Regarding reducing washers, looking for guideance in proper way to install reducing washers. I have always put the raised portion of both washers to face into enclosure. This prevents movement of washer and connector, let's say. I recently spoke with a solar installer who installs them opposite, flat against enclosure and raised portion facing away from opening in enclosure. Feedback?
crw16 is offline   Reply With Quote
Old 12-02-2019, 10:40 PM   #2
joe-nwt's Avatar
Rewards Points: 998
Your way is correct. They can't properly reduce the hole unless they are in the hole. Thr raised portion keeps the washer centered.
samgregger and splatz like this.
Old 12-02-2019, 10:42 PM   #3
Light Bender
eddy current's Avatar
Rewards Points: 7,738
Depends on how thick the enclosure wall is. I install them with the raised part going in usually, but if the connector bottoms out and does not get tight, then I might put one of them backwards and sometimes both.
Keep in mind that you can not use them as a bond connection as per code so it really doesn’t matter which way you install them, although like Joe just posted, it helps keep them in place when installed inwards
Old 12-02-2019, 10:45 PM   #4
Awg-Dawg's Avatar
Rewards Points: 726
Is that a Canadian code about the reducing washers not being used for bonding?
I feel sorry for people who don't drink, when they wake up in the morning, that's the best they will feel all day.
Awg-Dawg is offline   Reply With Quote
Old 12-02-2019, 11:09 PM   #5
Light Bender
Yes 10-606(2)
But I assume the NEC has a similar rule no?
Old 12-02-2019, 11:12 PM   #6
Awg-Dawg's Avatar
Rewards Points: 726
Yes 10-606(2)
It’s allowed , unless the code changed and I overlooked it.
The Following User Says Thank You to Awg-Dawg For This Useful Post:
Southeast Power (12-02-2019)
Old 12-03-2019, 12:47 AM   #7
Rewards Points: 3,036
If putting both washers the 'right way' results in it being too loose, I'll put one the 'right way' and the other the 'wrong way'. This ensures that the fitting is centered on the oversize hole and also the locknut makes a tight connection.
I've also been known to screw a blank plate (4sq. , 3-0 or 4-0 round) over the oversize hole and punch the correct size KO in it. This is especially handy with larger motors that have sheet steel terminal boxes and huge KOs.
Of course, this violates the listing and who knows how many other equally idiotic regulations...........
Cow, flyboy, tmessner and 3 others like this.
Old 12-03-2019, 12:54 AM   #8
dronai's Avatar
Rewards Points: 4,605
Ha ! We had this problem today, and that solution was mentioned 11/2 KO in the peckerhead, but this one wasn't threaded
micromind likes this.
Old 12-03-2019, 03:45 AM   #9
CMP
CMP's Avatar
Rewards Points: 114
Yes 10-606(2)
Could be a gray are depending on AHJ and brand of reducing washer.
250.96 Bonding Other Enclosures.
(A) General. Metal raceways, cable trays, cable armor, cable sheath, enclosures, frames, fittings, and other metal non-current-carrying parts that are to serve as equipment grounding conductors, with or without the use of supplementary equipment grounding conductors, shall be bonded where necessary to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on them. Any non-conductive paint, enamel, or similar coating shall be removed at threads, contact points, and contact surfaces or be connected by means of fittings designed so as to make such removal unnecessary.
Then you have...
250.12 Clean Surfaces.
Nonconductive coatings (such as paint, lacquer, and enamel) on equipment to be grounded shall be removed from threads and other contact surfaces to ensure good electrical continuity or be connected by means of fittings designed so as to make such removal unnecessary.
So that says to remove paint or use a washer tested and marked UL to not require removing paint.
UL listing QVRC says
GROUNDING
Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with ANSI/NFPA 70, "National Electrical Code," for raceways containing other than service conductors. Reducing washers are intended for use with metal enclosures having a minimum thickness of 0.053 in. Reducing washers may be installed in enclosures provided with concentric or eccentric knockouts, only after all of the concentric and eccentric rings have been removed. However, those enclosures containing concentric and eccentric knockouts that have been certified for bonding purposes may be used with reducing washers without all knockouts being removed.
So technically, it depends on the reducing washer listing and the box type and listing. It's a fine point, but could be nit picked. I never have been.
I checked a few suppliers to see if there product was listed and marked for use.
The old Arlington ones on my shelf have no listing, the same with RACO.
Topaz, Crouse Hinds, and T&B did have a listing, and the products are marked with a UL stamp.
So is it compliant? Can you prove it? It depends...
CMP is offline   Reply With Quote
Old 12-03-2019, 07:05 AM   #10
Small Potatoes
flyboy's Avatar
Rewards Points: 3,889
Then you have...
GROUNDING
Any inspector that busts you on this one should have his genitals removed with a hook knife.
Old 12-03-2019, 07:45 AM   #11
Rewards Points: 7,487
Brutal.
Old 12-03-2019, 08:54 AM   #12
Gold Pliers Champion
Signal1's Avatar
Rewards Points: 2,322
Then you have...
GROUNDING
MTW and CoolWill like this.
Old 12-03-2019, 09:18 AM   #13
Light Bender
Here is the Canadian code. It’s pretty clear that they can not be used for bonding.
10-606
2) Reducing washers shall not be used to maintain the bonding continuity of the wiring system.
electricguy (12-03-2019)
Old 12-03-2019, 09:31 AM   #14
Rewards Points: 838
10-606
That is so convoluted.
CoolWill likes this.
Old 12-03-2019, 09:36 AM   #15
CoolWill's Avatar
Rewards Points: 3,926
10-606
Old 12-03-2019, 11:13 AM   #16
Small Potatoes
flyboy's Avatar
Yeah it's complicated too.
dronai and splatz like this.
Old 12-03-2019, 09:10 PM   #17
Awg-Dawg's Avatar
Rewards Points: 726
Then you have...
GROUNDING
All that stuff you said applies to raceways/cables and other supplies.
I would be surprised to see any reducing washers not listed(although I’ve never even paid attention), I would just install them and let the EI duke it out with the manufacturer.
Old 12-04-2019, 12:20 AM   #18
CMP
CMP's Avatar
Rewards Points: 114
Take it however you like, or don't. Most of the text was quoted from the NEC and UL. Reducing washers are a raceway accessory, so to my knowledge the information is accurate and enforceable.
I just took the time to post it for others, on reducing washer use. For washers that are not listed, I gave two brands as examples. It's a money saving thing to not list them.
As to letting the AHJ duke it out with the manufacturer, that's a good one, I'll need to remember that the next time I ever get a red tag. Southeast Power might be able to use that one in his sealing locknut issue.
Doing a job over again on my dime to clear a reg tag for something silly is not my way. I like to spend the customers money on doing it right the first time, and getting a cut of it.