Hi,
I have an existing 120/240V 200amp main panel. I did a 120/240V 90amp sub panel connected to the main. The city's inspector asked me what is the sub panel AIC rating. Where can I find the AIC rating? Is the sub panel AIC rating same as the main panel?
keithxie is offline   Reply With Quote
Old 06-24-2019, 06:40 PM   #2
MikeFL's Avatar
Rewards Points: 846
You need to fill out your profile before we're allowed to advise you.
Michael Gookin, President
GPS Timers
(833) GPS-TIME
Old 06-24-2019, 08:26 PM   #3
Rewards Points: 21,898
What kind of contractor are you running now .?
I know California have few verison of contractor type
the answer will varies depending on which type of contractor you are.
Old 06-24-2019, 09:38 PM   #4
DashDingo's Avatar
Rewards Points: 22
Originally Posted by keithxie View Post
Hi,
On the 90 amp breaker.
Assuming you put a 90 amp breaker in the 200 amp main panel to feed the sub panel.
DashDingo is offline   Reply With Quote
Old 06-24-2019, 09:58 PM   #5
Rewards Points: 2,015
Schneider says the AIC of the panel is the value of the branch circuit breaker with the lowest AIC rating.
Old 06-24-2019, 11:45 PM   #6
Rewards Points: 788
Some fuse manufacturers developed an app for calculating the AIC for equipment. I have one by Eaton that I forgot how to use.
Old 06-25-2019, 12:45 AM   #7
Rewards Points: 3,360
As noted above, the lowest rating of any breaker is the AIC of the entire panel.
I've never seen a modern breaker that has a rating of less than 10,000 amps so that would be the rating the inspector is looking for.
What feeds the 200 amp panel? It's very rare for a basic resi 200 amp panel to be fed with a source capable of more than 10,000 amps but it can happen.