I attempted to install GFCI protection on a Hayward pool pump the other day using a Cutler Hammer BR GFCI breaker. The pump is computer controlled and would go through the pre-startup sequence with no problem. However, as soon as the pump itself tried to start, the GFCI breaker would trip with a ground fault. After consulting with Hayward, I discovered that they require that a Siemens GFCI breaker be used to provide ground fault protection, but they could not or would not say why. The pump works fine with a Siemens QF220 GFCI breaker.
Can anyone shed some light on why a Siemens breaker works and a Cutler Hammer breaker does not when both at ID'd to trip with a 5 ma fault?
czars is offline   Reply With Quote
Old 02-07-2015, 04:01 PM   #2
Rewards Points: 1,762
I cannot think of a reason why one would work and not the other. What would you do if you had installed a sq.d panel or a ch cutler hammer panel?
Old 02-07-2015, 07:03 PM   #3
Rewards Points: 193
Wink
One would likely have to do what I did - install a small Siemens sub panel with a Siemens GFCI breaker.
Old 02-07-2015, 07:12 PM   #4
Retired Account
Rewards Points: 14,650
I'm at a loss Czar, can't imagine one manufacturer insisting on some other manufacturer's exclusive OCPD here......~CS~
Old 02-07-2015, 08:12 PM   #5
Rewards Points: 44
Use a circuit breaker disconnect with a GFCI breaker it's a lot cheaper then an entire panel change / add
FF301 is offline   Reply With Quote
Old 02-07-2015, 08:29 PM   #6
Rewards Points: 193
Looks to me like there is some difference in the operation of the different GFCI breakers such as a delay in the starting of the GFCI operation or something else that the manufacturers of the breakers and Hayward pumps won't admit to.
Old 02-07-2015, 09:22 PM   #7
Rewards Points: 193
FF301 - Good idea. Can you ID one compatible with Siemens breakers?
Old 02-08-2015, 05:43 PM   #8
Rewards Points: 44
Siemens W0408L125SPA60
125 amp rated. 4 spaces, includes 60 amp 2 pole gfi brkr
just install the size brkr you need. (return 60/2 brkr to HD for a credit)
it's advertised as a spa disconnect but you can use it for whatever.
Old 02-09-2015, 07:55 AM   #9
Rewards Points: 18,183
I have had a spa manufacture attempt this with me before. After much resistive hoopla, and they insisted a Siemens gfi breaker had to be installed, I had an alternate idea, which was to suggest to them that the customer and myself would be bringing out the chief inspector for the jurisdiction to make an inspection call. They re-sent the mechanic immediately who this time changed out the crappy faulting heating element and no further problems, using the square-d breaker originally installed. All fine afterwards, and their spa equipment is still allowed to be sold in these here parts. win, win.
JOBS GROWTH SOARS
RECORD WORKING
UNEMPLOYMENT 50-YEAR LOW
Drudge Report
Pool pump GFCI cord. 6 shooter General Electrical Discussion 17 06-04-2014 11:30 PM
Pool Pump Short or GFCI trip? Cletis General Electrical Discussion 40 08-09-2011 01:24 PM
No GFCI protection, non-dwelling sump pump? Chris Kennedy NEC Code Forum 5 07-08-2011 07:51 PM
pool; filter pump not working gfci breaker will not reset Pro Home Improvement Residential Electrical Forum 7 03-17-2011 11:27 PM
gfci protecting pool pump motor rebel34 NEC Code Forum 7 03-28-2008 08:15 AM