Step down transformer - Electrician Talk - Professional Electrical Contractors Forum
Like Tree9Likes
  • 2 Post By Tonedeaf
  • 7 Post By micromind
Old 12-20-2016, 10:02 AM   #1
Rewards Points: 384
Default Step down transformer
I have this 112.5 step down which is making a horrible noise. can anyone tell me why it doesn't let me attach a video.
Julius793 is offline   Reply With Quote
Old 12-20-2016, 10:38 AM   #2
Rewards Points: 1,018
post a video
what kind of noise?
If its a vibration type noise, you usually can't do anything unless its the transformer enclosure or at electrical connection points. You can tight up the associated fasteners to fix this.
If the noise is caused by the laminates moving back and forth or caused by the shims in the winding being loose, there is not much u can do.
If its nonlinear load related noise, the 3rd harmonic will circulate in the Delta side of the transformer and cause excess vibration which makes noise. They do make K rated transformer that handle nonlinear loads better. Alot of older transformers are not K rated.
Dry transformers are usually good or bad, not very often are they in the middle of going bad like oil transformers.
Make sure all the electrical connections are tight before you do anything.
Old 12-20-2016, 11:14 AM   #3
Rewards Points: 3,078
The bolts that attach the iron core to the frame need to be loosened a bit. They are tight for shipping and if left tight they will transmit noise.
Some transformers (most notably GE) are more noisy than others.
The Following 2 Users Say Thank You to micromind For This Useful Post:
360max (12-20-2016), therain (12-20-2016)
Old 12-20-2016, 01:18 PM   #4
NC Plc's Avatar
Rewards Points: 7,888
Some transformers are just noisy. For the love of god don't put a box around it to try to cut down on the noise.
I would rather ask a seemingly stupid question than not ask it and make a stupid mistake.
NC Plc is offline   Reply With Quote
Old 12-20-2016, 02:06 PM   #5
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
What type of loads? High harmonic currents will absolutely cause a lot of additional iron vibration and make a transformer noisy as hell.
Transformers that only run large VFD loads often sound terrible for just this reason.
Always wear your gloves.
Old 12-20-2016, 07:39 PM   #6
Rewards Points: 1,950
Transformers that make excessive noise, I mean really loud, may have the laminations delaminating.
Time for replacement, if that is the case.
Check load types as noted above, see if any new loads were added.
Old 12-20-2016, 08:38 PM   #7
Rewards Points: 384
i still cant upload my video i took on my iphone so its basically the same humming noise you would expect to hear from a transformer but just really load. additionally there is a balanced load of about 20A primary side and the transformer is really hot. is that info helpful?
Old 12-20-2016, 08:47 PM   #8
Rewards Points: 21,896
20 amp on primary side on 112.5 Kva transfomer ??
The room is hot then you will expect the transfomer to be hot of course.
Most transfomer can handle pretty high tempture rise without much issues.,,
What type of load it is running thru the transfomer ?
as other poster here gave ya the answer so double check the connection and ya the mounting bolt sometime some peoples forget to remove or loosen up the shipping bolt that useally most common curpit.
You can reduce the noise by putting a rubbber pads below the transfomer unless it is wall hung type which I dont see often on that large a transfomer.
some case you may have to put in a flexi conduit to reduce the noise too.
Old 12-20-2016, 09:10 PM   #9
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 300
How good is the ammeter you're using? Do the readings make sense proportionately on primary and secondary?
20A is nothing, even if it were all harmonics I wouldn't expect that to be able to heat a 112kVA transformer.
Old 12-20-2016, 09:38 PM   #10
Assuming your testing is correct and the noise is truly excessive
See my post above.
Old 12-20-2016, 10:01 PM   #11
Rewards Points: 384
See my post above.
Yes I think replacement is where we will end up. Thanks
Old 12-21-2016, 03:26 AM   #12
Rewards Points: 1,504
Usually means something is loose.
or you have shorted turns.
Can you get to the tranny internals ?
or is it a sealed unit ?
Backfeeding Delta-Y Transformer to Y-Delta petedrt Services and Service Equipment 15 07-02-2016 05:07 PM
Transformer neutral bond sizing (paralleled secondary) haltonelectrician Canadian Electrical Forum 27 06-19-2016 07:21 PM
Step Up single phase transformer mr_electrician Services and Service Equipment 4 05-25-2016 06:29 AM
Step up transformer Mikmed98 General Electrical Discussion 11 04-27-2016 09:36 PM
Transformer Bonding CES Services and Service Equipment 25 04-23-2016 12:54 AM