Am building a new service wherre the AIC is 31,000. I need (3) 200 amp disconnects for this. I usually use breakers, but is there an economical breaker for this AIC or do I need to go to a fusible disconnect?
John M. is online now   Reply With Quote
Old 12-02-2017, 08:19 AM   #2
Rewards Points: 1,360
AIC is a rating for a breaker or fuse, not the actual current... just a minor nit.
So where is this 31000 amps available? At the transformer? What is the wiring method between the transformer and disconnects? Copper, aluminum, PVC, rigid, overhead, single phase, three phase, 208, 480, etc?
hardworkingstiff likes this.
Old 12-02-2017, 08:31 AM   #3
Rewards Points: 14,714
I haven't priced anything in ages, but if you are using 3 panels with mains, probably a series rated panel with a fusible main would be the least expensive (at least it used to be that way).
If you have a single disconnect for the whole service, past pricing for me would be a fused disconnect over a breaker.
All that being said, I'd try to upsell the breaker install if you find the correct one.
chicken steve likes this.
Old 12-02-2017, 12:36 PM   #4
Retired Account
Rewards Points: 14,650
The RK fuses have the highest AIC for the $$$
Old 12-02-2017, 03:19 PM   #5
Rewards Points: 21,898
For that high of AIC typically RK fuse useally do it for pricewise vs the high AIC rated breakers are.
but the actual numbers will varies a bit depending on distance and type of conductor and type of transfomer so the number can be reduced somehow
in this case you may need a EE to stamp the correct info before you get too far with the OCPD AIC rating. that the inspectors may want to see that details. so be prepared for that.
60 to 100 amp service change question Chevys10zr2 Residential Electrical Forum 9 09-07-2017 02:51 AM
Service question chappy Residential Electrical Forum 19 04-23-2017 08:06 AM
Service question detspark Services and Service Equipment 6 04-11-2017 05:16 PM
Service change up question squirrelshot General Electrical Discussion 12 01-17-2017 12:47 PM
Help with 400A 3PH 120/208 service question MacCallum Electric Canadian Electrical Forum 7 09-27-2016 08:05 AM