Just curious. What type conductors/wiring methods you residential guys are using for the branch circuit conductors from the main service panel in a wood frame house new construction over crawl space to a 120/240 volt 100 amp Intermatic pool panel mounted on the exterior wall of the same structure about 35 feet away with a #8 insulated grounding conductor requirement.
These provisions shall apply to any feeder on the supply side of panelboards supplying branch circuits for pool equipment covered in Part II of this article and on the load side of the service equipment or the source of a separately derived system. (A) Wiring Methods.
(1) Feeders.
Feeders shall be installed in rigid metal conduit or intermediate metal conduit. The following wiring methods shall be permitted if not subject to physical damage:
Liquidtight flexible nonmetallic conduit
Rigid polyvinyl chloride conduit
Reinforced thermosetting resin conduit
Electrical metallic tubing where installed on or within a building
Electrical nonmetallic tubing where installed within a building
Type MC cable where installed within a building and if not subject to corrosive environment
Exception: An existing feeder between an existing remote panelboard and service equipment shall be permitted to run in flexible metal conduit or an approved cable assembly that includes an equipment grounding conductor within its outer sheath. The equipment grounding conductor shall comply with 250.24(A)(5).
680.25 Feeders. These provisions shall apply to any feeder on
derived system.
(A) Feeders. Where feeders are installed in corrosive environments
as described in 680.14, the wiring method of that
portion of the feeder shall be as required in 680.14(B) or shall
be liquidtight flexible nonmetallic conduit. Wiring methods
installed in corrosive environments as described in 680.14 shall
contain an insulated copper equipment grounding conductor
sized in accordance with Table 250.122, but not smaller than
12 AWG.
Where installed in noncorrosive environments, feeders shall
comply with the general requirements in Chapter 3.