Can I have some one help me be a little less ignorant? I need to use 4 750kcmil copper conductors to run 225 amps 1000' to a 480v panel 3 phase 4 wire. I want to reduce the cost by using smaller wires in parallel. What formula can I use to calc the wire size. Or does anyone know this off of the top of their head?
edster is offline   Reply With Quote
Old 01-24-2015, 03:41 PM   #2
freeagnt54's Avatar
Rewards Points: 66
Chapter 9 table 8 in 2011 nec.
freeagnt54 is offline   Reply With Quote
Old 01-24-2015, 03:50 PM   #3
Rewards Points: 1,224
Using parallel conductors to reduce voltage drop does not reduce the amount of copper you need. If the voltage drop calc shows you need 750kcmil, then you will need parallel conductors that total at least 750 kcmil, for example three sets of 250 kcmil.
Old 01-24-2015, 04:00 PM   #4
Rewards Points: 60
That is a good point what Don stated. You don't use the ampacity chart to calculate the parallel size in this case because we are dealing with voltage drop.
If, for instance, you needed a conductor that carried 475 amps as 750 kcm does then if amp. was all we were looking for then we could use parallel 250 kcm (2 sets not 3) but because of the voltage drop the cm must be equal so as Don stated 3 sets of 250 KCM would equal the 750 KCM
Old 01-24-2015, 04:36 PM   #5
Retired Account
Rewards Points: 14,650
VD calculator
Old 01-24-2015, 09:25 PM   #6
Cow
Rewards Points: 34
That will be a fortune, all our long runs like that are done in aluminum.
The Following 2 Users Say Thank You to Cow For This Useful Post:
Bad Electrician (01-25-2015)
Old 01-25-2015, 12:57 AM   #7
Rewards Points: 2,950
I couldn't agree more. Heck, I use aluminum for anything over 50'. I couldn't imagine using copper for a 1000' feeder.
Old 01-25-2015, 07:28 AM   #8
Retired Account
Iirc, there's an engineered pull pressure one should not exceed, or damage may occur
I would imagine the weight of it alone would require multiple pull points, lest it defeat a tugger.
Weight is probably the best reason to parallel...
just my wimp opinion
Old 01-25-2015, 09:27 AM   #9
Rewards Points: 4,138
We did 3 runs of 3C500 5kv teck on a job that was 285 meters (935').. I think for the one half we had 16 guys on it... There was 2 runs on one reel and when we pulled the first one in, it was 7 meters short... Fortunately it was a quick fix and became long enough, but we had quite a bit of excess on the second one...
We had another one on that site that was a 4C2/0 that was close to 500 meters (1,640') if I remember right.. It was feeding a light and a heat trace circuit on a well...
Old 01-25-2015, 09:40 AM   #10
dronai's Avatar
Rewards Points: 441
Quick fix ??
The Following 3 Users Say Thank You to dronai For This Useful Post:
CADPoint (01-25-2015), hardworkingstiff (01-25-2015), MTW (01-25-2015)
Old 01-25-2015, 10:15 AM   #11
Retired Account
16 man stretcher?
The Following 2 Users Say Thank You to chicken steve For This Useful Post:
dronai (01-25-2015), glen1971 (01-25-2015)
Old 01-25-2015, 10:45 AM   #12
Rewards Points: 1,004
I would offer the owner a big deduct to use Alum.....then pocket half the savings
cdslotz is offline   Reply With Quote
Old 01-25-2015, 10:59 AM   #13
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
I would step the voltage up on the feed end and reduce it down on the other end. Two small transformers will save you alot of copper.
Old 01-25-2015, 11:23 AM   #14
Originally Posted by dronai View Post
Quick fix ??
The cables came from the west and went along the full width of the north side of the building, then went south for about 30' then turned back to the west and inside for about 20'... We added two lengths of tray from the north wall straight inside above the gear and cut our distance down by quite a bit.. Sold it to the engineers on cable tray loading and got the fix ok'd... The boss wasn't ok initially with the scrap tails, but after he heard the reason why, or fix for it and that otherwise we'd have had a 275 meter scrap piece, he was ok with it..
The Following 2 Users Say Thank You to glen1971 For This Useful Post:
dronai (01-25-2015), hardworkingstiff (01-25-2015)
Old 01-25-2015, 11:32 AM   #15
Originally Posted by mcclary's electrical View Post
I would step the voltage up on the feed on and reduce it down on the other end. Two small transformers will save you alot of copper.
It was a 4,160 volt feeder off the generator to a 4,160 volt distribution panel in another MCC building. Adding 4 transformers wasn't an option, mainly for real estate at each building, and I'm guessing the cost would have been close...
Old 01-25-2015, 12:02 PM   #16
Rewards Points: 250
He's talking to the OP
local134gt is offline   Reply With Quote
Old 01-25-2015, 12:28 PM   #17
Cow
Rewards Points: 34
I don't see the advantage of bumping a 480v feeder to what, 600v? That isn't much gain. Installing transformers that burn Kw's all day long as well as extra disconnects/OCPD's make this less than ideal in the long run.
I'd pull aluminum and be done with it.
samgregger (01-25-2015)
Old 01-25-2015, 02:40 PM   #18
Not to mention the additional terminations and installation time of 2 more transformers...
Old 01-25-2015, 07:30 PM   #19
Cl906um's Avatar
Rewards Points: 1,206
Agree.
Old 01-25-2015, 07:56 PM   #20
Cl906um's Avatar
Aluminum is worse for v.d. Plan on running twice the conduit, and pull twice the runs.
Parallel feeders to an MCC glen1971 Canadian Electrical Forum 16 04-22-2014 08:03 AM
Capacitor in parallel with feeders Sparky305 General Electrical Discussion 14 11-30-2013 10:17 PM
Parallel Feeders Kryptes General Electrical Discussion 16 08-26-2013 01:17 PM
Parallel Feeders Help stuiec Canadian Electrical Forum 16 08-06-2012 10:59 PM
Parallel feeders himself General Electrical Discussion 12 07-15-2011 07:17 PM