for pad mounted transformer secondary side, pulling wire no ground wire required? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree7Likes
  • 2 Post By Switched
  • 4 Post By Cow
  • 1 Post By Big John
Old 04-08-2017, 09:44 PM   #1
Rewards Points: 540
Default for pad mounted transformer secondary side, pulling wire no ground wire required?
anybody has this kind of experience about the pad mounted transformer:
here is the situation, this pad mounted transformer is in the street, its primary side is from the hydro, around 25,000V, and secondary side is going to a building's main switch gear,
the question is when we pull the wire for the switch gear, do we need to pull the ground wire for that?
or just three phase plus neutral? I mean no ground wire required, the neutral is the ground wire as well in this situation?
for pad mounted transformer secondary side, pulling wire no ground wire required?-4624935949_5d81aacfbe_b.jpg   for pad mounted transformer secondary side, pulling wire no ground wire required?-maxresdefault.jpg
mike883 is offline   Reply With Quote
Old 04-08-2017, 09:56 PM   #2
Switched's Avatar
Rewards Points: 10,268
You guys pull your own wiring from the utility owned transformer?
I can't say as to Canada, but we would not pull a ground from a utility transformer to the gear, just the hots & neutral. Your grounding begins at the gear and downstream of it.
lighterup and telsa like this.
Old 04-08-2017, 11:17 PM   #3
triden's Avatar
Rewards Points: 382
Why are you pulling it? Typically it's the contractors responsibility to install the conduit from the transformer to the gear where Hydro will then pull the conductors. No ground typically needed as grounding is established at your service entrance.
If this were a customer owned service with a unit sub, that would be different.
Old 04-08-2017, 11:30 PM   #4
Dash Dingo's Avatar
Rewards Points: 318
No ground
Dash Dingo is offline   Reply With Quote
Old 04-09-2017, 12:04 AM   #5
Cow
Rewards Points: 5,098
We work with a few different power companies. One of them has us pull to the padmounts.
And no, you do not need a ground wire. There are no ground wires until your main disconnect. Down here in the US, everything is bonded with the "grounded" conductor up to the service disconnect. After that you have an equipment grounding conductor.
Old 04-09-2017, 02:38 AM   #6
Southeast Power's Avatar
Rewards Points: 9,040
I asked that question and the cable splicer told me that I could install a ground wire if I was required to but, they have no place to connect it.
Old 04-09-2017, 08:15 AM   #7
Rewards Points: 23,880
Ground your own equipment not the utilities.
Old 04-09-2017, 08:36 AM   #8
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
Yep, there's a big padeye on XO and a bonding strap to a single frame ground bolt.
You can run an EGC all you want, but at the end of the day when they bond it at the transformer and then you rebond it at the service all you've done is create a poorer parallel neutral path.
Southeast Power likes this.
Always wear your gloves.
Old 04-09-2017, 09:24 AM   #9
Rewards Points: 4,102
Hydro pulls the secondary conductors? Not on any that I've done..
Any padmount transformers I can remember prepping for, we installed the ground grid, rods around it, tails into the transformer, 4" PVC with long radius 90's to the location determined by the utility and all the secondary conductors. When it came to terminating, we did all the secondary terminations and since the last 20ish years have been industrial, it has all been teck, and the cable grounds have been terminated. If I remember the specs right from my time on the engineering side, there was always a ground conductor called for in the underground PVC.
Old 04-09-2017, 01:22 PM   #10
triden's Avatar
Rewards Points: 382
Hydro here pulls them all the time. That's why their service entrance spacing requirements are crazy - 20" of width in a switchgear/mcc section to pull and terminate the secondaries. Guess every province is different...good to know. Hydro here also installs and supplies the triplex/quad for overhead services. Does Transalta do the same?
Transformer neutral bond sizing (paralleled secondary) haltonelectrician Canadian Electrical Forum 27 06-19-2016 06:21 PM