Subject to physical damage? - Electrician Talk - Professional Electrical Contractors Forum
Old 08-06-2013, 05:01 AM   #1
carryyourbooks's Avatar
Rewards Points: 1,292
Default Subject to physical damage?
what defines this? 300.5 (d)4 says conductors that are subject to physical damage shall be installed in sched 80 pvc, etc.
i am having a house built where there is no jurisdiction do inspections. the EC is installing sched 40 where direct burial conductors emerge. i always install sched 80. isn't the side of my house where mowers and weed eaters will be passing by considered "subject to physical damage"? i am pretty sure it is, but please, correct me if i'm wrong.
carryyourbooks is offline   Reply With Quote
Old 08-06-2013, 05:09 AM   #2
Jlarson's Avatar
Rewards Points: 4,074
It's open to interpretation. Since there is no inspection its up to the installer.
The Following User Says Thank You to Jlarson For This Useful Post:
HackWork (08-06-2013)
Old 08-06-2013, 05:55 AM   #3
Retired Account
Rewards Points: 14,650
That conductors are sleeved at all rates five stars here Books
and inasmuch as sch80 is lauded as the new physical damage fix in art 300 , methinks one could run either 80 OR 40 over with a tank...
Old 08-06-2013, 06:38 AM   #4
8V71's Avatar
Rewards Points: 2,900
Sched 40 will offer good protection from the scenerios you mentioned.
8V71 is offline   Reply With Quote
Old 08-06-2013, 05:10 PM   #5
220/221's Avatar
Rewards Points: 4,126
It's just one of the many vague phrases use in the NEC.
If you are going to effectively write law, you need to take out interpretation.
The Following User Says Thank You to 220/221 For This Useful Post:
janagyjr (08-06-2013)
Old 08-06-2013, 08:27 PM   #6
mbednarik's Avatar
Rewards Points: 1,120
I think if sch 40 straped as required you will not have any issues with general wiring. Now service entrance conductors I do sleeve with 80.
Old 08-06-2013, 09:24 PM   #7
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
Install some SEU cable and call it a day.
Replies based on NEC 2014
Old 08-06-2013, 09:28 PM   #8
mbednarik's Avatar
I dont think you can use seu for direct burial. SEU on the exterior of a home here is required to be sleeved for protection from physical damage.
Old 08-06-2013, 09:29 PM   #9
Going_Commando's Avatar
Rewards Points: 1,542
There is no definition in the code book for "subject to physical damage". It is basically up to the AHJ. What pisses me off is that I can't find anywhere to get couplings and whatnot that is schedule 80, and that is usually where PVC breaks. Kinda defeats the whole purpose if you ask me.
ETA: When stubbing up out of the ground I always use Schedule 80 or RMC either to the meter, disco, or whatever, and for the first 10 feet going up a pole. If it is on the edge of a parking lot or what have you, then it is in rigid.
Old 08-06-2013, 09:30 PM   #10
mbednarik's Avatar
I have only seen sch 80 elbows, that it. It gives the inspector a warm fuzzy feeling inside, kinda like RMC.
Old 08-06-2013, 09:31 PM   #11
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
I was being facetious. There's a five-dollar word. My bad.
NM subject to physical damage raider1 NEC Code Forum 42 01-29-2012 09:54 AM
"subject to physical damage"??? bctoasters NEC Code Forum 42 10-17-2011 10:24 PM
Where subject to physical damage vos General Electrical Discussion 17 08-16-2010 09:08 PM
Sch 40 PVC subject to damage? nitro71 NEC Code Forum 4 05-01-2010 11:39 AM
PVC Jacketed MC Cable Subject to Physical Damage Mountain Electrician General Electrical Discussion 2 08-20-2007 11:08 PM