Neutral Question - Electrician Talk - Professional Electrical Contractors Forum
Like Tree12Likes
  • 3 Post By HackWork
  • 5 Post By Southeast Power
  • 4 Post By eddy current
Old 03-22-2019, 03:27 PM   #1
Rewards Points: 44
Default Neutral Question
Hi gang, been a hot minute!!
I have a scenario where we are running a 50 amp 3-ph circuit that requires no neutral, however we are incorporating a few 120v control devices (contactor/timer) which will be tapped and fused-down from one of the legs (2 amps). Question is, can I run a #12 neutral with this circuit?
Ideally I would get a 208v contactor and timer and not utilize a neutral, however client has already purchased these items and insists on using them.
electricut is offline   Reply With Quote
Old 03-22-2019, 03:43 PM   #2
Rewards Points: 391
If you are going to run a #12 neutral, why not just run a normal 120V 2-wire circuit instead of tapping and fusing it?
Service Call, Helmut and Bird dog like this.
Old 03-22-2019, 04:28 PM   #3
Rewards Points: 44
Well, there will be a control box, and client is adding all necessary items too, which means less wire/labor (250ft) on my end. We are basically taking over a project that they intended on doing in-house so trying to make it as painless as possible. They will do the control side.
Mainly, I want to know from code perspective whether it would be compliant...I can't see a reason it isn't so as long as it's fused within its ratings.
Old 03-22-2019, 04:33 PM   #4
Rewards Points: 7,520
No. Well not per the Canadian code you can’t.
electricut (03-22-2019)
Old 03-22-2019, 04:33 PM   #5
Fishbulb's Avatar
Rewards Points: 110
No. It may not be smaller than the EGC.
Fishbulb is offline   Reply With Quote
The Following User Says Thank You to Fishbulb For This Useful Post:
Old 03-22-2019, 04:35 PM   #6
Rewards Points: 44
This makes sense. Do you happen to know code ref?
Old 03-22-2019, 04:41 PM   #7
86 45 20
Southeast Power's Avatar
Rewards Points: 7,876
Use two legs, and a transformer with nice built in fuse block.
Old 03-22-2019, 04:45 PM   #8
Rewards Points: 44
Yeah, there are definitely better options like what you are saying, but they are gonna use what they already purchased, which has no xfrmr included.
Old 03-22-2019, 04:46 PM   #9
Rewards Points: 391
I am not understanding why you would pull 1 #12 but not 2 of them. Why have to tap and fuse it?
Old 03-22-2019, 05:08 PM   #10
Tell them they will need to buy one. For only 2 amps, it will be small, probably fit in the same box as the contactor, and not cost much.
Do it right
Old 03-22-2019, 05:50 PM   #11
Fishbulb's Avatar
Rewards Points: 110
Well, shoot. Now that you've asked I can't locate it. For feeders it's easy enough and maybe that's what I was thinking of. Right now I can't find anything to justify a smaller neutral on a MWBC at all. I will keep looking (for my own sanity as well, I was pretty certain of this) but in the meantime it might be best to ignore what I said.
Old 03-22-2019, 06:39 PM   #12
Bird dog's Avatar
Rewards Points: 1,322
Are you thinking about the service neutral?
Old 03-22-2019, 06:47 PM   #13
Rewards Points: 16,780
There are a couple good answer posted in the fourm in here and for myself .,,
I would get a properly sized transformer with fused block on it and be done with it and not have to mess with neutral conductor at all.
Oh by the way # 12 awg on 50 amp circuit is a no go ( look up at art 430 and 440 that is a starting point and there are few other codes in the mix it will pop up )
Old 03-22-2019, 06:50 PM   #14
Just keep in your mind the service neutral and feeder neutral is different item to deal with it.
Old 03-22-2019, 07:40 PM   #15
Rewards Points: 1,160
I have not seen a section for branch circuit neutrals and I have brought this up a few times.
It makes sense to me that in the scenario of a short circuit (hot to neutral) that the neutral should be able to carry the fault. This is why there is a minimum size equipment grounding conductor so why would a neutral be allowed to be smaller than the equipment grounding conductor?
I can't help it if I'm lucky
Old 03-22-2019, 08:26 PM   #16
Our code refers to the white wire as a grounded conductor and it needs to be sized to carry the load. An actual neutral is only a conductor that carries the unbalanced load and can be smaller than the ungrounded because of that. It can never be smaller than the bond though.
Hot Neutral Question Quenth88 Canadian Electrical Forum 1 01-15-2019 06:23 PM
3 phase 120/208V with a grounded neutral question jprebb Commercial Electrical Forum 16 05-21-2018 10:17 PM
Question about sharing a neutral ChunkyDrummer NEC Code Forum 17 09-10-2016 06:37 PM
interesting question: what if there is no bonding between ground and neutral? mike883 General Electrical Discussion 35 05-29-2016 02:18 PM
not your normal neutral question Elec tricka Services and Service Equipment 15 04-15-2016 02:38 PM