I did this experiment many years ago when I was teaching a grounding class for an neighboring local. When I set up the class I asked the training director to drive a ground rod for me in the grass outside the building. We had a couple of inches of rain in the day before the class....still only 4 amps when 120 volts was connected to the rod.
xpertpc (01-28-2015)
Old 01-28-2015, 07:15 AM   #22
Rewards Points: 1,004
that's about 30 ohms - you need another rod
xpertpc is offline   Reply With Quote
Old 01-28-2015, 07:30 AM   #23
Retired Account
Rewards Points: 14,650
To the OP,
the old 250.32 allowed a 3 wire to detached buildings
N&G bonded, to a GEC
This had it's flaws , mainly due to everything becoming a potential noodle in between them, being summarily amended to N&G separation some code cycles ago.
You may still see them out there, but we can't install that way any more
Ironically, the poco can!
The Following 2 Users Say Thank You to chicken steve For This Useful Post:
51360 (01-28-2015), meadow (01-28-2015)
Old 01-28-2015, 07:58 AM   #24
Rewards Points: 20
Originally Posted by 3D Electric
Does anyone have any suggestions or comments on how they would like me to perform this experiment? I am going to record it so I can upload it here.
Yes, come to my job, pound the 2 rods in, do your test, and you can leave the rods there.
Doobster08 is offline   Reply With Quote
The Following 2 Users Say Thank You to Doobster08 For This Useful Post:
A Little Short (01-28-2015), mcclary's electrical (01-28-2015)
Old 01-28-2015, 09:00 AM   #25
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
Originally Posted by hunterjo View Post
all these replies make sense. I know some building inspectors will allow a sub panel in a detached building to not have a grounded conductor just the 2 ground rods 2hot and one neutral with the grounded and grounding bar bonded. but in sub in attached building the neutral has to be floating. does this sound sight.
thanks again for all the feed back so far looking to read more good info
That Setup hasnt been legal since the 02 code
Old 01-28-2015, 10:14 AM   #26
Rewards Points: 3,090
can some explain why a attached building has a sub panel with the grounding bar and the grounded bar isolated but in a detached building both bars are bonded with ground rods.
Originally Posted by 3D Electric View Post
A sub panel has the grounds and the neutral separated. Being in a detached building has nothing to do with it being a sub panel. The grounds and neutrals are still required to be seperated.
Ok, obviously this thread is using the NEC.
Are the ground and neutral required to be isolated in a seperate building? Even in buildings housing livestock?
Borgi
Old 01-28-2015, 10:22 AM   #27
evil bastard
Rewards Points: 746
Borgi
Yes....
51360 (01-28-2015)
Old 01-28-2015, 10:53 AM   #28
Rewards Points: 308
Originally Posted by meadow View Post
Very true, but driving a ground rod actually proves how little or how much resistance it has. Even if someone received half an ohm, as much as people would celebrate, that is still would not low enough to be truly safe with any standard breaker.
Nothing beats a copper wire back to the source, nothing.
Don't be so absolute. A grc conduit with no equipment ground has been proven in testing by US Steel to return fault current faster and better than the properly sized copper equipment ground matched to the test fault .
Libtard logic: It’s okay for people to LOOT in person, but not VOTE in person
Old 01-28-2015, 01:38 PM   #29
Very Long Vacation
Rewards Points: 5,262
Any links, Im curious?
I did leave that out, my mistake. But when it comes to things like earth electrodes forget it.
Old 01-28-2015, 01:48 PM   #30
Very Long Vacation
Originally Posted by chicken steve View Post
To the OP,
The code would restrict it if anything like a phone line or pluming line was going out to the structure. The issue was that people would often add them latter in time creating an unknown issue. The CMP proposal also mentioned it would be safer eliminating the wire 3 feeds; which I would imagine refers to an open noodle.
POCOs are always an exception, being the only ones who do it in the industry.
Old 01-28-2015, 02:12 PM   #31
Mad Skills
Celtic's Avatar
Rewards Points: 2,050
NEMA - Bulletin No 97
Steel Tube Institute - Equipment Grounding Using Steel Conduit
Top 2 results from a google search
póg mo thóin
The Following User Says Thank You to Celtic For This Useful Post:
meadow (01-28-2015)
Old 01-28-2015, 02:14 PM   #32
Very Long Vacation
Thanks!
Old 01-28-2015, 02:17 PM   #33
Rewards Points: 430
Not that it has anything to do with "earthing" but, go to link below and check out the reports, while you're there download the GEMI software.
http://steeltubeinstitute.org/steel-...ysis-research/
Originally Posted by piperunner I just told you guys why you just cant read try to read better does that happen a lot up north must be the cold .
Fibes is offline   Reply With Quote
The Following User Says Thank You to Fibes For This Useful Post:
meadow (01-28-2015)
Old 01-28-2015, 03:53 PM   #34
220/221's Avatar
Rewards Points: 4,352
I really want to do this so, fill me in.
Old 01-28-2015, 04:01 PM   #35
This is the biggest offender I have seen in every place I have worked in the last 40 years.
from the above link -
"where the raceway is terminated at concentric or eccentric knockouts. The raceway must be bonded to the enclosure using the same"
Old 01-28-2015, 04:31 PM   #36
Rewards Points: 60
It depends on the voltage. There is no issue with 120 or 240V branch circuits or feeders with the concentric ko's. Services require bonding.
Also bonding is req. when you have more than 250v to ground depending on the situation.
Celtic (01-29-2015)
Old 01-28-2015, 04:59 PM   #37
Very Long Vacation
I want to see the results to
A test like that would add a lot to this site, as it debunks again the greatest misconception in the trade.
Old 01-28-2015, 05:06 PM   #38
Rewards Points: 60
Don has already mentioned that they did the experiment. McClary stated why you didn't need to do the experiment and I mentioned that a mike holt member performed the experiment. What more do you need. It will not blow the circuit unless you tie the rod to the service. 120v connected directly to the rod will only wake up the worms unless you live in one of those rare places on earth where you have less than 5 ohms.
V=amps x Resistance
or
R= V/I
R= 120V / 20 amps = 6 ohms
51360 (01-28-2015)
Old 01-28-2015, 05:52 PM   #39
evil bastard
Rewards Points: 746
V=amps x Resistance
or
R= V/I
We did a total of 9 cell towers in the last two years, and I can tell you that 5 ohms is very hard to get.
Old 01-28-2015, 06:19 PM   #40
Rewards Points: 60
And virtually impossible with rods
Square D QO panels and Square D Plug On Neutral QO panels DavidSattero General Electrical Discussion 9 07-16-2014 07:23 PM
Who knows their CH panels? Joefixit2 General Electrical Discussion 16 02-28-2014 01:17 PM
Sub panels Copper 0/2 General Electrical Discussion 7 01-24-2013 04:31 PM
Sub Panels Svtlightning207 Residential Electrical Forum 7 04-05-2012 08:46 PM
Replacing 50 year old westinghouse panels with newer panels SPINA ELECTRIC Services and Service Equipment 1 08-08-2010 01:20 PM