Are you suggesting that a delta Wye transformer be installed or like micro stated to disconnect the MOV or other modifications to the drive?
Old 03-31-2017, 06:48 PM   #22
Rewards Points: 320
Exactly. If you have a Delta or HRG Wye system, you can disconnect the ground reference point of the MOVs, but then you also lose the L-G surge protection.
So another option is a Drive Isolation Transformer. That will give you a Wye secondary (regardless of whether there is a voltage change or not**), then ground the X0 terminal on the secondary. It has no effect on your entire plant-wide Delta or HRG grid, but it gives the VFD what it was made for.
** A lot of Drive Isolation Transformers are 1:1., no voltage change.
splatz (03-31-2017)
Old 03-31-2017, 07:35 PM   #23
This should be a sticky
Old 04-02-2017, 02:13 AM   #24
Rewards Points: 44
Had a store that was a delta service and needed more outlets we just installed a delta/wye transformer with a 208 primary and did away with high leg.
FF301 is offline   Reply With Quote
Old 04-02-2017, 08:33 AM   #25
Rewards Points: 3,006
Sounds cost effective.
Old 04-02-2017, 08:41 AM   #26
Makes zero sense.
You missed April 1st by more than an hour.
You used the high leg to neutral for the primary and installed receptacles off of that?
Old 04-02-2017, 10:59 AM   #27
Rewards Points: 1,972
Makes zero sense.
There is no 208 primary as the phase to phase voltage is 240, NOW if they installed a 208/120 single phase which would require a FSS or 277 CB.
Or more likely if it was a delta=/wye a 2-1 transformer 240 to 208/120
Old 04-02-2017, 12:50 PM   #28
I could see, with some stretch of the imagination getting a feeder under the high leg lug and the other side to neutral if the high leg was underutilized.
I don't like doing that as in my mind the high leg to neutral is somewhat of an auto transformer traveling through a transformer and a half.
It's solid in theory but, we don't see it used like that here at all.
It seems desperate to me but, if you had control over the line and load taps they could do it.
Old 04-02-2017, 02:15 PM   #29
Right transformer for the job 240-208/120 even then there may be issues with loading the Hi-leg transformer due to sizing of the transformers.
Old 04-02-2017, 10:00 PM   #30
Ok, one of those heavy epoxy transformers.
But, like you mentioned, if the lighting transformer is overloaded, it's another problem.
brian john likes this.
Old 04-03-2017, 01:56 PM   #31
Rewards Points: 21,896
Originally Posted by dmxtothemax View Post
The 208v high leg,
Does it have a practicle purpose ?
or is it just the unintended result of something else ?
Is it deliberately used anywhere ?
Why is it so ?
In USA side few members did hit on the spot with good information they posted.
I know there are few new delta service do show up a bit in Cebu Philippines but at my island Minado Islands we are mostly Wye system but yes we do see few new delta but only used with full load of motors but anything else we do use wye in most case.
Now ya say stingers ? sure we do have them here ., but the voltage is much higher useally about 410-416 volt range and once a while I will see some dolts try to use that connection for single phase load and not too pretty due most of the 240 volts items are not too well taken with 415 volt stingers.,,