sub panel feeds no neutral - Electrician Talk - Professional Electrical Contractors Forum
Old 06-11-2012, 07:18 AM   #1
Rewards Points: 63
Default sub panel feeds no neutral
I have a 12-2 with ground romex feed that i want to have a small 240 /120 sub panel at. or a 240 v load and a 120v load is this possible. by pounding another ground. or adding a transformer
myenergy is offline   Reply With Quote
Old 06-11-2012, 07:26 AM   #2
Rewards Points: 2,242
You can add a transformer but pounding a ground rod will not give you as neutral or a ground.
I can't help it if I'm lucky
Old 06-11-2012, 07:30 AM   #3
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 1,038
wow. a whole #12-2 feeder ? with the entire circuit ampacity available ? what are you going to do with all that power ?
Old 06-11-2012, 07:35 AM   #4
Rewards Points: 63
I know it's funny. the home owner paid the electrician to get power out to that side of the house before the basement was finished. so she could have it there when she installed her in ground pool. Just trying to get 7 amps at 240v for pump and a convienence outlet thats what I need the neutral for.
Old 06-11-2012, 07:37 AM   #5
I'm thinking its a really small 120v load right? Is it a power adapter for something? I remember a while ago somebody asked a question a bit like this and then they found a 240v power adapter for whatever they were using and used an inline fuse. It was something to do with a water heater.
Just saw update nvm
jakeparr is offline   Reply With Quote
Old 06-11-2012, 07:41 AM   #6
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
Just tag a convenience receptacle back to back of an existing inside receptacle and use the 12 feed for your pump. Doesn't the pool ( a body of water that doesn't discharge after use) require a insulated ground?
Old 06-11-2012, 08:49 AM   #7
wildleg's Avatar
1) wire the pump 120 and use the existing ckt.
2) pull a feed
Old 06-11-2012, 10:05 AM   #8
Rewards Points: 1,006
If 680.21(A)(4) applies in his jurisdiction, he's okay with the portion of the wiring that's inside the house being in NM without an insulated grounding conductor. Where he goes outdoors, conduit is required, and a green insulated grounding conductor, never smaller than 12AWG.
(4)
One-Family Dwellings. In the interior of one-family dwellings, or in the interior of accessory buildings associated with a one-family dwelling, any of the wiring methods recognized in Chapter 3 of this Code that comply with the provisions of this paragraph shall be permitted. Where run in a cable assembly, the equipment grounding conductor shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable assembly.
__________
Was born in HACKensack, NJ
CraigV is offline   Reply With Quote
electrical panel ground vs. neutral bobster NEC Code Forum 96 11-08-2013 01:32 PM
How many Neutral and Gnd in off a 3-phase panel swimmer NEC Code Forum 8 08-10-2011 11:08 AM
Fused neutral panel! zoopenny Vintage Electrical 18 05-29-2011 08:08 PM
CH Plug-on neutral panel Magnettica Services and Service Equipment 24 02-08-2011 10:03 PM
Neutral in Sub-panel BrianJayT General Electrical Discussion 4 03-13-2009 06:49 PM