Resistance and splicing - Page 2 - Electrician Talk - Professional Electrical Contractors Forum
Old 02-22-2015, 02:59 PM   #21
More than lead and elbows
JW Splicer's Avatar
Rewards Points: 1,130
Are we talking about wire nuts, or soldered split sleeve on a paper insulated lead cable? What is the method and voltage etc? If the splicer is good, it should be negligible. If the splicer is really just a hack, you will have higher resistance due to improper cable prep, over or under torquing, wrong crimp die, bird caging of conductor, air voids, over insulation, water in the cable, oxide removal and prevention.... It's a long list.
Every once in a while I get to hang a pothead!
JW Splicer is offline   Reply With Quote
Old 02-22-2015, 03:15 PM   #22
JW Splicer's Avatar
Ok what I think Macmikeman is try to say is that at the split bolt connection, if properly installed, the total volume of the cable is doubled at least for a short length. In which case the resistance does go down. Now here me out. It is negligible, but if you think about a #12 and a #10 of equal distance, the #10 has less total resistance. The reason you upsize for VD. Ok now what if you had a #12 with multiple spots (splices) where the volume of the conductor is increased for short lengths to essentially #10. The total resistance of the circuit would be less than an equal length #12 and more than an equal length #10.
Old 02-22-2015, 03:18 PM   #23
Rewards Points: 1,526
How clean is the connection? Over time, will it oxidize? Is it soldered? Exposed ? Pretty vague imo. Bad splices can certainly add resistance, but properly done, there should be zero added resistance.
Wpgshocker is offline   Reply With Quote
The Following User Says Thank You to Wpgshocker For This Useful Post:
macmikeman (02-22-2015)
Old 02-22-2015, 03:23 PM   #24
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
I don't believe that for a moment
guest (02-22-2015)
Old 02-22-2015, 03:23 PM   #25
Rewards Points: 18,281
Myself, I won't go so far as to say zero, but given the original content of the thread, the shortening of the overall length of conductor in the subject of this thread is by far the greater of the reduction of resistance vs the micro addition of resistance, when properly installed.
It is just to much for the non illuminati believers to grasp.
JOBS GROWTH SOARS
RECORD WORKING
UNEMPLOYMENT 50-YEAR LOW
Drudge Report
Old 02-22-2015, 03:24 PM   #26
Rewards Points: 3,090
So far it is your conjecture vs my conjecture. At least I have spoken to Burndy about this in the past, and while they man was somewhat cadgey because of the fact that almost no one in our trade will properly install split bolts, so mostly they will add resistance, he maintained that there will be no added resistance to a proper bolted connection. I just don't remember his name sadly. I did this using google about a half decade back maybe to get to that source, so get your engines going, and lets get the proof and dunk the macmikeman into the water. Or not....
A salesman from Burndy?
The second part is true, no added resistance to a proper bolted connection!
Still a fun thread to follow!
Borgi
Old 02-22-2015, 03:32 PM   #27
JW Splicer's Avatar
Perfect world, we are in anything but. Even copper oxidizes and there is probably some galvanic action between the split bolt/wire nut or whatever. Real world scenario the resistance will most likely go up due to external factors.
The Following User Says Thank You to JW Splicer For This Useful Post:
guest (02-22-2015)
Old 02-26-2015, 02:32 AM   #28
Depending on the splices it will make the resistance go up or down, if you make sure the splices are tight the resistance will go down. So basically depending on the quality of your work.
jesseswope8 is offline   Reply With Quote
Old 02-26-2015, 02:42 AM   #29
five.five-six's Avatar
Rewards Points: 10,226
Originally Posted by don_resqcapt19 View Post
Can you cite a source for that?
Old 02-26-2015, 02:47 AM   #30
triden's Avatar
Rewards Points: 382
Who here would argue that this splice will increase the resistance of the cable? We assume that it was done properly - oxide removed and then glyped and taped.
If resistance is based on total cross sectional area, the splice should technically have a lower resistance given that the cable is twice the diameter at the splice.
Here is a graph of a splice that is soft soldered together. One can see that as the cable overlap increases, the overall resistance does decrease (in the nOhm range though). This chart shows the resistance of the splice itself, not the overall cable which is important.
The Following 4 Users Say Thank You to triden For This Useful Post:
51360 (02-26-2015), JW Splicer (02-27-2015), macmikeman (02-26-2015), meadow (02-27-2015)
Old 02-26-2015, 02:48 AM   #31
There is no way that the splice itself has lowered the resistance. Now if you have shortened the total length, sure, but that is not because the split bolt connection has reduced the resistance.
The resistance of the connection may approach that of the the unspliced conductor, but it will always be higher.
There will be twice the circular mills of copper at the area of the splice.
Negligible but I think he who believes in the illuminati has a point.
Old 02-26-2015, 01:46 PM   #32
Rewards Points: 1,224
Sure there is increased area, but there is also the connection between the two cables. I just don't see that as being a zero ohm connection.
millelec (02-27-2015)
Old 02-26-2015, 03:28 PM   #33
Rewards Points: 183
There won't be any Resistance cause the wire is too short now.
EC2253 is offline   Reply With Quote
Old 02-26-2015, 04:45 PM   #34
Retired Account
Rewards Points: 14,650
Old 02-27-2015, 01:50 AM   #35
Im giving out mostly ''F'''s here, one or two ''A'''s and an A+. Class is dismissed.
JOBS GROWTH SOARS
RECORD WORKING
Drudge Report
Old 02-27-2015, 02:19 AM   #36
Very Long Vacation
Rewards Points: 5,262
Basically paralleling high Z paths to get one low one?
Old 02-27-2015, 02:44 AM   #37
triden's Avatar
Rewards Points: 382
Or too low Z paths to get a low one
Old 02-27-2015, 10:42 AM   #38
Rewards Points: 374
Theoretically, I think there would be more resistance in a splice if the wire was already at its maximum ampacity but otherwise I can't imagine any difference. If the wire was loaded to capacity I would think there would be some minscule increase in resistance as electron flow was diverted through the splice. I am not saying it would be measurable, just that I can see it existing. JMO fire away
Hawkrod is offline   Reply With Quote
Old 02-27-2015, 11:36 AM   #39
By that thinking, stranded wire would be a mess of impedence. On the contrary, splitting up a conductor into the strands lowers resistance.
JOBS GROWTH SOARS
RECORD WORKING
Drudge Report
Old 02-27-2015, 11:45 AM   #40
JDJ
Rewards Points: 547
For clarity, what's your take on properly installed split bolt?
JDJ is offline   Reply With Quote
Torque vs resistance Cantafford General Electrical Discussion 6 02-19-2015 12:07 PM
[email protected] 95 from Resistance @35 bibincjoy General Electrical Discussion 3 07-18-2014 03:26 PM
UF splicing brichter General Electrical Discussion 14 05-26-2014 06:11 PM
high resistance? 3tigerz Services and Service Equipment 8 04-18-2009 01:52 PM
high resistance? 3tigerz Site Help and Suggestions 3 04-09-2009 04:34 PM