I Got Three Receptacle Circuits That Are Going To Share A Neutral And I Used 12-2 But I Have 10 AWG That Im Going To Use For Homeruns Should I Change My Homerun Wire To 12 AWG That Way I Can Fit My Ground Homeruns In My 3/4 EMT
Eestrada94 is offline   Reply With Quote
Old 01-26-2018, 09:18 AM   #2
jw0445's Avatar
Rewards Points: 1,818
Are you working with 3 phase? What voltage? I can't make sense out of your question.
Old 01-26-2018, 09:25 AM   #3
zac
Rewards Points: 826
?Name:  giphy.gif
Signal1 likes this.
Old 01-26-2018, 09:29 AM   #4
Yea 3 phase 120/208 im asking cause the maximum conductors for 10 AWG Is 10 and I Got 3/4 EMT I had forgot about my ground when doing my calculations I Got 2 multiwire circuits going into that EMT
Old 01-26-2018, 10:53 AM   #5
Rewards Points: 18,181
Does the spec require that you run a ground wire in addition to your emt? . And don't forget that once you go over 8 current carrying conductors for size 10 cu wire then additional de-rating is required. Might be time to run some additional conduit...
JOBS GROWTH SOARS
RECORD WORKING
UNEMPLOYMENT 50-YEAR LOW
Drudge Report
Old 01-26-2018, 11:09 AM   #6
I Don't See It No Where on the plans but don't you have to run a ground how are the receptacles are going to be grounded and 2 circuits have gifs
Old 01-26-2018, 11:22 AM   #7
Coffee drinking member
Wirenuting's Avatar
Rewards Points: 6,532
What did your Journeyman say?
Is he nearby?
MikeFL likes this.
Old 01-26-2018, 11:23 AM   #8
Is this a side job? Your profile says apprentice. Apprentice's probably are unaware that emt is a legal and well used method of grounding circuits, although we have a whole bunch of so called electricians running about that don't even know that......... Watch how they will respond suddenly.
Apprentices don't usually understand de rating for conduit fill or temperature.
Apprentices are not supposed to be running jobs.
I'm not trying to spank you, but I am sure curious about why you are asking us these questions.
JOBS GROWTH SOARS
RECORD WORKING
Drudge Report
Old 01-26-2018, 11:30 AM   #9
MXer774's Avatar
Rewards Points: 608
For starters, the specs are typically a separate document (sometimes they are on the drawings).
It is allowable to use EMT as a EGC, as for grounding the devices, use a bonding pigatail from the device box. Also, GFI's do not care about the EGC, they monitor the neutral.
Personally, with 3/4" EMT, I TRY to limit my conductors to 3 Hots, 3 Neutrals, & 1 EGC.
Not being ugly here, but do you understand what & why you are installing?
MXer774 is offline   Reply With Quote
Old 01-26-2018, 11:54 AM   #10
Yea The Reason I'm Asking Is To Be Sure
Also The Circuits I have made I Need 6 Hot Conductors And 2 Neutrals and I'm trying not to run more conduit cause I have limited space to work with
Old 01-26-2018, 12:08 PM   #11
Rewards Points: 7,575
12/2 already has a ground conductor. Why are you running Romex in a conduit? And, you can't share neutrals on a GFI circuit.