Service Equipment Attached To Metal Siding - Electrician Talk - Professional Electrical Contractors Forum
Like Tree6Likes
  • 1 Post By HackWork
  • 1 Post By Glock23gp
  • 1 Post By Bird dog
  • 1 Post By sbrn33
  • 1 Post By macmikeman
  • 1 Post By tates1882
Old 04-23-2017, 10:15 AM   #1
Default Service Equipment Attached To Metal Siding
Just wondering how grounding, bonding and separation of ground and neutral apply to a situation like this: A 200 AMP service meter box is attached to the metal siding of a pole barn using unistrut channels and the neutral in the meter box is bonded to the meter box which in turn bonds it to the metal siding via the unistrut channel. The main 200 amp panel has the Ground and Neutral buses bonded and the grounding electrode conductor originates here and terminates in two grounding electrodes. Does the neutral from the service being bonded to the metal pole barn siding pose a potential problem?
ricpad is offline   Reply With Quote
Old 04-23-2017, 10:32 AM   #2
Rewards Points: 1,141
Nope, that is perfectly normal. Everything sounds good.
Old 04-23-2017, 10:39 AM   #3
MXer774's Avatar
Rewards Points: 608
There's not much you can do to correct it.
There probably will be return current between the metallic portions of the meter and panel.
I've build numerous services like this with no issues.
I wish the utilities would allow an isolated neutral in their can.
MXer774 is offline   Reply With Quote
Old 04-24-2017, 11:34 AM   #4
Glock23gp's Avatar
Rewards Points: 96
You need to scrape some paint off the tin and attach a lug with a bonding jumper to the ground bus.
Then if the tin were to become energized it has a path to ground better than a human body.
That's a requirement here.
Done dozens of them.
Sent from my SAMSUNG-SM-N910A using Tapatalk
Using Tapatalk
Glock23gp is offline   Reply With Quote
Old 04-24-2017, 12:54 PM   #5
Bird dog's Avatar
Rewards Points: 862
One place I worked, they isolated the whole can with a plywood backboard.
Old 04-24-2017, 12:58 PM   #6
sbrn33's Avatar
Rewards Points: 3,508
That is one of the dumbest things I have ever heard. Your inspectors need a kick in the nards.
macmikeman likes this.
Old 04-24-2017, 01:00 PM   #7
Rewards Points: 18,141
I was thinking the same thing. Unistrut bolts to the siding is enough of a connection to not require any more nonsense.
telsa likes this.
JOBS GROWTH SOARS
RECORD WORKING
UNEMPLOYMENT 50-YEAR LOW
Drudge Report
Old 04-24-2017, 01:22 PM   #8
Rewards Points: 3,006
Not sure if it is relevant but our code says bond attachment can serve no other purpose but bonding, so that means no equipment fasteners can be used for bonding.
sort of like when home owners just bond a light fixture to the mounting strap and not continue it to the bond conductor
Old 04-24-2017, 01:31 PM   #9
MXer774's Avatar
Rewards Points: 608
Why? Was the riser & feeder nonmetallic as well?
Old 04-24-2017, 01:35 PM   #10
Bird dog's Avatar
Rewards Points: 862
They wanted little or no current on all the grounding conductors. Yes, riser & feeder were nonmetallic.
Old 04-24-2017, 01:44 PM   #11
MXer774's Avatar
Rewards Points: 608
I see, so that backboard was used for the sole purpose of providing an insulator between the meter enclosure and metal building?
Old 04-24-2017, 01:52 PM   #12
Bird dog's Avatar
Rewards Points: 862
To isolate the MDP which was fed by a genset. But yes sole purpose was for isolation.
Old 04-24-2017, 08:39 PM   #13
Retired Account
Rewards Points: 14,650
Does said pole barn share power or communication lines with any other proximal structure?
Old 04-25-2017, 11:49 AM   #14
zap
tates1882's Avatar
Rewards Points: 1,072
According to 250.116 informational note "Where extensive metal in or on buildings may become energized and is subject to personal contact, adequate bonding and grounding will provide additional safety."
Because the above statement doesn't contain the words shall or shall not and is an informational note I would say its up to the AHJ. That being said a metal enclosure mounted to metal strut on the side of metal building is considered bonded around here.
Old 04-27-2017, 06:43 PM   #15
No it does not.
Can SDGE require my customer to pay for transformer Jeremy9 General Electrical Discussion 13 06-17-2018 11:51 PM
Hiring Service Techs emahler General Electrical Discussion 0 11-30-2016 02:08 PM
Electric Company Service Drop Upgrade MustangRider6688 Services and Service Equipment 12 07-11-2016 06:03 PM
Changing my service AK_sparky General Electrical Discussion 30 06-22-2016 10:48 PM
Ungrounded Delta 480 Station Service with ground reference App4DaWin General Electrical Discussion 30 04-14-2016 01:12 PM