Thermostat question? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree14Likes
  • 1 Post By inetdog
  • 3 Post By MechanicalDVR
  • 2 Post By emtnut
  • 1 Post By Signal1
  • 1 Post By Drsparky14
  • 5 Post By MechanicalDVR
  • 1 Post By electricguy
Old 03-31-2017, 07:14 PM   #1
Rewards Points: 30
Default Thermostat question?
This may sound really simple, but would this line stat work to break one leg of a 120/240 volt baseboard heater?
Family guy is offline   Reply With Quote
Old 03-31-2017, 07:15 PM   #2
Rewards Points: 30
Old 03-31-2017, 07:17 PM   #3
Rewards Points: 36
Originally Posted by Family guy View Post
Attachment 102953
Yes. The NEC may require that there be a disconnect that opens both L1 and L2 at the same time, but a control thermostat only needs to open one.
Sent from my XT1585 using Tapatalk
inetdog is offline   Reply With Quote
Old 03-31-2017, 07:28 PM   #4
Rewards Points: 30
Yeah normally I get the spdt stat with the four leads but got the wrong one will have to freshen up on nec requirements for resistive loads.
Old 03-31-2017, 07:35 PM   #5
Rewards Points: 3,006
You mean you usually get a DPST.
Old 03-31-2017, 07:53 PM   #6
Rewards Points: 30
Ok. So I read in 424.20(b) that thermostats that do not directly interrupt all ungrounded conductors are not permitted as disconnecting means.
The disconnecting means in 424.19 needs to simultaneously disconnect heater and controller from all ungrounded conductors.
424.19(A) states that the if there be supplementary overcurrent protection the disconnecting means must be within sight.
The stat is not overcurrent protection, but there is a thermal cutoff within the baseboard.
Breaker is around the corner from the stat and heater it controls.
It does not jump out and tell me that it this would be a violation, unless I am missing something.
Old 03-31-2017, 08:00 PM   #7
Band Member
emtnut's Avatar
Rewards Points: 2,004
I'd be surprised if the breaker wasn't the disconnect
MechanicalDVR and circuitman1 like this.
Old 03-31-2017, 08:45 PM   #8
Gold Pliers Champion
Signal1's Avatar
Rewards Points: 2,356
As Inetdog and your instructions on the box both said, if you wire it that way it will electrically work fine, but will not provide a disconnecting means within sight as required by NEC 424.19 (B)(1).
A thermostat that opens all ungrounded conductors AND has a marked OFF position on it can serve as both the disconnecting means and the controller. See 424.20(A) parts 1-4 and 424.20(B).
Edit: Somehow missed your post #6, glad you do your homework!
I'm not sure if I would consider the thermal as "overcurrent protection", as that's more a high limit to prevent a fire (IE idiots piling laundry on the heater) and not really to protect the conductors.
shocksystems likes this.
METGA
Signal1 is online now   Reply With Quote
Old 04-02-2017, 04:03 PM   #9
Rewards Points: 28
Just use that t stat and throw a lockout in the panel.
Majewski likes this.
Drsparky14 is offline   Reply With Quote
Old 04-02-2017, 04:13 PM   #10
I take it you haven't installed that much electric baseboard. Always had breakers for each room and a t-stat per room unless it was a large room that needed a lot of heat.
Breaker was the means of disconnect, I'd never rely on a thermostat for a means of disconnect.
Old 04-02-2017, 04:49 PM   #11
Rewards Points: 3,012
I have had a few thermostats that would not turn off in the off position
electricguy is online now   Reply With Quote
Old 04-02-2017, 10:31 PM   #12
I've had many that have an off position but one side is welded in place and still passes voltage.
Old 04-03-2017, 10:41 AM   #13
Wyome
Rewards Points: 914
We have installed a fair bit of electric heat, with room t-stats. Never had an inspector fail us for this reason. I always thought about though.
Transformer internal wiring question JasonCo General Electrical Discussion 11 03-22-2017 06:10 PM
Installing a double pole thermostat to 2 heaters smh382 General Electrical Discussion 2 12-28-2016 07:56 PM
Question about interview score disclosure EmilyRose Electrician Apprentice Forum 18 10-30-2016 12:06 PM
Question about Solenoids (Relay/Starter/Contactor) JasonCo General Electrical Discussion 14 10-03-2016 01:04 PM
Line Voltage Thermostat with Terminals splatz Residential Electrical Forum 7 04-10-2016 06:11 PM