MV cable shield - Electrician Talk - Professional Electrical Contractors Forum
Like Tree7Likes
  • 5 Post By triden
  • 1 Post By JRaef
  • 1 Post By triden
Old 03-17-2017, 11:08 PM   #1
triden's Avatar
Rewards Points: 382
Default MV cable shield
Does 4160v cable usually have a shield? Looking at a feeder that failed last week for unknown reasons (still investigating) and it only had a ground wire - no shield. Is this common? It was a TECK90 cable by Southwire - the stuff with the orange jacket.
http://www.southwire.com/ProductCata...rodcatsheetT37
Anyhow, cable was in a conduit and it blew the fuses. Phase-to-phase fault. Keep you updated when we find out more, but more than likely shielding would have saved it.
Old 03-17-2017, 11:29 PM   #2
Rewards Points: 3,986
Most of the 5 kv teck cable I've done is unshielded.. It has been in both the orange and black jackets... And the SOW I've used is also unshielded.. I think I'e only worked on few couple of shielded 5 kv cables..
glen1971 is online now   Reply With Quote
triden (03-18-2017)
Old 03-18-2017, 01:15 AM   #3
Rewards Points: 3,108
In my experience, 5KV cables (more than 1 conductor) are not shielded. Single conductor wire usually is shielded. If there's no neutral, the shield is the ground. If there is a neutral, it's the shield and a separate ground is pulled.
One exception is airport lighting wire (single conductor, 5KV) is not shielded.
Higher than 5KV, everything is shielded except the ground. It's basic 600 volt wire.
The Following 4 Users Say Thank You to micromind For This Useful Post:
frenchelectrican (03-18-2017), glen1971 (03-18-2017), telsa (03-18-2017), triden (03-18-2017)
Old 03-18-2017, 11:54 PM   #4
Rewards Points: 21,896
Sorry for delay on my reply on this one.,,
Most case I useally run into most of the MV cables useally unshielded but for single run of conductor it will be shielded ( pay attetion to bonding on shield part )
There is not too much differnce between the unshielded and shielded verison.
I useally run into alot of MV DLC ( diesel locomovite cable ) in my area.
Old 03-21-2017, 02:31 AM   #5
triden's Avatar
Rewards Points: 382
Found the problem. Cause of failure is still questionable, but most likely installation damage at this point.
Old 03-21-2017, 02:01 PM   #6
Rewards Points: 322
I'm not sure if this is one of those minor differences in the NEC vs the CEC, but the NEC here made shielding mandatory for field wiring over 2kV some time ago. The only place you can use unshielded cable in inside of gear, and in "industrial establishments where the conditions of maintenance and supervision ensure that only qualified persons service the installation", or where replacing existing MV unshielded cables (because it USED to be OK, so those installations are "grandfathered". There are other exceptions as per usual of course.
Big John likes this.
Old 03-21-2017, 11:19 PM   #7
That looks icky........lol.
An in-line splice on MV TEK cable is not much fun and it takes a long time. And your arms and hands will be sore for a while.........
Old 03-22-2017, 02:01 AM   #8
triden's Avatar
Rewards Points: 382
Not too familiar with the logistics of a TECK splice, but it was pulled through a buried conduit, so a splice was probably less than economical in this case. Fault was somewhere in the middle of the run. Paid the $40k and pulled a new feeder.
glen1971 likes this.
Old 03-22-2017, 02:06 AM   #9
triden's Avatar
Rewards Points: 382
Why did they make it mandatory? Was it because the shield might make the cable less likely to fault given external influence (metal, water, dirt, etc)? I couldn't imagine what it would be like to terminate a shielded 4160v cable into a peckerhead of a motor...that is unless they make them much larger these days.
Old 03-22-2017, 02:12 AM   #10
Rewards Points: 3,006
Ouch!
cable box reboot hockeydad20 Electrician Apprentice Forum 5 06-08-2017 03:07 PM
Running low voltage (48 volt) in cable tray RFguy Canadian Electrical Forum 4 02-13-2017 09:24 PM
Ground/Shield VFD cable termination Kris Wu General Electrical Discussion 8 07-07-2016 01:58 PM
No MC Cable Bushings swimmer Commercial Electrical Forum 32 07-04-2016 06:47 AM
stove cable max length oscar sparo General Electrical Discussion 0 03-21-2016 03:53 PM