shunt trip breaker - Electrician Talk - Professional Electrical Contractors Forum
Old 04-04-2011, 09:29 AM   #1
Default shunt trip breaker
I am having a brain cramp, do you connect one lead to the nutrual bar.
spider is offline   Reply With Quote
Old 04-04-2011, 10:19 AM   #2
Salvatoreg02's Avatar
Rewards Points: 1,002
Does it have a neutral?
Sal
P.E.S
Salvatoreg02 is offline   Reply With Quote
Old 04-04-2011, 10:44 AM   #3
No just the two black leads
Old 04-04-2011, 10:48 AM   #4
BBQ
Salty Member
BBQ's Avatar
If you are sure the trip unit is 120 volts then yes one black lead needs to go to the neutral bar.
Old 04-04-2011, 10:50 AM   #5
Yes it 120 or 240
Old 04-04-2011, 10:58 AM   #6
BBQ
Salty Member
BBQ's Avatar
Originally Posted by spider View Post
Yes it 120 or 240
Well now I am lost because I have never seen a shunt with just two leads rated 120 or 240.
Old 04-04-2011, 11:16 AM   #7
Ax grinder
raider1's Avatar
Rewards Points: 1,162
Agreed, all the shunt trip devices that I have seen are typically 1 voltage.
Chris
The Following User Says Thank You to raider1 For This Useful Post:
ce2two (04-06-2011)
Old 04-04-2011, 11:21 AM   #8
Did you Install a push button switch also?
Sal
P.E.S
Old 04-04-2011, 02:48 PM   #9
Sorry for the delay but this shut has dual voltage 120 to 240 first time I have come across this but I will treat it like a 120 application.
Old 04-04-2011, 04:13 PM   #10
Rewards Points: 6,421
I'm not so sure I'd hook it to the neutral bar if this was a 277/480 panel. I'd probably also not hook it to the neutral bar if your control power comes from someplace else. Use that "someplace else" neutral.
Smoke (04-04-2011)
Old 04-04-2011, 04:20 PM   #11
Is there a terminal you need to move around on the accessory, inside the breaker? Got a manufacturer and part number for this rascal? I'm curious. I've never seen a dual voltage unit with only two leads either.
Old 04-04-2011, 04:30 PM   #12
The shut trip breaker is a GE 3 pole thbq
Old 04-04-2011, 04:32 PM   #13
Rewards Points: 504
Funny, my experience has been the exact opposite
Almost all the shunt trips I've seen can handle more than one voltage and need a separate circuit to feed the shunt coil and make the breaker trip.
(I'm using SquareD numbers here because that's what I have been mainly using and have the numbers handy on my phone)
The coil ratings on the ones I've seen are 12 to 24 volts. Those I see in a lot of car washes inside control cabinets. They can handle AC or DC voltages.
12V - 60VA
24V - 168VA
and the coils on the others I more commonly run into are 120 to 240 volt. I see them all the time in gas stations and started running into them a lot more the last few years. AC voltage only on the coils.
120V - 72VA
208V - 228VA
240V - 288VA
Normally the shunt coils are fed with a separate circuit and wired at 120V around here. One side of the coil goes to neutral and the other needs a hot to complete the circuit. Liven up the shunt coil and it trips the breaker.
I've been using big red mushroom switches that need to be manually pulled up, but breakers are rated to accept momentary contacts. Once tripped the breakers have to be manually reset, and if the contact to feed the shunt is a maintaining contact, it has to be opened. That confused the hell out of me the first time I ever saw one, not realizing I had to go across the building and pull up a mushroom switch.
The ones I've used take an extra breaker space, so a single pole 15A breaker shunt trip breaker takes the same space as a 2 pole breaker, a 2 pole takes the space of a 3 pole and so on.
Also, in the applications I use them for, the breaker with the circuit that feeds the shunt coils are normally locked on so they can't be turned off accidentally as their operation serves important safety/security measures.
Mike_586 is offline   Reply With Quote
Old 04-04-2011, 04:38 PM   #14
Thanks it work on a 120 input off fire alarm system, works great passed inspection
Old 04-04-2011, 08:24 PM   #15
Smoke's Avatar
Rewards Points: 250
thats not entirely correct, he is likely working on an elevator shunt (doesnt matter though). the neutral comes from the source, rarely the panel the shunt is located, but possible.
unrelated to quote, hot on one wire neutral on the other, color doesnt matter.
i put 2 red wires off the shunt here this weekend, i like it to be obvious the shunt circuit is there and not fed from the panel (277/480 in my case).
its a coil, polarity is irrelevant.
there's some technical crap to mull over
Smoke is offline   Reply With Quote
Old 04-04-2011, 08:27 PM   #16
Smoke's Avatar
Rewards Points: 250
doesnt matter, its 2 wires to a shunt coil, only the voltage you need to trip it is relevant.
Old 04-04-2011, 09:56 PM   #17
vos
vos's Avatar
Rewards Points: 150
what's a shunt trip breaker?
vos is offline   Reply With Quote
Old 04-04-2011, 10:54 PM   #18
Rewards Points: 3,030
I've seen lots of shunt trip coils that were rated for more than one voltage. I'd say most of them I've seen recently.
Two black wires, but the inrush is way more for the higher voltages.
Remember, a shunt trip coil is energized only for a very short time; not long enough to cause the coil to heat up.
The only ones I've seen that are single voltage are either 125 or 250 DC. Just about everything else has a range of voltages.
One wire goes to the switch leg of whatever will cause the breaker to trip, the other wire goes to the return; often the neutral bus. Sometimes the grounded side of the control transformer.
Rob
Old 04-04-2011, 11:02 PM   #19
Rewards Points: 2,012
Never mind. I was gonna be a wise ass. But never mind.
Old 04-05-2011, 12:19 AM   #20
Golden Controls
dowmace's Avatar
Rewards Points: 502
A breaker than can be remotely tripped by an outside voltage source. Thats the easiest description I can come up with.
dowmace is offline   Reply With Quote
The Following User Says Thank You to dowmace For This Useful Post:
vos (04-05-2011)
Shunt trip breakers jack756 NEC Code Forum 14 10-07-2010 01:30 AM
10 A Shunt Trip RePhase277 General Electrical Discussion 3 07-13-2009 10:42 AM
Shunt Trip shunt trip New Member Introductions 4 01-27-2009 09:08 PM
? about shunt trip requirement Greg General Electrical Discussion 11 07-17-2008 06:03 AM
Shunt Trip Breaker???? lorddrago General Electrical Discussion 4 12-30-2007 11:38 AM