I don't do this much. I looked online but get conflicting help. Here's my specs.
The load is 240 VAC, 29 amps. I have a shy 208 available volts. This is single phase.
John M. is online now   Reply With Quote
Old 02-11-2019, 06:42 AM   #2
Rewards Points: 524
Is there nobody home?
Old 02-11-2019, 06:45 AM   #3
CoolWill's Avatar
Rewards Points: 1,694
You size it by the difference in voltage times the amps. So,
240-208 = 32
32 x 29 = 928
1 kVA transformer.
brian john, splatz and nomadapower like this.
Old 02-12-2019, 08:07 AM   #4
Rewards Points: 524
Is the secondary voltage determined by the voltage increase that I need?
Old 02-12-2019, 08:13 AM   #5
CoolWill's Avatar
Yes, you want a 16/32 volt secondary.
The Following 2 Users Say Thank You to CoolWill For This Useful Post:
John M. (02-12-2019), nomadapower (02-12-2019)
Old 02-12-2019, 11:22 AM   #6
Rewards Points: 16,730
Also when you do the connection for autotransformer or Buck and Boost set up please make sure you follow the wiring connection diagram if they come with it due there is many way to do that so make sure you get the manufacter wiring connection diagram to make sure you are right on the spot.
and yuh you only need one BB that it. ( on single phase but three phase you need two or three depending on the set up )
the last thing you have to be aware is line to neutral voltage will be different after the BB set up. so if you have line to neutral loads be aware of it.
Old 02-12-2019, 05:16 PM   #7
Rewards Points: 1,392
the last thing you have to be aware is line to neutral voltage ON THREE PHASE will be different after the BB set up. so if you have line to neutral loads be aware of it.
Fixed it for you
Old 02-12-2019, 06:15 PM   #8
Fixed it for you
yuh but I am aware it do affect the line - neutral connection only after the buck/Boost transformer on both single and three phase verison.
Cable sizing for 3 Phase Induction Motor Electrical-EE PLCs, VFDs, Motors and Controls 16 10-21-2017 05:04 AM
Breaker Sizing Heater 746 Watts Canadian Electrical Forum 21 09-18-2017 12:23 AM
Auto transformer Sizing JPRO2 General Electrical Discussion 6 12-14-2016 06:04 PM
transformer sizing. jsmart84 General Electrical Discussion 4 09-12-2016 05:22 PM
Transformer neutral bond sizing (paralleled secondary) haltonelectrician Canadian Electrical Forum 27 06-19-2016 06:21 PM