NEC question - Electrician Talk - Professional Electrical Contractors Forum
CLICK HERE AND JOIN OUR COMMUNITY TODAY, IT'S FREE!
Go Back   Electrician Talk - Professional Electrical Contractors Forum > Electrical Forum > General Electrical Discussion


Like Tree7Likes
  • 1 Post By gpop
  • 1 Post By Whidbey
  • 1 Post By Dennis Alwon
  • 1 Post By NDC
  • 2 Post By Wiresmith
  • 1 Post By Wiresmith
Reply
 
Thread Tools Display Modes
Old 07-24-2018, 09:05 PM   #1
NDC
Senior Member
 
NDC's Avatar
 
Join Date: Jan 2016
Location: Ontario
Posts: 1,338
Rewards Points: 2,156
Default NEC question

Is it a code rule in the NEC to install only WR marked GFCI receptacles outdoors?
I'm in Canada and am just curious as it's not a code rule here. I was told this was a code rule in the states.

Last edited by NDC; 07-24-2018 at 09:23 PM.
NDC is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 07-24-2018, 09:09 PM   #2
Senior Member
 
Join Date: May 2018
Location: florida
Posts: 1,406
Rewards Points: 1,032
Default

Quote:
Originally Posted by NDC View Post
Is it a code rule in the NEC to install only WR marked GFCI receptacles outdoors?

2 ways to read that question

1/ can i install a wr receptacle inside
2/ can i install a receptacle thats not wr rated outside
Voltron likes this.
gpop is offline   Reply With Quote
Old 07-24-2018, 09:20 PM   #3
Member
 
Whidbey's Avatar
 
Join Date: Aug 2013
Location: Washington
Posts: 37
Rewards Points: 10
Default

Damp or wet location? 406.9


Sent from my iPhone using Tapatalk
MechanicalDVR likes this.
Whidbey is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 07-24-2018, 09:25 PM   #4
Moderator

 
Dennis Alwon's Avatar
 
Join Date: May 2009
Location: Chapel Hill, NC
Posts: 21,118
Rewards Points: 1,264
Default

Here is one statement

Quote:
(6) Weather-Resistant Receptacles. Weather-resistant receptacles
shall be provided where replacements are made at receptacle
outlets that are required to be so protected elsewhere in
this Code.
MechanicalDVR likes this.
__________________
They say I shot a man named Gray and took his wife to Italy
She inherited a million bucks and when she died it came to me
I can't help it if I'm lucky
Dennis Alwon is online now   Reply With Quote
Old 07-24-2018, 09:25 PM   #5
NDC
Senior Member
 
NDC's Avatar
 
Join Date: Jan 2016
Location: Ontario
Posts: 1,338
Rewards Points: 2,156
Default

Quote:
Originally Posted by gpop View Post
2 ways to read that question

1/ can i install a wr receptacle inside
2/ can i install a receptacle thats not wr rated outside

Are you what happens when people who are too smart become electricians?
tjb likes this.
NDC is offline   Reply With Quote
Old 07-28-2018, 01:49 PM   #6
Vacated
 
Wiresmith's Avatar
 
Join Date: Feb 2013
Location: United States
Posts: 1,454
Rewards Points: 2,844
Default

2017 NEC

406.9 (B)(1)wet locations
All 15 and 20 ampere 125 v and 250 volt non-locking type receptacles shall be listed and so identified as the weather resistant type
MechanicalDVR and NDC like this.

Last edited by Wiresmith; 07-28-2018 at 03:44 PM.
Wiresmith is offline   Reply With Quote
Old 07-28-2018, 03:27 PM   #7
NDC
Senior Member
 
NDC's Avatar
 
Join Date: Jan 2016
Location: Ontario
Posts: 1,338
Rewards Points: 2,156
Default

Quote:
Originally Posted by Wiresmith View Post
new in 2017 NEC

406.9 (B)(1)wet locations
All 15 and 20 ampere 125 v and 250 volt non-locking type receptacles shall be listed and so identified as the weather resistant type

Thanks this is what I was told as well. it's not code in Canada yet but I would assume it's going to be the case here soon.
So if you gfi the circuit at the panel, do you still need WR rated devices?
I see Cooper makes them http://www.cooperindustries.com/cont...5r_wrbr15.html

Last edited by NDC; 07-28-2018 at 03:31 PM.
NDC is offline   Reply With Quote
Old 07-28-2018, 03:43 PM   #8
Vacated
 
Wiresmith's Avatar
 
Join Date: Feb 2013
Location: United States
Posts: 1,454
Rewards Points: 2,844
Default

Quote:
Originally Posted by NDC View Post
Thanks this is what I was told as well. it's not code in Canada yet but I would assume it's going to be the case here soon.
So if you gfi the circuit at the panel, do you still need WR rated devices?
I see Cooper makes them http://www.cooperindustries.com/cont...5r_wrbr15.html
yep, i think the contact areas are more corrosion resistant
MechanicalDVR likes this.
Wiresmith is offline   Reply With Quote
Old 07-28-2018, 08:17 PM   #9
Old Grumpy Bastard
 
MechanicalDVR's Avatar
 
Join Date: Dec 2007
Location: "Old Dominion"
Posts: 59,296
Rewards Points: 1,008
Default

Quote:
Originally Posted by Wiresmith View Post
yep, i think the contact areas are more corrosion resistant
I'd say that's a pretty safe bet.
__________________
I'm as Christian as possible in the times we live in.

Always just a stallion in a china shop
MechanicalDVR is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
question about code book 2-308 mike883 Canadian Electrical Forum 5 04-01-2018 07:41 PM
I would like to ask a real higher-up engineer a question HackWork Milbank Manufacturing 37 02-09-2018 05:20 PM
How would you go about finding the answer to this code question? Dizzykidd NEC Code Forum 8 09-02-2017 07:43 PM
Odd question about residential 120V smoke detectors Bzzzzzt General Electrical Discussion 20 08-26-2017 10:46 PM
Code Question ? louconstant Electrician Apprentice Forum 13 08-10-2016 10:33 AM


All times are GMT -4. The time now is 10:22 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com