:04 PM   #4
Rewards Points: 159
No according to 310.15 B in 2014 you’d need 600 MCM XHHW AL for 83% of desired ampacity
Using 350 MCM copper for a 400 amp next week
MrsElectric is offline   Reply With Quote
Old 07-30-2018, 08:52 PM   #5
Southeast Power's Avatar
Rewards Points: 8,644
I've used parallel 4/0 Al on one 400amp service job and the next job, parallel AL 250s.
I'm not the engineer
Old 07-30-2018, 09:31 PM   #6
Speedy Petey's Avatar
Rewards Points: 596
We use 500mcm AL all the time for 320/400A residential services.
320 continuous is less than 350.
For sale Encore 250 MCM KCMIL Aluminum Tray Cable XHHW Stranded Service Entrance Powe Jramirez2408 Electrician Swap 8 06-05-2018 01:53 PM
Service feeders in crawlspace longer than 1.5 meter SReichy Canadian Electrical Forum 19 05-15-2018 02:46 AM
Service change - extending feeders Ontario Hangry Canadian Electrical Forum 49 02-10-2018 09:16 PM
Copper vs Aluminum for feeders Drsparky14 Services and Service Equipment 25 10-16-2017 11:49 PM
Residential 200 amp service with two 100 amp feeders dham206 General Electrical Discussion 18 08-17-2017 12:35 AM