I am working on an electric steam kettle. The element is a 6 wire element (three loops) that is 24kW three-phase 220v. There are two contactors and a low water switch, t-stat, and tilt switch. The kettle was converted from 480v by switching out the element, removing a transformer, and adding one of the contactors. During that install, some wires were switched, shorting out the new contactor. A second new contactor was installed. The steam kettle worked for dozens/hundreds of cycles. Just recently the "new" contactor fried. After examining the circuitry I think the cause was the wiring. The wiring running to the contactor was never replaced after the first short.
I have replaced all suspect wires and put in a new contactor, but the element will not heat. Each of the three element loops has continuity and is reading the same (and to spec) resistance. There is no short to the kettle body. I am getting a reading of 212v across the element. There is the correct phasing going to the element terminals.
It appears that the element is functioning and I am getting a correct voltage reading across the element - but no heat. Ohm's law doesn't lie, so something is not right. Any thoughts on what I am over looking?
barnacleak is offline   Reply With Quote
Old 01-05-2018, 09:34 PM   #2
Rewards Points: 21,896
You should get a electrician to come out and help you on this one.
it much safer to have a electrician to take a look of it.
accourding to your profile it say .,
food production equipment
therefore the best answer is get electrician and deal with it due they will know excatally what to look for.
John Valdes and The_Modifier like this.
Old 01-05-2018, 09:36 PM   #3
Light Bender
eddy current's Avatar
Rewards Points: 7,812
Just because there is voltage, and continuity, does not mean the element will work. It’s probably fried
Old 01-05-2018, 09:52 PM   #4
Rewards Points: 226
If you are not an electrician, please visit our sister site.
http://www.DIYChatroom.com/register.php/
The_Modifier likes this.
Old 01-05-2018, 10:43 PM   #5
A Little Short's Avatar
Rewards Points: 1,014
You forgot to "lock the door"!
zac and The_Modifier like this.
Old 01-05-2018, 10:47 PM   #6
sbrn33's Avatar
Rewards Points: 3,516
There is no such thing as a 3 phase element.
readydave8 likes this.
Old 01-05-2018, 11:41 PM   #7
Rewards Points: 7,603
That's what I was thinking. But at least the "phasing" is correct.(?) Along with the "tilt switch", the low water switch, the T-stat, and the second contactor, I'd suggest checking if it's plugged in.
Old 01-05-2018, 11:55 PM   #8
Rewards Points: 3,986
Phase rotation on a heater is very important.. Otherwise it takes heat from the air and doesn't give off heat..
sbrn33, readydave8, emtnut and 1 others like this.
telsa (01-05-2018)
Old 01-05-2018, 11:57 PM   #9
Rewards Points: 3,112
If the 3 elements are 480 volt each, they will be connected ∆. If so, there should be 480 across each element. If there is only 212 volts, the problem is upstream from the elements.
I would measure voltage at the incoming line (under load of course), if it's good then I'd do a fall of potential test from the element to the incoming line.
Have you measured current at the elements?
It's also possible you have an open fuse somewhere.
Old 01-06-2018, 12:10 AM   #10
Rewards Points: 1,510
is the phase rotation correct ?
Is it a star or delta set up ?
Old 01-06-2018, 01:17 AM   #11
It all depends on what you call correct. Our rotation in the U.S. goes completely opposite from the "land down under"!
Old 01-06-2018, 03:56 AM   #12
Does that mean we go the right way ?
And you guys go the wrong way ?
Old 01-06-2018, 07:16 AM   #13
Southeast Power's Avatar
Rewards Points: 8,696
Is the OCP fuses by any chance?
micromind likes this.
Old 01-06-2018, 12:56 PM   #14
Thanks for the responses. I will be getting an electrician.
The Following User Says Thank You to barnacleak For This Useful Post:
The_Modifier (01-06-2018)
Old 01-06-2018, 10:06 PM   #15
Please come back and let us know what it was ?
Tags
contactor, element, three phase, water heater
Phase loss monitor doesn't like generator gottspeed PLCs, VFDs, Motors and Controls 8 12-27-2017 07:04 PM
Financing large jobs Ty the electric guy General Electrical Discussion 27 12-17-2017 01:10 PM
220 single phase to 3 phase? TechieBecky Canadian Electrical Forum 16 02-19-2016 04:46 AM
Can be both a three or single phase motor just the cowboy General Electrical Discussion 2 01-21-2016 11:36 AM