No Equipment Ground - Sub-Panel - Electrician Talk - Professional Electrical Contractors Forum
Like Tree6Likes
Old 04-04-2019, 05:22 PM   #1
Rewards Points: 321
Default No Equipment Ground - Sub-Panel
I'm working on a house that has a sub panel (located in the same house) that is fed from a 6-3 NM cable that doesn't have an equipment ground. Was this allowable at any time? Do you bond the grounds from the branch circuits to the neutral at the sub-panel in this case (as long as there are no other parallel paths back to the main panel) or do you have to run a separate equipment ground? Or, do I need to install new feeders with an equipment ground? I have seen this several times at several places. I thought there was an exception to a general rule regarding this somewhere but I am having trouble finding it. Any help will be appreciated.
Paul S. is offline   Reply With Quote
Old 04-04-2019, 05:27 PM   #2
Russian Bot
Helmut's Avatar
Rewards Points: 3,765
6-3 NM should have a ground with it.
Should be black, red, white and a bare copper ground.
Alright, Alright, Alright... I'll tell you what to do. Go that way, reeeeeeeeeally fast. If something gets in your way......turn.
Old 04-04-2019, 05:27 PM   #3
Rewards Points: 487
I have seen this too. I think it might have been allowed at one time long ago, but I am not sure.
I will usually recommend installing a new feeder and panel.
Not the old stuff.
brian john likes this.
Paul S. (04-04-2019)
Old 04-04-2019, 05:28 PM   #4
Rewards Points: 1,175
I think it was acceptable pre 87'-ish, if it is existing and you are running new circuits from it, you would attach your ground and neutrals to the same bar just as you would in a main panel.
The Following User Says Thank You to samgregger For This Useful Post:
Old 04-04-2019, 05:31 PM   #5
Russian Bot
Helmut's Avatar
Not the old stuff.
No kidding. More like SE cable then?
Old 04-04-2019, 05:51 PM   #6
Rewards Points: 321
Not the old stuff.
The problem here is that I believe there are parallel paths to ground so I don't want to just bond the neutral to the grounds. Like you said, I think recommending new feeders is really the best option here. I asked my inspector about bonding the ground bar to the grounding electrode/bond conductor, which happens to be close by, and he kind of hemmed and hawed about it. He said that we both know that would perform the task needed but he didn't really think it was code compliant.
Old 04-04-2019, 05:55 PM   #7
Bird dog's Avatar
Rewards Points: 1,366
You mean 6-3 with gnd.
Old 04-04-2019, 06:01 PM   #8
Rewards Points: 321
No, this is older NM cable with no equipment ground; just 3 wires, red, black, and white.... No equipment ground.
The Following User Says Thank You to Paul S. For This Useful Post:
Bird dog (04-04-2019)
Old 04-04-2019, 06:06 PM   #9
Rewards Points: 487
Think of the old 14-2 romex that didnít have an EGC yet.
Paul S. likes this.
Old 04-04-2019, 06:14 PM   #10
Bird dog's Avatar
Is it cloth & rubber insulation?
Old 04-04-2019, 06:24 PM   #11
Rewards Points: 321
In this case, it's rubber... I often see this type of wiring on older dryer circuits and range circuits too.
Old 04-04-2019, 06:29 PM   #12
Bird dog's Avatar
I'd replace it. Don't give the customer the option of bonding the neutral.
Old 04-04-2019, 06:34 PM   #13
Rewards Points: 321
It seems to me that there was exception in the code somewhere for this kind of situation but I can't find it right now... However, I'm not looking that hard as I have a bunch of other paperwork in front of me that also needs attention. (Whew! ... lot's to do.)
Old 04-04-2019, 06:42 PM   #14
Russian Bot
Helmut's Avatar
Approx how old is this wiring?
1950?
Old 04-04-2019, 06:54 PM   #15
Rewards Points: 321
1950?
I'm guessing it's from the 80's, but I'm not positive about that.
Old 04-04-2019, 08:17 PM   #16
Rewards Points: 1,496
I'd bet Pre 60 something maybe 50ish Definitely pre 1970
Old 04-04-2019, 08:48 PM   #17
Rewards Points: 280
Early 60's.
Old 04-04-2019, 10:02 PM   #18
CoolWill's Avatar
Rewards Points: 2,022
I don't think there was ever a provision in the code that allowed this for panels in the same structure. The only places I can think where the neutral could be used as a ground is at the service equipment, on dryers and ranges, and at remote structures. I have seen it done too, but I think it's just people getting away with it.
Short of replacing the cable, one fix might be to turn it into a 120 volt subpanel if practical, then you'd have all the wires necessary.
Paul S. likes this.
I'm With Her! Hillary 2016
Paul S. (04-05-2019)
Old 04-04-2019, 11:17 PM   #19
Rewards Points: 15,935
40's and fifties. If this one you saw had a sort of cloth material for the outer sheath. Sounds like it did it the internal wires were rubber covered. When they did do it this way , it wasn't really legal code wise but common. Usually there would be a #6 bare copper running out of the sub panel to the water heater cold and bonded to the metal of the sub panel.
Agree with the frames of ranges and dryers part. That was legal, in my lifetime.
Paul S. likes this.
Old 04-05-2019, 09:01 AM   #20
jw0445's Avatar
Rewards Points: 1,646
Just run a ground wire using the same route. NEC 300.3(B)2
(2) Grounding and Bonding Conductors. Equipment grounding conductors shall be permitted to be installed outside a raceway or cable assembly where in accordance with the provisions of 250.130(C) for certain existing installations or in accordance with 250.134(B),
Sparkychick likes this.
Tags
ecg, equipment ground, sub panel
Panel Relocation and Grounding nkmacualay General Electrical Discussion 8 09-13-2018 05:25 PM
Old Zinsco Service Panel - No ground? 818han General Electrical Discussion 3 08-24-2018 08:06 PM
Radon fan tripping GFCI WronGun Residential Electrical Forum 52 07-15-2018 08:14 PM
Instrument to record the operation of equipment in electric panel Signode Services and Service Equipment 16 04-19-2017 09:00 PM
equipment ground conductor for PV arry? gabriel*PV NEC Code Forum 5 02-08-2016 11:46 AM