If you wanted/needed to test insulation with a Megger on new wiring for a house should the joints be taken apart at the boxes?
The EGCs and neutrals would be removed at the panel but not sure if the splices/joints should be taken apart at the boxes.
There are no devices installed yet.
Old 07-10-2018, 01:04 AM   #2
Rewards Points: 18,183
Cap all loose ends of conductors or you will possible be reading shorts all over the place.
JOBS GROWTH SOARS
RECORD WORKING
UNEMPLOYMENT 50-YEAR LOW
Drudge Report
Old 07-10-2018, 01:05 AM   #3
Magic Smoke Remover
Rewards Points: 1,966
Seems like you'd have to test an awful lot of points if you took every wire nut off...
If you pigtail receptacles, you'd only have to test each circuit at the breaker, and then each switch leg.
If you don't pigtail receptacles/disconnect everything, you'd have to meg each box wouldn't you?
Old 07-10-2018, 01:23 AM   #4
I'm really only concerned with home runs.
Old 07-10-2018, 01:53 AM   #5
And cables with the sheath missing right? Ole macmikey git's around you know...
JOBS GROWTH SOARS
RECORD WORKING
Drudge Report
Old 07-10-2018, 02:13 AM   #6
Old 07-11-2018, 01:48 AM   #7
Rewards Points: 1,972
Everything connected with any electronics and light bulbs removed, neutrals isolated from ground, power off, switches on.
You could test all the conductors at one time CBs on, L1 to neutral, L2 to neutral, L1 to L2 and Neutral, L1, L2 to ground if the reading is full scale all is good if you get a low reading turn off one CB at a time.
A Little Short (07-11-2018)
Old 07-11-2018, 02:18 AM   #8
I did the test today and thankfully everything checked out.
I didn't have any breakers installed yet so I checked each circuit.
But that is a great idea to check with the breakers. That would save a lot of time.
New construction residential wiring Cow General Electrical Discussion 21 04-15-2018 05:24 PM
Testing wiring with a megger Angel Advanced Tech Services and Service Equipment 46 12-22-2017 11:24 AM
NETA Testing Co. Looking for Several Field Techs ykavanagh Looking To Hire 1 03-24-2017 01:28 PM
Damaged wiring inside a water heater - questions Islander General Electrical Discussion 14 01-01-2017 05:37 AM
NPLFA circuit wiring khfiei General Electrical Discussion 5 02-06-2016 12:03 AM