Question about residential main breakers - Electrician Talk - Professional Electrical Contractors Forum
Like Tree26Likes
Old 10-09-2017, 08:16 PM   #1
carryyourbooks's Avatar
Rewards Points: 1,292
Default Question about residential main breakers
Today, a topic come up about residential main breakers, specifically 100a and 125a side-mounted main breakers. I was told that the space right across from a main breaker should not be used due to heat. I know some panels are made so that you cannot use that space directly across from them because there is not bus bar there, but what about those that are? We always install new panels with a main at the top, but what about existing panels? Are they in some sort of violation if they have other branch breakers across from the main?
carryyourbooks is offline   Reply With Quote
Old 10-09-2017, 08:25 PM   #2
Rewards Points: 1,651
Nope.
If you can physically install the breaker there and it doesn't say not to install one on the sticker on the panel cover, you are good to go.
The sticker will tell you if a main can be installed, which breaker to use, and which hold-down kit to use.
The older Siemens hold-down kit was small and allowed a breaker to be installed across from it. The newer hold-down kit takes up that space, not allowing a breaker to be installed.
carryyourbooks (10-10-2017)
Old 10-09-2017, 08:29 PM   #3
Here is an example. This is a 12 space panel that they factory install a 100a main. You can see in the picture that you can use all 10 remaining spaces, including the 2 across from the main: http://www.homedepot.com/p/Eaton-100...SRNV/100568618
Old 10-09-2017, 11:00 PM   #4
220/221's Avatar
Rewards Points: 4,126
No matter what the instructions say, logic says to give it some breathing room if you can.
I have seen probably one hundred AC breakers burn the bus along with the breakers and bus next to it so I got into the habit of, when possible, leaving some space and not putting big loads next to to each other.
Old 10-09-2017, 11:08 PM   #5
That's because you geniuses live in the scorching hot desert and put your panels outside in the sun and heat.
Those of us who live in normal places with panels inside never saw 100 AC breakers burn the bus along with the breakers next to it.
Logic says if breakers need breathing room they would be spaced apart.
jbfan and MTW like this.
strawburner (10-13-2017)
Old 10-10-2017, 02:51 AM   #6
Thanks, guys!
Old 10-10-2017, 06:33 AM   #7
Retired Account
Rewards Points: 14,650
The topic resurfaces every now/ then
Your answer is in the listing
Specifically, the 'bus' of any given panel is good for XX amps
Old 10-10-2017, 07:58 PM   #8
Chief Flunky
Rewards Points: 338
Circuit breakers should NOT overheat. The residential ones almost exclusively use a thermal trip element which works on heat so it SHOULD get hot if there is a fault. Otherwise if your panel is hot, its a high resistance connection that is an impending failure and needs to be replaced. That's why progressive companies use infrared cameras to check their panels.
The biggest design/installation error is under sizing the AIC in industrial panels...basically putting it on too big of a transformer for what it is rated for. This is rarely a problem in residential conditions. Instead I tend to see double tapped mains, common neutrals, putting way too many wires under a terminal, all kinds of wire but violations, improper ground terminations or maybe no ground bar at all, never filled out the panel schedule or 6 entries that all say "receipts" or "lights", and no grounding or plastic bushings, two screws with all kinds of things other than a single NM under them, and things stripped waaay too far back.
And 125A panels? That's OK for 1970s stuff but not now. Not sure you can even buy them that small. When you can buy a prepopulated lighting panel rated 150 or 200 A with 24 breakers already installed for about $300 even a SqD and not a throwaway India made Siemens or GE (made in the same plant!), why buy the unpopulated panel and individual breakers except to soak the customer on parts?
Sent from my Galaxy Tab 2 using Tapatalk
Old 10-10-2017, 08:03 PM   #9
I was with you for a while, but then you went full ret*rd. You never go full reta*d.
TheLivingBubba likes this.
Old 10-10-2017, 08:26 PM   #10
Magic Smoke Remover
Rewards Points: 1,966
I've seen BR melt down in a conditioned space with A/Cs grouped, but not 100 of them.
Old 10-10-2017, 08:36 PM   #11
HTTR
Jack Legg's Avatar
Rewards Points: 804
its in the listing. If there is a limit it will state something like this:
Jack Legg is offline   Reply With Quote
The Following User Says Thank You to Jack Legg For This Useful Post:
telsa (10-12-2017)
Old 10-10-2017, 08:39 PM   #12
There must have been some other issue.
If this was a thing, the manufacturer would specify no large breakers next to each other or to leave an empty space between them. Or the NRTL that listed the panel would make them require that.
Old 10-10-2017, 08:56 PM   #13
MTW
Rewards Points: 10,292
Are you Telsa's alter ego?
A Little Short likes this.
Old 10-10-2017, 09:58 PM   #14
Rewards Points: 1,360
The bus stabs have a rating like posted above. I've seen some say 110, some are 125, and some are 140 amps per stab. So, for example, if the stabs are rated at 110 amps, then putting two 60 amp breakers across from each other would be a no no. It stands to reason that this would apply to the bus the main is attached to as well.
eddy current and splatz like this.
Old 10-12-2017, 04:56 PM   #15
220/221's Avatar
I was born in Phoenix and if I moved, I doubt it would ne to Jersey lol. Talk to me at the end of January when you are freezing your nuts off and I'm still in shorts and short sleeves.
The panel location is irrelevant because 99.9% of them work just fine.
But AC's do work hard here.
Old 10-12-2017, 06:34 PM   #16
Chief Flunky
Rewards Points: 338
This doesn't make any sense. The bus is protected by the main, not the branch circuit breakers. You could have a 10 slot panel rated 100 A and 10 15 A breakers. It can theoretically be loaded to 150 A but that would then trip the main. The branch breakers protect the branch circuits. This almost never happens in practice due to diversity (loads are not 100%) and granted unless they are 100% rated they trip at 80% (12 A) etc., etc., but the idea that branch circuit breaker sizes and positions are limited by the bus size does not pass the smell test.
This is far different from vertical vs. horizontal ampacity in MCC but that's different because there isn't a separate overcurrent device for the vertical bus sections. In that circumstance and some feeder cases it is legal and required to protect upstream bus with downstream protection but that's not the case in a panelboard.
Old 10-12-2017, 07:06 PM   #17
It makes perfect sense. You should think twice, or 3 times, before question MrPhase.
The bus, but not the stabs.
The branch circuit breakers protect the stabs.
Here is an example of the listing of a Murray panel:
SUM OF MH-T BREAKER RATING IS NOT TO EXCEED 110 AMPS PER BRANCH CIRCUIT BUS STAB.
http://www.homedepot.com/catalog/pdf...8846ea993e.pdf
As you can see, you can't put a 90A and 60A breaker on the same stab (next to each other) since the stabs are only rated at 110A.
That is what MrPhase was speaking about.
MechanicalDVR (10-12-2017)
Old 10-12-2017, 09:06 PM   #18
Rewards Points: 1,986
A Molded case circuit breaker trips on a fault from magnetic trip NOOT THERMAL, thermal tripping is from an sustained overload.
Check the load on a residential panel and except for houses with electric heat most residential services are way over sized.
The biggest design/installation error is under sizing the AIC in industrial panels...basically putting it on too big of a transformer for what it is rated for. T.
The size of the transformer is not this issue in regards to AIC, It is the available fault current the utility can provide in their distribution system. Two identical transformers can have different available fault currents based on many variables in the distribution system.
HackWork and TheLivingBubba like this.
Old 10-12-2017, 09:14 PM   #19
Bad CB or high resistance connection to the bus.
MechanicalDVR and HackWork like this.
Old 10-12-2017, 09:35 PM   #20
I'm going to send a strongly worded email to the major panel manufacturers telling that that Paul from "The Carolinas" doesn't like the way their breakers smell. Strongly worded. Strongly.
matt1124 likes this.
Odd question about residential 120V smoke detectors Bzzzzzt General Electrical Discussion 20 08-26-2017 11:46 PM
Double panel design question. JohnJ65 Services and Service Equipment 23 07-07-2017 09:19 PM
Locking residential main breaker in the 'ON' position. Sparkysquared Canadian Electrical Forum 16 09-28-2016 06:42 PM
ontario smoke/co/strobe for residential rules question lohirise Canadian Electrical Forum 11 04-17-2016 11:56 PM
Residential main feed voltage fluctuation stackvortex General Electrical Discussion 27 03-14-2016 09:53 PM